Results 1 to 6 of 6
Thread: Hot gas defrost
-
09-08-2008, 12:54 PM #1
Hot gas defrost
Got a small williams through the wall unit with hot gas defrost. Evaporator has frozen up and is thawing out over the weekend.
What is a suitable defrost termination temperature for such a contraption?
3C seems a bit cool to me to ensure all the ice has melted but i'm more used to electric defrost.
Cheers Jon
-
09-08-2008, 02:05 PM #2
Re: Hot gas defrost
15degrees then you know that any ice on the coil is defrosted
-
09-08-2008, 08:10 PM #3
Re: Hot gas defrost
Jon set for ten minutes and 30c termination temp.
philTransvestites are men who like to eat, drink, and be Mary.
-
09-08-2008, 08:19 PM #4
Re: Hot gas defrost
Cheers,
Its set for 20 minutes and 3c at the moment.
Will have a play with it on monday.
Cheers Jon
-
10-08-2008, 03:03 PM #5
Re: Hot gas defrost
the location of the sensor is another important factor.
-
10-08-2008, 06:17 PM #6
Re: Hot gas defrost
The probe is at the end of the coil. I think i'll put a new probe on it just to be sure anyway.
Jon