    Pump Down Procedure



    Hello: While servicing low pressure side, I saw a machanic using pump down procedure as follows. 1. Closed HP valve on the discharge side of compressor
    2. Unit was kept running for short while, with suction side valve open unit suction side pressure came down to 30psi (low pressure trip was set at 26psi). 3.Unit was stopped and Low pressure valve was closed after that. This way, he would collect refrigerant into condenser unit and thereafter he would work on the evaporator.
    I just want to know is this a correct procedure, is there any gereral pump down procedure besides this.
    Best regards



  2. #2
    Join Date
    Jul 2006
    Location
    New Zealand
    Age
    77
    Posts
    65
    Rep Power
    18

    Re: Pump Down Procedure

    Quote Originally Posted by hamidpia View Post
    Hello: While servicing low pressure side, I saw a machanic using pump down procedure as follows. 1. Closed HP valve on the discharge side of compressor
    2. Unit was kept running for short while, with suction side valve open unit suction side pressure came down to 30psi (low pressure trip was set at 26psi). 3.Unit was stopped and Low pressure valve was closed after that. This way, he would collect refrigerant into condenser unit and thereafter he would work on the evaporator.
    I just want to know is this a correct procedure, is there any gereral pump down procedure besides this.
    Best regards
    I assume the HP valve you refer to is the outlet valve on the liquid receiver, not the discharge service valve on the compressor?

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Pump Down Procedure

    it can be done this way,but make sure to come in the vacuum, watch the manifolds closely. if you want to do it that way, do it via the relays by manual command,otherwise when you start the system whit the indoor command its take to long before you can stop the system and may possible damage the compressor.

    when its not possible work whit a walkie talkie and a extra pair of hands , and ears.

    Ice

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Pump Down Procedure

    O, bey the way, you olso can invest in a recuparation device ( 1000,-€ ), an empty bottle , and a refrig scale (450,-€)
    than you can work on the complete system whitout los of oil and refrig.
    change the compressor oil, purge the tubes and clean them, install burn out filters, ......and so on.

    think about it

    Ice

  5. #5
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Pump Down Procedure

    there is something amiss if you close the discharge on the compressor it should cut out on hp strait away

  6. #6
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Pump Down Procedure

    therefore we have Small screwdrivers,ho block the spring for doing so .

    Ice

  7. #7
    Join Date
    Aug 2008
    Location
    Iraq
    Age
    54
    Posts
    23
    Rep Power
    0

    Re: Pump Down Procedure

    Hi,
    you shoud be close the liquid resevaer valve (don't closed HP servece valve is v.dangeres )then operate the Compressor until suction presuer drop to 10PSI and then closed the suction servece valve.
    Remark the low presure switch shoud be cancel.
    Many Thanks.

  8. #8
    Join Date
    Apr 2008
    Location
    philippines
    Posts
    95
    Rep Power
    17

    Re: Pump Down Procedure

    Quote Originally Posted by hamidpia View Post
    Hello: While servicing low pressure side, I saw a machanic using pump down procedure as follows. 1. Closed HP valve on the discharge side of compressor
    2. Unit was kept running for short while, with suction side valve open unit suction side pressure came down to 30psi (low pressure trip was set at 26psi). 3.Unit was stopped and Low pressure valve was closed after that. This way, he would collect refrigerant into condenser unit and thereafter he would work on the evaporator.
    I just want to know is this a correct procedure, is there any gereral pump down procedure besides this.
    Best regards

    TRY THIS ONE

    [EX.1 IF YOU HAVE A LIQUID RECIEVER]
    -first the unit must be operating
    -do not close the high side service valve of the compressor.
    -first close the access valve in the liquid reciever going to the evaporator..
    -watch the pressure, then close the access valve in the reciever from the high side of the compressor "not the high side service valve of the compressor"
    -all the liquid refrigerant go to your reciever

    [EX.2 IF YOU DONT HAVE RECIEVER, BUT YOU CAN DO ONLY IN SPLIT A/C SYSTEM]
    -first the unit must be operating
    -close the discharge valve of the condensing unit
    -watch the pressure, then close the suction valve in the condensing unit.. all the refrigerant is now in the condensing unit..
    With great power Comes Great Responsibility

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Help with condensor pump
    By Bakerbj in forum Air Conditioning
    Replies: 23
    Last Post: 14-06-2009, 12:39 AM
  3. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Replies: 7
    Last Post: 08-08-2008, 05:13 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •