    restricted system



    Hi guy, I have a problem with icecream freezer just hermetic. suction pressure down to 0, compressor too hot, amps high by 1 amps. when I turn off liquid line become cold suction press only 30psi. do I have a restricted system?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: restricted system

    Yes.
    If it runs on 134a, cup tube.
    Replace drier.

  3. #3
    agfb96's Avatar
    agfb96 Guest

    Re: restricted system

    Its 404, but I purge the system and change the drier, its all good now. thanks!