    Refrigerant vs Chilled Water



    I am building a system using an automotive ceiling mount evaporator rated at 22000 BTU, but I want to use chilled water instead of R134a.

    Besides making sure that the water has the appropriate corrosion inhibitors, are there any other gotchas that I should be aware of?


    Mark Baker

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    If the given capacity was rated at -10°C (i assume this) then your water/glycol must alos have +/- -10°C. Otherwise you won't reach your 22000 BTU.

    Remove eventually the distributor and make sure you fit the correct pump.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hi baker,

    looks like a bad idea to me. water coils have a different design.

    consult Marc O'Brien. I'm sure he can help you with it.

    chemi

  4. #4
    Join Date
    Oct 2001
    Location
    Perth, Australia
    Posts
    87
    Rep Power
    23
    Just to clarify, I am using water because the unit will be in a sleeper cab and I don't want to risk smothering the occupant should the evaporator spring a leak.

    The compressor is only rated at 7600 BTU/H, and the evaporator was selected for size and availability, rather than capacity.
    Mark Baker

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    ok baker,

    its about 1HP now you will need a condensing unit with some sort of gas/ water heat exchanger, I would have use a welded plate one, a water pump, magnetic will never leak! and a small expention tank.

    all of that should be desiged as small as possible with all the necessary protections for both circuits, water and gas, and find a good tech. to build it for you.

    good luck

    chemi

Similar Threads

  1. Do I need a chilled water buffer vessel
    By Consultant in forum Commercial
    Replies: 32
    Last Post: 02-03-2011, 09:40 AM
  2. Refrigerant to water heat exchangers
    By sunwind in forum Technical Discussions
    Replies: 20
    Last Post: 24-06-2008, 01:40 PM
  3. Chilled Water Coil
    By elmusasc in forum Fundamentals
    Replies: 4
    Last Post: 11-08-2006, 02:42 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Replies: 1
    Last Post: 31-07-2002, 08:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •