    refrigerant design cappacities



    Hi all

    Does anybody know or have got a conversion factor for R22 against R404A

    I need to select a unit to operate on R22 (Existing equipment)but all the manufacturers now only list there capacities in R404A, is there a percentage adjustment that i can use to get the R22 equiverlant????

    I need approx 43kw,

    Cheers
    CB



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: refrigerant design cappacities

    Quote Originally Posted by chillyblue View Post
    Hi all

    Does anybody know or have got a conversion factor for R22 against R404A

    I need to select a unit to operate on R22 (Existing equipment)but all the manufacturers now only list there capacities in R404A, is there a percentage adjustment that i can use to get the R22 equiverlant????

    I need approx 43kw,

    Cheers
    CB

  3. #3
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: refrigerant design cappacities

    Thanks Nike

    Thats not quite what i needed.

    example if the manufacturer list the product as capable of 43kw on R404A with a 6 dt
    What would that same product do on R22 would it be the same or would it be less than or more than 43kw???

    Cheers for your help
    CB

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Quote Originally Posted by chillyblue View Post
    Thanks Nike

    Thats not quite what i needed.

    example if the manufacturer list the product as capable of 43kw on R404A with a 6 dt
    What would that same product do on R22 would it be the same or would it be less than or more than 43kw???

    Cheers for your help
    CB
    What you exactly mean by "product"?

    This is correction factor for ECO evaporators whose nominal capacity is given for R22. If you want correction coefficient for R22 for evaporator whose nominal capacity is given for R404A simply multiply given nominal capacity with 1/X where X is coefficient from this table.

    Example:Evaporator for R404A at standard evaporation temperature SC2 of -8°C and dt 8K and RH of 85% has nominal capacity 43 kW
    What is his capacity with R22 gas at -10°C room temperature and dt6K?
    Solution:
    43kW x (1/0,714)= 43x1,4=62kW


    If you mean other product then evaporator, then I don't see purpose of that conversion from R404A back to "forbidden" R22.
    Last edited by nike123; 20-08-2008 at 08:39 AM.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Best Refrigerant for New Design
    By Andreas11 in forum Refrigerants
    Replies: 9
    Last Post: 05-09-2010, 09:30 AM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •