Thread: breaker type?

  1. #1
    Join Date
    Mar 2006
    Location
    newcastle upon tyne
    Posts
    51
    Rep Power
    19

    breaker type?



    hello,
    i recently replaced an old failed condensing unit with the same type, on starting the unit 230v it tripped the 16a b type breaker, i checked the start amps and it pulled 54a then ran at 9.4a (max run 11.5a on the unit plate) i advised the customer that a c type 20a breaker was required, the customer got an electrician out who said the breaker was ok for the appliction and the fault lay with my unit, was i right ? i went back today and checked it over again all ok except the breaker trips on 50% of starts.

    please advise

    thanks



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: breaker type?

    I'd be inclined to fit a MOTOR rated type 3 (D) breaker to anything with a motor.
    B curve is not designed for high inrush applications.

    How long does the comp draw 54A?

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: breaker type?

    Needs to be a 'C' or 'D' type to run a motor. 'B' types are for resistive loads only.
    Sound like the sparky is used to doing domestic work only and not motor circuits.
    If the max run is 11.8A then a 16 C/D type would do.

    Jon

  4. #4
    Join Date
    Mar 2006
    Location
    newcastle upon tyne
    Posts
    51
    Rep Power
    19

    Thumbs up Re: breaker type?

    thanks for the reply boys, just wanted to make sure i wasnt talking bull!!!!!

    oh the 54 amp is just the start amps only showing when the amp meter is on peak hold and only for 1/2 a second or less
    Last edited by tait71; 20-08-2008 at 10:15 PM.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: breaker type?

    Quote Originally Posted by tait71 View Post
    thanks for the reply boys, just wanted to make sure i wasnt talking bull!!!!!
    Starting current of normal compressor is 6 times grater then running current (which is exactly your case). Sparky need few days of additional education!

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: breaker type?

    The tripping curve on a 'C' type mcb is rated for motor inrush currents and is the correct application for full speed motors.

    The tripping curve on a 'D' type mcb is designed for Transformer circuits as these tend to have a higher and longer inrush current.

    You may find that you could end up with damage to a compressor if you use a D type mcb as these will allow the motor to operate under fault conditions longer than a C type mcb.

    Type 'B' mcb's are suitable for inverter driven motors as these tend not to have large inrush currents

  7. #7
    Join Date
    Feb 2008
    Location
    Surrey
    Age
    67
    Posts
    17
    Rep Power
    0

    Re: breaker type?

    From what I remember without getting the regs book out is that for instant tripping 0.1 secs
    a type b needs 5 x rating
    a type c needs 10 x rating
    a type d needs 20 x rating of the breaker

    so the 16a type b would be 16 x 5 = 80 amp would make it trip in 0.1 secs
    a type c would need 16 x 10 = 160 amps for instant trip and a 16 amp type d would need 16 x 20 = 320 amps to flow before it tripped instantly.
    So the 16 a type b is not in the the instant tripping part of the curve but in a near tripping area.
    I would say the 16 c sounds best.

  8. #8
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: breaker type?

    Would fit type D breaker for AC unit
    Transvestites are men who like to eat, drink, and be Mary.

  9. #9
    Join Date
    Mar 2006
    Location
    newcastle upon tyne
    Posts
    51
    Rep Power
    19

    Re: breaker type?

    just an update, the sparkie has fitted a c16a breaker and the plant is now running fine not trip for 24 hours, thanks for all the replys.

    cheers

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: breaker type?

    Some very useful info Guys!
    Thanks Grizzly

  11. #11
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    18

    Re: breaker type?

    Would always go for a C first, if there is still a neusance trip issue then fit D type.

  12. #12
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: breaker type?

    Bumping this one again.
    I've got an LG 7kW wall split that have nuisance trips.
    It's wired with 2.5mm cable and a 16A c/b (c type)

    The system FLA is 13A, it's a recip compressor with soft start PCB and extra capacitor.
    When starting, it easily pulls 16A measured with a clamp meter.

