    Tick-tick-tick noise while off?



    What causes this noise several minutes after shutdown? I see this on two new systems. Both systems were properly evacuated during installation. I evacuated the second system down to 400 torr and valved it off and watched the gauges. The first system was on outdoor heat pump section only. The second system is all new stuff. It has new equipment all around with new piping from end to end. Brazing was accomplished with a steady flow of inert gas. There are no restrictions in the piping. I used a tubing bender for the bends and joined the lengths to fit neatly with straight couplings. Years ago, would have put a long elbow where pipes went around corners.

    Once the unit shuts off, the outdoor section starts making a tap tap or tick-tick sound a few minutes later. The pressure gauge on the high side reflects this result on the needle. It is as though there is trapped refrigerant somewhere flashing to gas. The vibration is most noticable in the outdoor unit expansion valve.

    This seems to occur when the system has been off a while, maybe three to five minutes. I haven't gotten around to installing the optional crankcase heaters. The will be installed before winter.

    Superheat, subcooling, gauge readings, temperature readings are all on the mark IMHO. One is a fully matched new system with expansion valve. The other is a mismatched system, also with an expansion valve. They are both scroll compressor systems. They are Rheem/Ruud split system gear. One is 1.5 tons and the other is 3.5 tons.

    One system was delivered new nearly empty of refrigerant. I suspected contamination, because the system required 90 percent of a full charge. That is to say, it contained only 10% of the factory supplied refrigerant. I wondered if the service valve had a leak, because the factory had overtightened it. It was really stuck. I worried my hex wrench would snap off in the valve. The second unit balanced to the charging tables to the oz after allowance for the piping length.

    These are R22 systems.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Tick-tick-tick noise while off?

    Maybe scroll running backward until pressure equalize.

  3. #3
    Join Date
    Jun 2006
    Location
    USA
    Posts
    204
    Rep Power
    18

    Re: Tick-tick-tick noise while off?

    This is not the typical Brrbpppttt noise they can make at shut down for a moment. This is a tap tap tap or tink tink tink sound it makes several minutes after shut off. The sound is one to several seconds between knocks. It lasts several minutes more at times. The service gauge pointer jumps with each sound.

  4. #4
    Join Date
    Oct 2008
    Location
    USA
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: Tick-tick-tick noise while off?

    What are your line set sizes, lengths, and amount of 90os.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Tick-tick-tick noise while off?

    Could it be the sound of pipes contracting or expanding?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: Tick-tick-tick noise while off?

    I have noticed a ticking noise on split systems in winter when they have been off for a little while, i believe it is migration of refrigerant but its a pretty subtle sound. it can be pretty loud but never put the guages on to see what was happening.

  7. #7
    Join Date
    Feb 2008
    Location
    QLD
    Age
    53
    Posts
    74
    Rep Power
    17

    Re: Tick-tick-tick noise while off?

    Do both systems use the same style of controll?

    If it is an electronic expansion valve, it might be driven back to a home possition?
    getting ready for restarting
    Last edited by stefs_cruiser; 22-01-2009 at 04:00 AM.

  8. #8
    Join Date
    Mar 2007
    Location
    manchester
    Age
    17
    Posts
    63
    Rep Power
    19

    Re: Tick-tick-tick noise while off?

    maybe your radio needs tuning?>lol

  9. #9
    Join Date
    May 2009
    Location
    uk
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: Tick-tick-tick noise while off?

    daikins have electronic expansion valve clicks back to a diferent position few mins before start up

  10. #10
    Join Date
    Oct 2007
    Location
    ENGLAND
    Posts
    27
    Rep Power
    0

    Re: Tick-tick-tick noise while off?

    i like daikins i could just rub one

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,554
    Rep Power
    26

    Re: Tick-tick-tick noise while off?

    Quote Originally Posted by Larry2 View Post
    This is not the typical Brrbpppttt noise they can make at shut down for a moment. This is a tap tap tap or tink tink tink sound it makes several minutes after shut off. The sound is one to several seconds between knocks. It lasts several minutes more at times. The service gauge pointer jumps with each sound.
    Had a similar problem with a Toshiba(s), it was one with a long indoor coil, the coil would expand and contract, causing the plastic casing to tap, tap the noise travel all the way through the system.
    The basic fault was the screws were to tight hold the coil to the case, we loosened of a bit, all cured (many units)

  12. #12
    Join Date
    Jun 2009
    Location
    Columbus Ohio
    Age
    55
    Posts
    169
    Rep Power
    15

    Re: Tick-tick-tick noise while off?

    if they are electronically controlled, sometimes ive found the computer boards are homing up the EEV, or the reversing valve clocks on and off if the board is reset..
    -Christopher

Similar Threads

  1. Mitsubishi SRK25ZG-S noise
    By paparoulis in forum Air Conditioning
    Replies: 9
    Last Post: 30-11-2009, 07:17 AM
  2. Noise induced hearing loss damages
    By Abe in forum Legal-Business-Marketing
    Replies: 7
    Last Post: 26-05-2008, 10:36 AM
  3. Thumping noise in the compressor
    By Husky250 in forum Air Conditioning
    Replies: 6
    Last Post: 16-05-2008, 10:48 PM
  4. Noise Level
    By Cewek ITS in forum Technical Speculations
    Replies: 4
    Last Post: 20-09-2007, 01:47 AM
  5. noise inverter compressor
    By Airclima in forum Air Conditioning
    Replies: 1
    Last Post: 26-07-2007, 11:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •