As the thread title suggests.
When there is a low oil level in the sight glass, does it always mean that the compressor is short of Oil?
NO!
Most of the guys on this forum will already know this.
Basically most recips when running at Low Loads for long periods.
Will have a higher than normal rate of "oil carry over"
resulting in sometimes the compressor tripping on oil failure.
The older and more tired the machine the more this can happen.
So as a tip from an old timer!
Next time you see a comp with low oil level and provided there is enough oil left in it to do so?
Run the compressor for long enough to allow it to fully load up.
This will force the oil that has been sitting out in the system to return to the compressor sump.
It may require running for a fair while but you will be amazed at the amount of oil that will come back.
Also the set point may have to be dropped to induce enough load.
Of course there could be many other reasons why the oil level is low.
But I seem to be finding a lot lately with the above problem.
Cheers Steve.
-
05-08-2008, 06:24 PM #2
Re: The Oil Sight Glass Shows a low Oil Level!
God bless you. Please spread the Word. Us compressor manufacturers will thank and bless you.
-
05-08-2008, 06:59 PM #3
Re: The Oil Sight Glass Shows a low Oil Level!
Good and true one Grizzly!
-
05-08-2008, 07:16 PM #4
Re: The Oil Sight Glass Shows a low Oil Level!
True, so true.
Simple words of wisdom that are so often forgotten.
A couple of years ago I was called in to look at a chiller that didn't work, another engineer had already spent over a week on it.
When I arrived the valve plates were all smashed up, the story from the first engineer went something like:
-Called in, found OP switch tripped. No oil in sight-glass added 5 l (!!!)
-Got compressor running but found the circuit SOG. Pressure tested, repaired leak and re-commissioned the unit.
I got called in the day after and the oil I managed to get out of the system were over twice the volume the manufacturer recommended!
-
05-08-2008, 07:23 PM #5
Re: The Oil Sight Glass Shows a low Oil Level!
Hi Steve. J type? Been there so many times.
-
05-08-2008, 09:21 PM #6
Re: The Oil Sight Glass Shows a low Oil Level!
Yep J type are bad but they are not alone as NoNickName points out.
Unless they are now made in Italy!
Out of interest N.N.N. Have you any particular elegance to a specific Manufacturer?
Curious that's all.
I can think of quite a few good recip companies
Who have Italian Roots.
Steve.
-
05-08-2008, 09:33 PM #7
Re: The Oil Sight Glass Shows a low Oil Level!
Frascold, my present employer
-
05-08-2008, 09:35 PM #8
Similar Threads
-
Odd view in a sight glass
By dkemper in forum Trouble ShootingReplies: 16Last Post: 16-06-2010, 12:10 PM -
Leaking sight Glass!?!!
By The MG Pony in forum FundamentalsReplies: 10Last Post: 19-04-2007, 06:09 AM -
liquid line sight glass mystery
By austech in forum Technical DiscussionsReplies: 19Last Post: 18-07-2006, 08:16 PM -
Sight glass , Flashing ?
By kfjoe in forum FundamentalsReplies: 15Last Post: 14-02-2004, 04:41 AM -
Sight Glass Located
By Abe in forum Trouble ShootingReplies: 3Last Post: 22-01-2002, 01:22 AM