    Copeland Scrolls going to earth



    Evening all,

    Dont have specifics so bare with me but has anyone else had problems with NEW copeland scrolls going to earth. One of my collegues has fitted 2 in the last week and both have gone down, going straight to earth after a couple of days. System has all the usual protection devises, pressure switches, overloads, timers set a 2 mins, system clean so genuinely think its a fault with the compressors.

    Anyone else had a problem.

    Regards

    Fatboy

    Update:- The engineer has just texted me, the compressor is a ZS56K4E
    Last edited by Latte; 02-08-2008 at 12:37 AM. Reason: Updated info



  2. #2
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Copeland Scrolls going to earth

    Have they got phase rotation devices?

    Multisync
    London

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Copeland Scrolls going to earth

    Not as far as i am aware, although i am going to site on monday with another compressor to have a look.
    From what i am being told and from memory when i last went there for another job its a fairly basic condensing unit feeding 2 remote multidecks that are individually conttrolled hence the timer. What is youre thinking, they are running the wrong way or phase device running it the wrong way

    Regards

    Fatboy

  4. #4
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Copeland Scrolls going to earth

    rdocwra,

    Here's a link to Copelands AE bulletins. Check out Section 4, bulletin 4-1299. There's good information here that might help you out.


    http://www.hvacrinfo.com/ae_index.htm

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland Scrolls going to earth

    Hi, Rdocwra

    Does these compressors are part of newly installed system, or they are installed after original compressors are burned-out?

  6. #6
    Nik BG's Avatar
    Nik BG Guest

    Re: Copeland Scrolls going to earth

    Hi, Rdocwra
    I guess this compressor works on 380V! One reason this problem could appear is working long time on low voltage. That happened to me couple of times. Normaly on the machines i install a phase control/low voltage device to protect compressors

  7. #7
    Join Date
    Feb 2008
    Location
    Wellingborough
    Age
    56
    Posts
    35
    Rep Power
    0

    Re: Copeland Scrolls going to earth

    Regarding the going the wrong way idea, you would know if they were as they don't pump correctly & they make a terrible 'bag of bolts' type of noise!

    Trust me, once heard, never forgotten!

  8. #8
    Join Date
    Apr 2008
    Location
    LJUBLJANA
    Age
    42
    Posts
    28
    Rep Power
    0

    Re: Copeland Scrolls going to earth

    Did anyone check the amps after the change out

Similar Threads

  1. newbie earth bonding
    By dave_k in forum Electrical
    Replies: 10
    Last Post: 06-05-2008, 12:37 AM
  2. Earth faults
    By reggie in forum Technical Speculations
    Replies: 17
    Last Post: 28-01-2006, 06:22 PM
  3. Earth tapped transformers
    By phil68 in forum Fundamentals
    Replies: 6
    Last Post: 04-01-2006, 09:32 PM
  4. Earth continuity
    By bernard in forum Electrical
    Replies: 3
    Last Post: 04-04-2005, 06:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •