restricted system
Hi guy, I have a problem with icecream freezer just hermetic. suction pressure down to 0, compressor too hot, amps high by 1 amps. when I turn off liquid line become cold suction press only 30psi. do I have a restricted system?
-
05-08-2008, 07:14 PM #2
Re: restricted system
Yes.
If it runs on 134a, cup tube.
Replace drier.
-
08-08-2008, 05:01 AM #3
Re: restricted system
Its 404, but I purge the system and change the drier, its all good now. thanks!