Denco Johnson control
Hi I have Been trying to work something out in my head for a while but am unsure as to the correct action.
I was looking at an old Denco unit it had tripped out on the duel Johnson control low pressure due to a lack of R22 ref.
My question is this I put a set of gauges on but although some psig was present standing, I could not get the relay to reset, I did attempt to engage it,this ran the compressor for a fraction but as I let go it stopped and the relay popped again. Would I have had to Isolate the system take out the Refrigerant, take care of the leaks and then try and secure the relay with new virgin refrigerant in place. Would the Johnson control allow this or would some attention be needed to the low pressure control.
Regards
Sparrow
Always easy on the eye.
-
13-08-2008, 09:16 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Denco Johnson control
Could you set low pressure control to lowest setting and try if it holds. Also make differential as high as possible to check this because, cut out is cut in minus differential.
P.S. Before any action, note current pressure settings, to be able later set these again as they were.Last edited by nike123; 13-08-2008 at 09:20 PM.
-
13-08-2008, 11:05 PM #3
Re: Denco Johnson control
Surely this indicates that the LP control is working correctly.
Low pressure in system and the pressure switch is preventing the compressor from running.
You will have to recover the refrigerant anyway so that you can find/fix the leak.
When you recharge the system the LP switch will be reset automatically as the pressure rises.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
14-08-2008, 09:07 AM #4
Re: Denco Johnson control
Ok that makes sense, Thanks Nike 123 , Brian.
Sparrow.Always easy on the eye.
-
13-04-2010, 10:26 AM #5
Re: Denco Johnson control
On any denco units we have a LP delay timer, this is fitted to prevent unnecessary trips when the unit is starting in cold ambients, if the unit trips off straight away when you start up from isolation i would suggest that the timer has not been set up or has been bypassed.
Similar Threads
-
Denco Close Control Units
By Freecool in forum Air ConditioningReplies: 12Last Post: 05-05-2010, 12:50 PM -
Airwell Florida Inverter Air Condition - in need of help
By AndY1 in forum Air ConditioningReplies: 21Last Post: 05-07-2008, 10:48 AM -
Frick Quantum LX Compressor control panel: Capacity Control Screen
By screw_geek in forum Industrial CompressorsReplies: 17Last Post: 15-06-2008, 06:47 AM -
Control scenario
By Mike Hopkins in forum Technical DiscussionsReplies: 5Last Post: 14-09-2007, 11:25 AM -
New Capacity Control Solution
By embrown in forum New TechnologiesReplies: 19Last Post: 30-12-2003, 01:33 PM