Thread: Copeland Scrolls going to earth
-
01-08-2008, 08:37 PM #1
Copeland Scrolls going to earth
Evening all,
Dont have specifics so bare with me but has anyone else had problems with NEW copeland scrolls going to earth. One of my collegues has fitted 2 in the last week and both have gone down, going straight to earth after a couple of days. System has all the usual protection devises, pressure switches, overloads, timers set a 2 mins, system clean so genuinely think its a fault with the compressors.
Anyone else had a problem.
Regards
Fatboy
Update:- The engineer has just texted me, the compressor is a ZS56K4ELast edited by Latte; 02-08-2008 at 12:37 AM. Reason: Updated info
-
01-08-2008, 09:57 PM #2
Re: Copeland Scrolls going to earth
Have they got phase rotation devices?
Multisync
London
-
01-08-2008, 10:05 PM #3
Re: Copeland Scrolls going to earth
Not as far as i am aware, although i am going to site on monday with another compressor to have a look.
From what i am being told and from memory when i last went there for another job its a fairly basic condensing unit feeding 2 remote multidecks that are individually conttrolled hence the timer. What is youre thinking, they are running the wrong way or phase device running it the wrong way
Regards
Fatboy
-
02-08-2008, 02:44 PM #4
Re: Copeland Scrolls going to earth
rdocwra,
Here's a link to Copelands AE bulletins. Check out Section 4, bulletin 4-1299. There's good information here that might help you out.
http://www.hvacrinfo.com/ae_index.htm
-
04-08-2008, 07:30 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Copeland Scrolls going to earth
Hi, Rdocwra
Does these compressors are part of newly installed system, or they are installed after original compressors are burned-out?
-
06-08-2008, 01:21 PM #6
Re: Copeland Scrolls going to earth
Hi, Rdocwra
I guess this compressor works on 380V! One reason this problem could appear is working long time on low voltage. That happened to me couple of times. Normaly on the machines i install a phase control/low voltage device to protect compressors
-
12-08-2008, 03:41 PM #7
Re: Copeland Scrolls going to earth
Regarding the going the wrong way idea, you would know if they were as they don't pump correctly & they make a terrible 'bag of bolts' type of noise!
Trust me, once heard, never forgotten!
-
19-08-2008, 09:08 PM #8
Re: Copeland Scrolls going to earth
Did anyone check the amps after the change out
Similar Threads
-
newbie earth bonding
By dave_k in forum ElectricalReplies: 10Last Post: 06-05-2008, 12:37 AM -
Earth faults
By reggie in forum Technical SpeculationsReplies: 17Last Post: 28-01-2006, 06:22 PM -
Earth tapped transformers
By phil68 in forum FundamentalsReplies: 6Last Post: 04-01-2006, 09:32 PM -
Earth continuity
By bernard in forum ElectricalReplies: 3Last Post: 04-04-2005, 06:35 PM