Thread: Hot gas defrost in NH3
23-08-2008, 05:51 AM #1
Recently we came across a situation wherein the Plate freezer plates were bending after a period of about 6 months operation.
After checking the system it was found that the HGD system was without any pr. reducing valve & hence Ammonia at high pr was entering the Plates & that resulted in bending of the plates.
The paper which I had posted earlier had clearly specified that pr. reducing valve upto 80 KG is a must in the HG line.
24-08-2008, 12:43 AM #3
Re: Hot gas defrost in NH3
My first impression of this issue is not the pressure of the hot gas, but rather the factor of vapor propelled liquid in the hot gas line. This sort of issue can creta e a lot of energy that will bend metal (or break it) very easily.
My preference is to provide a means of draining the condensate out of the hot gas lines. If you do this, then the gas pressure does not have anything to do with it.If all else fails, ask for help.
24-08-2008, 06:08 AM #4
Dear Us Iceman,
Your point is also important & we shall take note of that as well
28-08-2008, 10:28 AM #5
I agree with the US ICEMAN's ideas.
Toshiba RAV SM/SP1400 defrost problem
By SteinarN in forum Heat PumpsReplies: 11Last Post: 20-02-2008, 04:25 PM -
No Power for Defrost Timer Motor
By kln in forum DomesticReplies: 6Last Post: 21-01-2008, 08:22 AM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
Hot gas defrost vs Electric defrost
By herdian in forum IndustrialReplies: 19Last Post: 13-08-2007, 11:25 PM