Results 1 to 8 of 8
Thread: Pump Down Procedure
-
10-08-2008, 05:37 AM #1
Pump Down Procedure
Hello: While servicing low pressure side, I saw a machanic using pump down procedure as follows. 1. Closed HP valve on the discharge side of compressor
2. Unit was kept running for short while, with suction side valve open unit suction side pressure came down to 30psi (low pressure trip was set at 26psi). 3.Unit was stopped and Low pressure valve was closed after that. This way, he would collect refrigerant into condenser unit and thereafter he would work on the evaporator.
I just want to know is this a correct procedure, is there any gereral pump down procedure besides this.
Best regards
-
10-08-2008, 05:45 AM #2
-
10-08-2008, 01:13 PM #3
Re: Pump Down Procedure
it can be done this way,but make sure to come in the vacuum, watch the manifolds closely. if you want to do it that way, do it via the relays by manual command,otherwise when you start the system whit the indoor command its take to long before you can stop the system and may possible damage the compressor.
when its not possible work whit a walkie talkie and a extra pair of hands , and ears.
Ice
-
10-08-2008, 01:22 PM #4
Re: Pump Down Procedure
O, bey the way, you olso can invest in a recuparation device ( 1000,-€ ), an empty bottle , and a refrig scale (450,-€)
than you can work on the complete system whitout los of oil and refrig.
change the compressor oil, purge the tubes and clean them, install burn out filters, ......and so on.
think about it
Ice
-
10-08-2008, 09:32 PM #5
Re: Pump Down Procedure
there is something amiss if you close the discharge on the compressor it should cut out on hp strait away
-
11-08-2008, 08:00 PM #6
Re: Pump Down Procedure
therefore we have Small screwdrivers,ho block the spring for doing so .
Ice
-
17-08-2008, 03:54 PM #7
Re: Pump Down Procedure
Hi,
you shoud be close the liquid resevaer valve (don't closed HP servece valve is v.dangeres )then operate the Compressor until suction presuer drop to 10PSI and then closed the suction servece valve.
Remark the low presure switch shoud be cancel.
Many Thanks.
-
19-08-2008, 11:09 AM #8
Re: Pump Down Procedure
TRY THIS ONE
[EX.1 IF YOU HAVE A LIQUID RECIEVER]
-first the unit must be operating
-do not close the high side service valve of the compressor.
-first close the access valve in the liquid reciever going to the evaporator..
-watch the pressure, then close the access valve in the reciever from the high side of the compressor "not the high side service valve of the compressor"
-all the liquid refrigerant go to your reciever
[EX.2 IF YOU DONT HAVE RECIEVER, BUT YOU CAN DO ONLY IN SPLIT A/C SYSTEM]
-first the unit must be operating
-close the discharge valve of the condensing unit
-watch the pressure, then close the suction valve in the condensing unit.. all the refrigerant is now in the condensing unit..With great power Comes Great Responsibility
Similar Threads
-
liquid ammonia pump calvitation
By Kathleen in forum Trouble ShootingReplies: 23Last Post: 20-05-2011, 02:18 AM -
Help with condensor pump
By Bakerbj in forum Air ConditioningReplies: 23Last Post: 14-06-2009, 12:39 AM -
Troubleshooting a vacuum pump and gauge set.
By Old Codger in forum FundamentalsReplies: 7Last Post: 08-08-2008, 05:13 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
SL/SB-400 Pump Down Procedures
By absolute-zero in forum TransportReplies: 1Last Post: 29-01-2008, 09:27 PM