    Problem with chiller



    HI
    I have a problem with 4compressor unit(2 tandem unit)-
    Because comp1 and comp3 burn out we replaced them with new comp,also oil has been changed and filter driers too.
    When start up was done I tried to close the both txv valves because my suction pressure was 7 bar (also head temp was very high) and I still had a lot of bubbles on glass, but the pressure did not fall.
    The condenser is OK also the fan motors.
    The refrigerant is R407C, Dt 4,5C and head temp now is 110C
    It would be a disaster if the new comps would burn out again.

    ANY CLUES

    Thanks



  2. #2
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Problem with chiller

    whats it running on ?high or low temp cold room????or what?

  3. #3
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Problem with chiller

    looks like you got a lot of air in system .decant it .vac it and then regas

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Problem with chiller

    Quote Originally Posted by jure View Post
    HI
    I have a problem with 4compressor unit(2 tandem unit)-
    Because comp1 and comp3 burn out we replaced them with new comp,also oil has been changed and filter driers too.
    When start up was done I tried to close the both txv valves because my suction pressure was 7 bar (also head temp was very high) and I still had a lot of bubbles on glass, but the pressure did not fall.
    The condenser is OK also the fan motors.
    The refrigerant is R407C, Dt 4,5C and head temp now is 110C
    It would be a disaster if the new comps would burn out again.

    ANY CLUES

    Thanks
    What serves this unit?
    What is evaporator air/water inlet temperature? What is evaporator type?
    What is condenser air/water inlet/outlet temperature?

    Bubbles on sight-glass with R407 is common thing, what is subcooling at TEV inlet and condenser outlet?

    What is superheat now after adjustment of TEV's? Did you checked, opened and cleaned TEV's after burn-out?

    Dt 4,5C
    What you mean by that?
    Also, what you mean by "head temp"?
    Last edited by nike123; 19-08-2008 at 06:23 PM.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Problem with chiller

    1. as Tony said >>>> AIR.

    2. replace the 407, its no good for nothing.

  6. #6
    Join Date
    Apr 2008
    Location
    LJUBLJANA
    Age
    42
    Posts
    28
    Rep Power
    0

    Re: Problem with chiller

    HI guys

    This is common water chiller
    Dt is delta evaporator inlet/outlet temp
    Head temp is temperature on top of the compressor (head)
    SSH is 9C
    But the compressors are still sweating
    But we didnt do the cleaning the txv(will do that
    And I am 200% sure there is no air inside, pressure test was OK and vacuum was OK
    About the bubbles I know there should be some due to high outside temp. but there is to many bubbles

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36
    Quote Originally Posted by jure View Post
    HI guys

    This is common water chiller
    Dt is delta evaporator inlet/outlet temp
    Head temp is temperature on top of the compressor (head)
    SSH is 9C
    But the compressors are still sweating
    But we didnt do the cleaning the txv(will do that
    And I am 200% sure there is no air inside, pressure test was OK and vacuum was OK
    About the bubbles I know there should be some due to high outside temp. but there is to many bubbles
    Few more answers expected!

    What is evaporator water inlet temperature?
    What is condenser air/water inlet/outlet temperature?
    What is subcooling at TEV inlet and condenser outlet?
    What is condensation pressure?
    Also, did you charged new virgin refrigerant?
    Did you charged by weight?

    I see 4 possible causes of elevated suction and discharge pressures (if that is case here, but we don't have discharge pressure and condenser TD to confirm that):
    1. Noncondensables
    2. Overcharge
    3. Faulty TXV
    4. High load

    Which one, or maybe it is combination, we will only know when you provide all necessary measurements and answers.
    Last edited by nike123; 20-08-2008 at 09:00 AM.

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: Problem with chiller

    sounds like air to me.

    or some bad combustion products from the burn out, pull the gas, oil, filters and replace everything.
    fit high cap burn out driers and replace again soon after.

  9. #9
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Problem with chiller

    If all the above were checked and problem still there check these - Blocked drier, did you put in a suction line filter for clean up, if so remove it, if not check suction strainer at compressor. If welded connection on discharge - is there a restriction ( I've seen the tube close on discharge from no expansion fitting used ). I'm sure a IR thermo would help located problem area

  10. #10
    Join Date
    Apr 2008
    Location
    LJUBLJANA
    Age
    42
    Posts
    28
    Rep Power
    0

    Re: Problem with chiller

    Hi
    We will fit in a new TXV because the compressors burned out after 166 hours of work, so we suspect that the TXV is too large(factory mistake) or even not good from the start.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Problem with chiller

    If I understand you correctly, this is an air cooled water chiller. Is that correct?

    For a proper evaluation, we need the following information:

    Low side:

    Evap water in temp
    Evap water out temp
    Saturated suction temp
    Suction line temp at evap outlet

    High side:

    Cond air in temp
    Cond air out temp
    Saturated condensing temp
    Liquid line temp at receiver outlet

  12. #12
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Problem with chiller

    About the bubbles I know there should be some due to high outside temp. but there is to many bubbles

    bubles dont always mean " air" , can be flasch gas.

    is the amount of gas sufficient, is it as the constructor recomends?

    if you are sure of the rest, vacuum ok , filters ok ,no leaks, check the refrig by the book, take note's and check the engine.

    Ice

Similar Threads

  1. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  2. York YK Chiller Problem
    By icebox in forum Refrigeration Books
    Replies: 13
    Last Post: 01-07-2008, 06:05 PM
  3. Help to solve problem on York chiller
    By nassersh in forum Trouble Shooting
    Replies: 7
    Last Post: 03-06-2008, 08:38 PM
  4. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM
  5. R11 Centrifugal Chiller Oil Problem
    By iceman007 in forum Trouble Shooting
    Replies: 8
    Last Post: 17-02-2008, 02:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •