Thread: walk-in cooler
-
19-08-2008, 10:17 AM #1
walk-in cooler
need help on r-22 walk-in cooler, new tev,compressor low side 70# high side165# will not take anymore refrigerant. low side is cold to touch &sweaty high side is slightly hot. can see refrigerant flashing. please help
-
19-08-2008, 11:09 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: walk-in cooler
What is evaporator air in and air out temperature when you measured this pressures?
What is condenser type (water,air?)?
What are condenser water/air in and out temperatures?
What are evaporator and total superheat and condenser subcooling readings?
What is discharge pipe temperature?
Why are you changed TEV?
Did you changed factory setting of TEV?
-
19-08-2008, 11:03 PM #3
Re: walk-in cooler
Is the room down to temperature yet?
Pressures need to be related to temperature to be of any use.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
19-08-2008, 11:43 PM #4
Re: walk-in cooler
the cooler never came down in temp. i'm afraid the tev maybe sized wrong. this is an air condenser unit. i will take temps on evaporator&condenser along withpiping temps. thanks brian
-
20-08-2008, 02:16 AM #5
Re: walk-in cooler
If all who ask for answers to problems associated with the refrigeration portion of a system would give us the following information I believe our answers would be better able to help them so in the future why don't we insist on the following readings
Discharge Pressure
Suction Pressure
Discharge Temperature
Superheat at compressor
Super heat at Evaporator
Sub cooling
Amp Reading
Tonnage(BTU, KW)
Now we have something to work with!
-
21-08-2008, 12:03 AM #6
Re: walk-in cooler
We keep trying Wambat, but it is a head against brick wall exercise I'm afraid
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-08-2008, 06:36 AM #7
Re: walk-in cooler
Why can't the site post these instructions on the home page and refer the client to them when posting? It seems to me that it would be a win-win situation for us and for the posters. This is a minimum of what they should be checking before asking for help. If the clients were given guidelines I believe we could do a better job in helping them
It's worth a try
-
21-08-2008, 07:43 AM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
-
08-03-2011, 07:27 AM #9
Re: walk-in cooler
I agree we should have those as email signatures
-
08-03-2011, 10:51 AM #10
Similar Threads
-
Leak in Leer Walk in cooler
By bulldawg 74 in forum Trouble ShootingReplies: 2Last Post: 04-06-2008, 01:20 AM -
TXV hunting in a walkin cooler
By dkemper in forum Trouble ShootingReplies: 9Last Post: 15-11-2007, 04:14 PM -
walk in cooler evaperator keeps freezing up
By ewart in forum Trouble ShootingReplies: 21Last Post: 30-07-2007, 09:30 PM -
walk in cooler EVAPORATOR coil icing up
By kurt854 in forum FundamentalsReplies: 5Last Post: 14-06-2007, 07:28 PM -
Walk in Cooler (short cycling)
By Brandon in forum Trouble ShootingReplies: 11Last Post: 05-05-2003, 11:43 AM