    Worth trying a 16A D type? I know the MCBs trip point is to do with way higher in rush current that I couldn't measure, it's the 16A I could see that's buggin me.
    I'd rather not use a 20A due to the unknown longish cable run (unknown at this stage where the cable runs exactly through the roof and walls, ventilation, insulation etc)

    I mean I guess I know the answer myself, try the 16A D curve, and if still a problem, run 4mm cable and a 20A MCB. For such installs that as this (7kw conventional recip split system with a over 15m cable length that I have done myself), I've usually got a sparky to use 4mm. But this system is over 5 years old and I don't know the history of the install, nuisanse trips, and neither does the new owner.
    Last edited by paul_h; 31-08-2010 at 10:10 AM.

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: breaker type?

    I'd try a D type as well, breakers can also get tired if they have been reset a lot in the past.

    Had a customer with a 3ph breaker that would trip a few times every milking and ignored our advice to get it changed till the day it blew up as he reset it, think it needed a new board once the smoke had cleared

  14. #14
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: breaker type?

    D type are a bit of a nail, if you dont have a option it looks like a C 20 to me, 2.5mm cable and its only start current so why not. wait for the rush of why nots !

  15. #15
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: breaker type?

    Quote Originally Posted by monkey spanners View Post
    I'd try a D type as well, breakers can also get tired if they have been reset a lot in the past.

    Had a customer with a 3ph breaker that would trip a few times every milking and ignored our advice to get it changed till the day it blew up as he reset it, think it needed a new board once the smoke had cleared
    Yeah the circuit breaker in this is new.
    A electrician was called first. They replaced the probably good C16 with some cheap chinese C16 and told the customer that if it trips again the a/c is faulty and get someone to look at it

    edit:
    If electricians of that calibre are the type to wire these installs, I don't trust their cabling enough to just go up a size to 20A
    What I really mean is 16A is probably the right size c/b for the cable, and they got that part right, problem is they used the wrong size cable.
    Last edited by paul_h; 01-09-2010 at 12:18 AM.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: breaker type?

    13 A for a 7 kW LG
    Speaking of a very low COP.
    There's something wrong with your unit or your clampmeter.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: breaker type?

    Ha, no, that is what is printed on the label of the A/C too.

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: breaker type?

    We may replace in Belgium the breaker with a motor protector, of course setted to the propers AMPs of the motor and not exceeding max AMP for the cable.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: breaker type?

    A good point there Peter.
    The MCB is installed to protect the cable, not the motor. You can increase the rating of the MCB providing you do not exceed the cable rating for the installation, taking into account proper cable sizing calcs including all derating factors.
    To protect the motor, you need to install a motor overload, set approximately 15 to 20% above FLC

  20. #20
    Join Date
    Nov 2009
    Location
    Adelaide, South Australia
    Age
    42
    Posts
    20
    Rep Power
    0

    Re: breaker type?

    As a sparky all I can say is that we generally use 'C' curve breakers for everything in Australia (resi+commercial+industrial) as that is what the wholesaler stocks! I have seen 'D' curves in industrial apps. I have never seen a 'B' curve in service. I'm sure they're about.

    For instant trip:
    Type B = 4x rated current
    Type C=7.5x rated current
    Type D=12.5x rated current
    (AS3000 Appendix B4.5)

    Paul H
    2.5mm2 is rated to:
    27A spaced from surface
    26A touching surface
    20A exposed to sun
    23A enclosed in air
    20A partially surrounded by insulation (but laying on a surface)
    19A partially surrounded in an enclosure clipped to a surface
    13A completely surrounded by insulation
    12A in an enclosure completely surrounded by insulation, 30A buried direct
    30A buried in enclosure.
    (AS3008 Table 10)

    Max cct length using 80/20 rule for 2.5mm2:
    (These figures DO NOT take volt drop into account, only fault loop impedance, frequently this distance is halved for volt drop. These numbers can be stretched with calculation and checking the upstream impedance)

    Type B 16A MCB = 160M
    Type C 16A MCB = 85M
    Type D 16A MCB = 51M

    Type B 20A MCB = 128M
    Type C 20A MCB = 68M
    Type D 20A MCB = 41M
    (AS3000 Table B1)

    Pheew!

