    mitsubishi heavy split fault



    I have just installed mitsubishi heavy below cieling split system.
    the unit is on a hard wired controller.
    problem is the indoor fan motor runs for a couple of seconds the cuts out then starts straight back up again and repeats this process.
    this happens in all modes
    the unit sometimes stays on with no problem.
    you can hear the relay on the pcb clicking as fan stops and starts.
    there is no fault code on the controller
    or irregular led lights on indoor or outdoor units.

    strange one
    can anyone help



  2. #2
    Join Date
    Aug 2008
    Location
    Belgium
    Age
    44
    Posts
    74
    Rep Power
    16

    Re: mitsubishi heavy split fault

    What model is the indoor and the outdoor unit ?

  3. #3
    Join Date
    Jan 2008
    Location
    Manchester, Uk
    Age
    53
    Posts
    57
    Rep Power
    17

    Re: mitsubishi heavy split fault

    Sounds like you have it set to heating mode, or in auto but calling for heat. The condensing unit will run, but the indoor fan will only run when the coil thermister reaches a certain temperature, if the fan is continuously starting and stopping, it is possible the refrigerant charge is short. Hope this helps. Regards, Andy C.

  4. #4
    Join Date
    Jul 2008
    Location
    london
    Age
    53
    Posts
    13
    Rep Power
    0

    Re: mitsubishi heavy split fault

    refrigerant charge is ok
    only a 10m pipe run and no low pressure error code displaying
    problem seems to happen in all modes
    but intermittant, sometimes runs ok in cooling and heating

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: mitsubishi heavy split fault

    What is the model no.?

  6. #6
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: mitsubishi heavy split fault

    This sounds like an FDEN model unit that has been fitted with an RCE hard wired remote controller and the infra red receiver hasn't been disabled.
    go to the discharge side of the unit and look for a light on the panel. if there is one or any numbers the unit still has the ir receiver connected so remove rh side panel and locate the 2 core cable going down length of unit in middle of which is an inline connector. Just pull this apart (with the power off!) and reboot system.
    Brit

  7. #7
    Join Date
    Jul 2008
    Location
    london
    Age
    53
    Posts
    13
    Rep Power
    0

    Re: mitsubishi heavy split fault

    thanks
    i spoke to mitsi technical before i recieved your message and they said the same
    disconnect infa red sensor

    not been back to site yet but im sure all will be ok

    thanks for your help

  8. #8
    Join Date
    Dec 2007
    Location
    england
    Age
    39
    Posts
    13
    Rep Power
    0

    Re: mitsubishi heavy split fault

    its a easy job to do i had same problem ,its just the matter of snipping a wire on indoor pcb board to transfer from infa red to hard wired

Similar Threads

  1. Fault code for a mitsubishi heavy
    By marc5180 in forum Air Conditioning
    Replies: 7
    Last Post: 29-02-2008, 08:22 PM
  2. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 10:23 PM
  3. Mitsubishi Heavy - Help needed Urgently
    By marc5180 in forum Air Conditioning
    Replies: 6
    Last Post: 19-10-2007, 11:45 PM
  4. Mitsubishi Heavy Industries
    By Freecool in forum Air Conditioning
    Replies: 6
    Last Post: 17-08-2007, 03:20 PM
  5. fault codes for mitsubishi heavy industries air con
    By mal in forum Trouble Shooting
    Replies: 1
    Last Post: 21-10-2006, 06:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •