Best sealant for pipe threads holding a vacuum
What is a good substance to seal pipe threads with when connecting a vacuum pump to a system? I tried Teflon tape and I still have a leak. Should I use regular pipe thread putty? Should I just keep tightening the brass to steel fitting? Something else?
Thanks,
OC
-
15-08-2008, 06:31 PM #2
Re: Best sealant for pipe threads holding a vacuum
Hi OC.
Provided the pipe thread is a tapered type or a compression style fitting.
Then I have found LEAKSTOP perfectly good.
BUT it does work on the principle that the paste (blue) is subjected to compression forces.
Hence the reference to the thread being tapered.
With a parallel thread then ptfe should be fine?
Just wrap more passes around the threads!
In the past I have used a soft putty compound around a leaking Shaft Seal to allow a 12hr Vacuum test. H.M. Navy requirement.
Cheers Steve.
Cheers GRIZZLY
-
15-08-2008, 07:16 PM #3
Re: Best sealant for pipe threads holding a vacuum
What is actually sealing between the brass connection and any port on the system is the rubber that seats in side the brass connector, if it is too short or damaged, you will have a leak.
-
15-08-2008, 08:14 PM #4
Re: Best sealant for pipe threads holding a vacuum
The vacuum pump port is just a straight piece of brass pipe with a 134A fitting and a ***** 12 fitting at one end and threads at the other end. No flange for any kind of gasket, just a threaded hole in the steel block at the vacuum pump that the port screws into.
Kep
-
15-08-2008, 10:07 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Best sealant for pipe threads holding a vacuum
If you want to use it where you don't need to dismantle joint frequently, like in your case, then use Loctite 569
-
15-08-2008, 11:25 PM #6
Re: Best sealant for pipe threads holding a vacuum
Do not use Teflon Tape for anything on refrigeration! The manufactures specify that their product is designed for 'lubrication only' not a sealant. I have done numerous repairs on leaking threaded systems and have found that the ' blue stuff ' just doesn't seal. The Loctite 567 is good for smaller fittings and anything over 3/8" you should use Loctite 271.
Just my 2 cents - it's free!
Similar Threads
-
Troubleshooting a vacuum pump and gauge set.
By Old Codger in forum FundamentalsReplies: 7Last Post: 08-08-2008, 05:13 PM -
Compressors start under vacuum
By narkom in forum FundamentalsReplies: 16Last Post: 22-02-2008, 09:13 PM -
inverters pulling vacuum
By bangoman in forum Air ConditioningReplies: 2Last Post: 05-02-2008, 09:12 PM -
vacuum timeline
By phicks1065 in forum CommercialReplies: 11Last Post: 12-01-2008, 10:10 PM -
Vacuum test
By Peter_1 in forum FundamentalsReplies: 15Last Post: 13-10-2006, 09:04 PM