Blast Freezer Cooling / Heating Times
Hi there,
First post so go easy on me.
I keep neing being asked by white wall contractors for max cooling / heating times to cool / heat a room in order for them to size the pressure relief valves to gaurd against walls collapsing / doors not easily opened. Now I thought I would be able to work this out quite simply but am really struggling to put an equation together. Has anyone got some form of equation that might help me here or any suggestions? It would be greatly appreciated.
-
09-08-2008, 12:01 AM #2
Re: Blast Freezer Cooling / Heating Times
How is the time involved related to air pressure generation within the room?
Surely your blast freezer is recirculating the air within the space.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
09-08-2008, 06:37 AM #3
Re: Blast Freezer Cooling / Heating Times
Yes time has an important role. The faster the cooling faster is the vacuum creation. I have few charts on this. But send me a PMS then only I can send the file. I have exhausted all the slots for uploading.
-
09-08-2008, 07:49 PM #4
Re: Blast Freezer Cooling / Heating Times
Interesting question. I did some searching and it seems each manufacturer has different specs. Here's a link to Kason's site which list how to size their pressure relief vents.
http://www.kasonind.com/images/stori...och_06.web.pdf
-
13-08-2008, 01:09 PM #5
Re: Blast Freezer Cooling / Heating Times
How do I send you a PMS?
-
13-08-2008, 06:26 PM #6
-
16-08-2008, 06:50 PM #7
Re: Blast Freezer Cooling / Heating Times
The problem occurs when the bfreezer door is closed and the freezing process is started. The warm air within the chamber cools very quickly causing a negative pressure within the chamber. If a releif device is not built into the structure of the chamber then a risk of collapse can occur. On smaller chambers usually the doors are pulled tight on their seals and become difficult to open, on large stores the whole structure can collapse.
Fermod used to make pressure reliefs and would offer a selection proceedure.
We used to cut a hole into the roof of the chamber to allow for pressure relieve ... this might not be acceptable today.Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
Similar Threads
-
underfloor heating and cooling
By Lc_shi in forum New TechnologiesReplies: 19Last Post: 11-12-2009, 12:22 PM -
Trolley freezer & blast freezer
By smpsmp45 in forum NH3Replies: 0Last Post: 25-08-2007, 07:29 AM -
Blast Freezer
By w.l.ong in forum IndustrialReplies: 17Last Post: 16-12-2006, 10:34 AM -
Heating / Cooling Control
By walden in forum ElectricalReplies: 11Last Post: 16-04-2006, 01:20 PM -
Blast Freezer Questions
By rickmor in forum IndustrialReplies: 2Last Post: 11-04-2006, 08:15 PM