    Suction line size too small



    In theory what would happen if a suction pipe of say 3/8th was used instead of 1/2" on a split system, with a pipe run of 10m?


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Stu Taylor's Avatar
    Stu Taylor Guest

    Re: Suction line size too small

    If you're taking about a mini split, the difference is a lot..
    Since mini splits are critical charge units, with metering devices on the outdoor units, the effect will increase input wattage, decrease perfromance, (adding longer run times) and increase return suction temperature tothe compressor. Not Recommended.

  3. #3
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Suction line size too small

    marc5180

    i do not think it would make a lot of differene during normal operation (average ambients)

    it may produce a better room condition (less dehumidificatioin & elevated off coil condition)

    it would struggle to achieve room condition (setpoint) during high ambients,


    Billy Ray

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Suction line size too small

    Anyone else?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    May 2008
    Location
    England
    Posts
    101
    Rep Power
    16

    Re: Suction line size too small

    Why would you want to use 3/8 instead anyway? Is it a refit?

  6. #6
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Suction line size too small

    Quote Originally Posted by Prince Vaillant View Post
    Why would you want to use 3/8 instead anyway? Is it a refit?




    What figure would you put on any performance loss 1,5,10,25,50 % I suspect only those with access to the test chamber data can really know..

    The pipe sizing is usually for a run of xx metres max .I can't remember seeing any mention of bends etc which should theoretically reduce that max figure.....

    Multisync
    London

  7. #7
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Suction line size too small

    in cooling you lose , in heating you gain.

    Ice

  8. #8
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    20

    Re: Suction line size too small

    Slightly unconnected but hopefully of some help to the original poster:

    I’m not sure of the exact circumstances here but, say the smaller pipeline was recently installed in error (new system), and the question now is whether to correct the mistake or let it stay like that……apart from the “will it work” issue, there is also the warranty aspect to take into consideration (ie new compressor and labour to change it).

  9. #9
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Suction line size too small

    Quote Originally Posted by icecube51 View Post
    in cooling you lose , in heating you gain.

    Ice

    Interesting - can you explain your reasoning

    Multisync
    London

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Suction line size too small

    Suction pipe sizing determines suction gas velocity for a fixed speed compressor at a given swept volume.

    If you increase the suction line diameter you decrease pressure drop and velocity and this could affect oil return.

    If you decrease the suction line size the opposite happens, suction gas velocity increases and pressure drop increases.

    If you decrease the suction line size too much then you will restrict the mass flow resulting in low suction pressures/temperatures, as the compressor cannot overcome the increased resistance.

    Lack of cooling gas = lost compressor.

  11. #11
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Suction line size too small

    OK, think i had better explain. A friend of mine has bought a cheapo nasty unit from china He asked me would i fit it, which i said i would. I looked in the manual and although it wasn't very clear i noticed that it said 1/4 for the liquid and 3/8th for a 2way or 1/2" for a 3way ( what ever a 2way or 3way is?)

    I looked at the flare nuts that came with th units and there were 2- 3/8th and 2- 1/2" . I looked at the indoor unit and saw that the pipework was 3/8th and had a 3/8th flare nut on. I cut off the flare nut and braized the 3/8th pipe onto the back of the indoor unit, mounted it and ran the pipe to the condensor- 12metrers away.

    Next i went to flare it and.........you guessed it 1/2" flare nut.

    So now i dont know what size pipe it should be. The liquid is ok at 1/4 but im not sure what the suction should be. It says in the installation manual 2way is 3/8th ( which i thought meant cooling only and in which case it's right) but then why is the condensor 1/2" flare nut.
    Do i put in a 1/2 suction then run the risk of having too big a suction line?

    What a nightmare, never again
    The difference between genius and stupidity is that genius has its limits.

    Marc

  12. #12
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Suction line size too small

    i think your friend both himself an early vrf system unit.
    they had 3 pipes to connect. then the found the 4 way valve and the 3# pipe was no longer used.

    just a guess,

    Ice

  13. #13
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Suction line size too small

    it depands on the capacity of the units.
    my experience tells me, 7 to 9000 btu 1/4 - 3/8
    12 to 24000 btu 1/4 - 1/2 or 3/8 - 5/8

    so take your pick,

    Ice

  14. #14
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Suction line size too small

    Its a 1200 btu unit. i have just been round and took out the 3/8th pipe and replaced it with the 1/2" pipe. Its on pressure test as we speak.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  15. #15
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Suction line size too small

    Its up and running now, with the 1/2" suction.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  16. #16
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Suction line size too small

    Quote Originally Posted by marc5180 View Post
    Its up and running now, with the 1/2" suction.
    You never mentioned which refrigerant you were using, however a 3/8 suction at 10 meters is good for only up to 4.000 BTU mo better with
    1/2 "

  17. #17
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Suction line size too small

    It's on R407c, not to worry now problem sorted. Thank everyone
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. suction line velocity
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 16
    Last Post: 24-08-2008, 01:26 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. suction line freezeing
    By karimihassan in forum Air Conditioning
    Replies: 4
    Last Post: 05-08-2007, 05:17 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •