    Unhappy Heat pump problem



    Hi all.

    i am currently working on a 30Kw cooling capacity email/york package aircon unit and was hoping that someone might be able to confirm my speculation as to what is wrong with it.

    When operating on cooling the unit operates fine but when switched over to heating mode I am getting very low suction pressures and high discharge pressures the line from the outdoor unit TX Valve also ices up from the TX. When i wind the TX valve all the way out the suction pressure increases momentarily and then drops back down....If i wind the TX all the way in the system pulls a vaccum

    All filter and coils are clean....I am speculating that the TX valve on the outside unit may be duff.....??

    Thoughts?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat pump problem

    Quote Originally Posted by Darc View Post
    Hi all.

    i am currently working on a 30Kw cooling capacity email/york package aircon unit and was hoping that someone might be able to confirm my speculation as to what is wrong with it.

    When operating on cooling the unit operates fine but when switched over to heating mode I am getting very low suction pressures and high discharge pressures the line from the outdoor unit TX Valve also ices up from the TX. When i wind the TX valve all the way out the suction pressure increases momentarily and then drops back down....If i wind the TX all the way in the system pulls a vaccum

    All filter and coils are clean....I am speculating that the TX valve on the outside unit may be duff.....??

    Thoughts?
    Check this thread!

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Heat pump problem

    It sounds like a typical fault with the reversing valve not changing over.

    Check temperatures across the valve in both modes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jan 2007
    Location
    Perth ,Western Australia
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Heat pump problem

    Thanks for the relies so far guys!

    I dont believe that it is the reversing valve as the unit changes over from heat to cool and there was no temp diff across the reversing valve....

    Thanks for the link to the TX valve discussion too! I have been reading through the posts and there is definetly some good info in there....

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat pump problem

    Do you have sight glass in front of heating txv? Is it full? Is the line in front of TXV warm or mild to tuch? If yes, than check your heating txv power element correct functioning!

    This is from another forum (hvacprotech):
    Checking the Power Element of a TXV

    Refrigeration systems which are operating with a higher than normal evaporator superheat value can be the result of several system problems. On systems using a thermostatic expansion valve (TXV) as the metering device, one cause could be a loss of charge in the bulb of the TXV. This is due to the fact that the refrigerant charge in the bulb of the power assembly is the opening force of the TXV. When a loss of charge exists in this bulb there is not enough force to throttle the valve open to its correct position.



    The following procedure can be used to see if loss of charge in the bulb of a TXV is the cause of a higher than normal evaporator superheat:

    On a valve with an external superheat adjustment, turn the adjustment nut to the full counterclockwise position. Verify that the evaporator's superheat is still too high before proceeding to the next step. If the evaporator's superheat has changed to a much lower value, try adjusting the valve to obtain the correct superheat value for the system.

    Remove the bulb from the suction line and hold it in your hand for several minutes to warm it up. Observe the suction pressure. If the valve has a refrigerant charge, you should see an increase in the suction pressure.

    If no change in the pressure occurs, it is reasonable to conclude the assembly has lost its refrigerant charge and needs to be replaced.

    Some TXVs have a removable power assembly which can be replaced instead of changing the entire TXV. If the power assembly can be removed, the bulb charge can also be checked by trying to depress the diaphragm with your thumb. You should not be able to depress this by hand. If you can, the assembly has lost its charge.
    Last edited by nike123; 16-08-2008 at 07:19 AM.

  6. #6
    Join Date
    Jan 2007
    Location
    Perth ,Western Australia
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Heat pump problem

    Turns out it was the Power Element after all. Thanks everyone for your responses.

Similar Threads

  1. heat pump to boil water
    By Lc_shi in forum New Technologies
    Replies: 36
    Last Post: 15-09-2010, 09:04 PM
  2. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  3. geothermal heat pump
    By goodguy in forum Heat Pumps
    Replies: 18
    Last Post: 06-02-2008, 10:30 PM
  4. bath room reclaim heat pump
    By Lc_shi in forum Heat Pumps
    Replies: 2
    Last Post: 19-11-2007, 08:59 PM
  5. sewage heat pump
    By Lc_shi in forum New Technologies
    Replies: 3
    Last Post: 03-11-2007, 11:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •