Results 1 to 8 of 8
    Somerset
    69
    4,697
    The Oil Sight Glass Shows a low Oil Level!
    As the thread title suggests.
    When there is a low oil level in the sight glass, does it always mean that the compressor is short of Oil?
    NO!
    Most of the guys on this forum will already know this.
    Basically most recips when running at Low Loads for long periods.
    Will have a higher than normal rate of "oil carry over"
    resulting in sometimes the compressor tripping on oil failure.
    The older and more tired the machine the more this can happen.
    So as a tip from an old timer!
    Next time you see a comp with low oil level and provided there is enough oil left in it to do so?
    Run the compressor for long enough to allow it to fully load up.
    This will force the oil that has been sitting out in the system to return to the compressor sump.
    It may require running for a fair while but you will be amazed at the amount of oil that will come back.
    Also the set point may have to be dropped to induce enough load.
    Of course there could be many other reasons why the oil level is low.
    But I seem to be finding a lot lately with the above problem.
    Cheers Steve.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: The Oil Sight Glass Shows a low Oil Level!
    God bless you. Please spread the Word. Us compressor manufacturers will thank and bless you.
    Sep 2003
    ISRAEL
    72
    4,248
    Good and true one Grizzly!
    Feb 2007
    2,473
    45
    True, so true.
    Simple words of wisdom that are so often forgotten.
    A couple of years ago I was called in to look at a chiller that didn't work, another engineer had already spent over a week on it.
    When I arrived the valve plates were all smashed up, the story from the first engineer went something like:
    -Called in, found OP switch tripped. No oil in sight-glass added 5 l (!!!)
    -Got compressor running but found the circuit SOG. Pressure tested, repaired leak and re-commissioned the unit.
    I got called in the day after and the oil I managed to get out of the system were over twice the volume the manufacturer recommended!
    Apr 2006
    Torquay
    59
    130
    Hi Steve. J type? Been there so many times.
    Somerset
    69
    4,697
    Quote Originally Posted by 1torr View Post
    Yep J type are bad but they are not alone as NoNickName points out.
    Unless they are now made in Italy!
    Out of interest N.N.N. Have you any particular elegance to a specific Manufacturer?
    Curious that's all.
    I can think of quite a few good recip companies
    Who have Italian Roots.
    Steve.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Frascold, my present employer
    Somerset
    69
    4,697
    Quote Originally Posted by NoNickName View Post
    Impressive.
    logged and remebered.
    Steve
  1. Odd view in a sight glass
    By dkemper in forum Trouble Shooting
    Last Post: 16-06-2010, 12:10 PM
  2. Leaking sight Glass!?!!
    By The MG Pony in forum Fundamentals
    Last Post: 19-04-2007, 06:09 AM
  3. liquid line sight glass mystery
    By austech in forum Technical Discussions
    Last Post: 18-07-2006, 08:16 PM
  4. Sight glass , Flashing ?
    By kfjoe in forum Fundamentals
    Last Post: 14-02-2004, 04:41 AM
  5. Sight Glass Located
    By Abe in forum Trouble Shooting
    Last Post: 22-01-2002, 01:22 AM