Results 1 to 8 of 8
  1. #1
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    30 gh pro dialog plus chiller (Carrier)



    Hi;

    30 GH chiller showing fault code 40,41,47,46,103,203.

    Replaced the exv motor ,pressure transaduser,sensor of both circute.
    still the chilller is tripping . somebody can help please?



  2. #2
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: 30 gh pro dialog plus chiller (Carrier)

    Hi vinod
    Are you still getting the same fault codes after changing all the listed parts.
    103 and 203 are HP trips on circuit 1 and 2. Have you checked the driers and are all the condenser fans running.
    Blocked driers can bring up 46 & 47.
    Paul

  3. #3
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: 30 gh pro dialog plus chiller (Carrier)

    Not sure if they are right for the 30GH but for the 30GX the codes are as follows.

    103 - Compressor A1 current imbalance >10%
    203 - Compressor A2 current imbalance >10%
    46 - Oil solenoid failure compressor A1. oil pd > 17kPa
    47 - Oil solenoid failure compressor A1. oil pd > 17kPa
    41 - loss of communications with analogue card
    40 - loss of communications with fan card

    Brit

  4. #4
    Join Date
    Jun 2008
    Location
    chuyer
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: 30 gh pro dialog plus chiller (Carrier)

    Hello,

    30GH's codes are not the same with 30 GX because the softs are different.
    For help me, Your display PRO DIALOG is Black or Grey?

  5. #5
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: 30 gh pro dialog plus chiller (Carrier)

    Hi Vinod, alarm # 46 & 47 indicate a need to check the oil solanoid valves. Sometimes they remain partly open due to some dirt.

  6. #6
    Join Date
    Mar 2009
    Location
    Goodlands
    Age
    44
    Posts
    9
    Rep Power
    0

    Re: 30 gh pro dialog plus chiller (Carrier)

    hi did you try change the exv board ,

  7. #7
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: 30 gh pro dialog plus chiller (Carrier)

    is it possible to take some note's of the temps and pressure wile its working???
    mabey couse of an unbalance in current the comps are not functioning like they should, and therefore give an unbalanced refrig isue, whitch cause an constand tripping on security's.

    just some loud thingking.

    Ice

  8. #8
    PPaul's Avatar
    PPaul Guest

    Re: 30 gh pro dialog plus chiller (Carrier)

    Can I have the wiring diagram of Prodiolog chiller 30GH 245?

    Thank You

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  3. Carrier Pro Dialog Plus help
    By borodave1973 in forum Air Conditioning
    Replies: 5
    Last Post: 11-11-2007, 07:47 PM
  4. Carrier Chiller Help
    By superswill in forum Trouble Shooting