    Go the D curve 16A or try a 20A C curve. I don't think you'll burn the house down with a 20A breaker in the middle of winter. If that doesn't solve it then the AC is stuffed. It is an LG after all!!! Are the caps dodgy and causing a higher inrush current than necessary? Sell them a new install and fit an MHI 7.1kW. I have one with an 10M run on a 16A C curve and no dramas at all, its max current is like 10A on the clamp. Even an MHI 8kW will work on a 16A 2.5mm run, we got confirmation from MHI and did it on a 50M+ run no worries at a school using the old RAC supply. Then you are the hero for saving them a power upgrade and another $250.

    For the last company I worked for I said stuff it and always used 4mm2 + 20A CB for 7kW units, especially fujitsu (warranty), LG and mideas. I wasn't paying for cable but all the other sparkies used 2.5mm and 16A because of stupidity/being tight for the boss.

  21. #21
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: breaker type?

    Yeah it's all different for inverters. Even conventional scrolls are normally fine.
    It's the big old 7kw recips that tend to draw higher current on start up. Normally need a 20A c/b on them.
    Problem was I don't chuck a 20a c/b on an install that someone decided on a 16A c/b, because it might have been for a good reason, ie heavily surrounded by insulation.

  22. #22
    Join Date
    Nov 2009
    Location
    Adelaide, South Australia
    Age
    42
    Posts
    20
    Rep Power
    0

    Re: breaker type?

    How hard is it to trace the cable? In a single story house often its just run in the eaves or on the ceiling lying across the batts near the walls unclipped and you can spend 10 minutes making sure it isn't completely surrounded by insulation. If its run in the wall or a 2 story between floor/ceiling I would just leave it with a 16A CB. The 20A CB can be a quick test to see if a D curve 16A will do the job. Actually the D curve 16A will allow more startup current than the 20A C curve but a 20A C curve is a lot easier to come by cheap.

  23. #23
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: breaker type?

    I'm going to try a d curve 16A, as I can get them cheap from a refrigeration wholesaler anyway.

    Acutally a couple of months ago I had a similar problem when someone replaced a HRC fuse with a c type 20A on a recip. Heaps of nusiance trips. No electrical wholesalers even had a 20a D type or could even get one! Best they could do was 25A.

    I went to a refrigeration wholesaler this time for this LG, and they said no probs, can get 16A and 20A d type easily.

  24. #24
    Join Date
    Nov 2009
    Location
    Adelaide, South Australia
    Age
    42
    Posts
    20
    Rep Power
    0

    Re: breaker type?

    Which wholesaler would that be Paul? Handy for me to know!

  25. #25
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: breaker type?

    Actrol, they have them in their warehouse, had to order it in to the branch, but at least they can get them. after I asked for a couple, they said they'd get a few extra and carry them on the shelf at that branch.
    L&H told me they couldn't even get a 20A D as it's not in their system and their suppliers don't carry them. Advanced electrical and rexel couldn't get them/didn't have them either
    Last edited by paul_h; 05-09-2010 at 04:41 AM.

Similar Threads

  1. Daikin Service CHecker Type III
    By Ben-Hur-Cool in forum Air Conditioning
    Replies: 27
    Last Post: 15-01-2010, 03:53 PM
  2. Flake type ice maker
    By vinod in forum Technical Discussions
    Replies: 0
    Last Post: 25-04-2008, 08:26 AM
  3. New or Old type of Chiller
    By sagittarius in forum Commercial
    Replies: 4
    Last Post: 16-03-2008, 03:10 PM
  4. samsung blows main breaker
    By cross in forum Electrical
    Replies: 1
    Last Post: 16-01-2008, 02:15 AM
  5. Oversize Piston in Open Type Recip. Compressor
    By imranmd in forum Commercial
    Replies: 29
    Last Post: 29-07-2007, 07:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •