18-08-2008, 07:33 PM #1
Problem with chiller
HI
I have a problem with 4compressor unit(2 tandem unit)-
Because comp1 and comp3 burn out we replaced them with new comp,also oil has been changed and filter driers too.
When start up was done I tried to close the both txv valves because my suction pressure was 7 bar (also head temp was very high) and I still had a lot of bubbles on glass, but the pressure did not fall.
The condenser is OK also the fan motors.
The refrigerant is R407C, Dt 4,5C and head temp now is 110C
It would be a disaster if the new comps would burn out again.
ANY CLUES
Thanks
-
18-08-2008, 07:51 PM #2
Re: Problem with chiller
whats it running on ?high or low temp cold room????or what?
-
19-08-2008, 07:42 AM #3
Re: Problem with chiller
looks like you got a lot of air in system .decant it .vac it and then regas
-
19-08-2008, 01:05 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Problem with chiller
What serves this unit?
What is evaporator air/water inlet temperature? What is evaporator type?
What is condenser air/water inlet/outlet temperature?
Bubbles on sight-glass with R407 is common thing, what is subcooling at TEV inlet and condenser outlet?
What is superheat now after adjustment of TEV's? Did you checked, opened and cleaned TEV's after burn-out?
Dt 4,5C
Also, what you mean by "head temp"?Last edited by nike123; 19-08-2008 at 06:23 PM.
-
19-08-2008, 04:59 PM #5
Re: Problem with chiller
1. as Tony said >>>> AIR.
2. replace the 407, its no good for nothing.
-
19-08-2008, 08:43 PM #6
Re: Problem with chiller
HI guys
This is common water chiller
Dt is delta evaporator inlet/outlet temp
Head temp is temperature on top of the compressor (head)
SSH is 9C
But the compressors are still sweating
But we didnt do the cleaning the txv(will do that
And I am 200% sure there is no air inside, pressure test was OK and vacuum was OK
About the bubbles I know there should be some due to high outside temp. but there is to many bubbles
-
19-08-2008, 09:02 PM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Few more answers expected!
What is evaporator water inlet temperature?
What is condenser air/water inlet/outlet temperature?
What is subcooling at TEV inlet and condenser outlet?
Also, did you charged new virgin refrigerant?
Did you charged by weight?
I see 4 possible causes of elevated suction and discharge pressures (if that is case here, but we don't have discharge pressure and condenser TD to confirm that):
1. Noncondensables
2. Overcharge
3. Faulty TXV
4. High load
Which one, or maybe it is combination, we will only know when you provide all necessary measurements and answers.Last edited by nike123; 20-08-2008 at 09:00 AM.
-
19-08-2008, 09:56 PM #8
Re: Problem with chiller
sounds like air to me.
or some bad combustion products from the burn out, pull the gas, oil, filters and replace everything.
fit high cap burn out driers and replace again soon after.
-
20-08-2008, 08:06 AM #9
Re: Problem with chiller
If all the above were checked and problem still there check these - Blocked drier, did you put in a suction line filter for clean up, if so remove it, if not check suction strainer at compressor. If welded connection on discharge - is there a restriction ( I've seen the tube close on discharge from no expansion fitting used ). I'm sure a IR thermo would help located problem area
-
26-08-2008, 01:37 PM #10
Re: Problem with chiller
Hi
We will fit in a new TXV because the compressors burned out after 166 hours of work, so we suspect that the TXV is too large(factory mistake) or even not good from the start.
-
27-08-2008, 01:00 AM #11
Re: Problem with chiller
If I understand you correctly, this is an air cooled water chiller. Is that correct?
For a proper evaluation, we need the following information:
Low side:
Evap water in temp
Evap water out temp
Saturated suction temp
Suction line temp at evap outlet
High side:
Cond air in temp
Cond air out temp
Saturated condensing temp
Liquid line temp at receiver outlet
-
28-08-2008, 06:36 PM #12
Re: Problem with chiller
About the bubbles I know there should be some due to high outside temp. but there is to many bubbles
bubles dont always mean " air" , can be flasch gas.
is the amount of gas sufficient, is it as the constructor recomends?
if you are sure of the rest, vacuum ok , filters ok ,no leaks, check the refrig by the book, take note's and check the engine.
Ice
Similar Threads
-
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
York YK Chiller Problem
By icebox in forum Refrigeration BooksReplies: 13Last Post: 01-07-2008, 06:05 PM -
Help to solve problem on York chiller
By nassersh in forum Trouble ShootingReplies: 7Last Post: 03-06-2008, 08:38 PM -
York Chiller Excessive Purges Problem
By imranmd in forum CommercialReplies: 5Last Post: 07-03-2008, 05:13 AM -
R11 Centrifugal Chiller Oil Problem
By iceman007 in forum Trouble ShootingReplies: 8Last Post: 17-02-2008, 02:14 AM