    Unhappy valve plate failure



    taken over system with 2 semiherm units working freezer @-25 c one system works perfect, other system discharge valve fails or in the past compressor has broken a piston .
    system on r404a tev s/heat 5c suction press 35psig disc press 190 any suggestions



  2. #2
    Join Date
    Jun 2004
    Location
    wales
    Age
    53
    Posts
    25
    Rep Power
    0

    Re: valve plate failure

    you say it has two units but does it have one or two evaps?

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: valve plate failure

    superheat too high for a freezer, should be maximum 3C

    at 5C superheat you are most likely to get liquid in your suction line,.

    chemi

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: valve plate failure

    Is there any way that refrigerant can condense nearby in the discharge line or in the valve assembly, say on the off cycle, or syphon back when the unit is off? If this happens when the head is cold, a tiny amount of liquid can cauase a trnendous amout of damage.

    This may happen if your unit is working as a lag system. Because the lead unit works most of the time, the conditions for liquid settlement don't exist.

    It's not unknown in the UK. I have found it in the past where hydraulic damage is caused in the top end of the piston assembly and in the muffler that may be right in front of it.

    If you have air cooled condensers sitting above the unit, have a look for check valves to prevent liquid settling at the lowest point by gravity.
    ________
    C77
    Last edited by Argus; 07-02-2011 at 08:05 AM.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: valve plate failure

    at 5C superheat you are most likely to get liquid in your suction line,.
    How is that Chemi?

    Any superheat above boiling point surely means that the liquid is now certainly a vapour? am I missing something?

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: valve plate failure

    of course you right argus.

    NRV after discharge valve will protect it from liquid migrating back.

    also good design of discharge piping can do wonders.

    chemi

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: valve plate failure

    hi frank,

    I was talking about a freezer. in AC its fine.

    chemi

Similar Threads

  1. Diagnosing valve plate problems
    By Dan in forum The Trail of Tears
    Replies: 36
    Last Post: 16-10-2009, 10:37 AM
  2. Close call (eye opener)
    By Tycho in forum Industrial
    Replies: 42
    Last Post: 17-03-2006, 07:33 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •