04-08-2008, 05:55 PM #1
TDSH 233 Capacity
Does Frick make their software available? I need to look at propane capacity of a TDSH 233 economized unit and don't have the software. Can I use Mycom software for equivalent rotor size?
-
04-08-2008, 06:42 PM #2
Re: TDSH 233 Capacity
It is available to "Frick Factors". If you can't find the info you need let me know. I may be able to help. What are the operating conditions and the motor size? Is it a S,L or XL?
-
04-08-2008, 06:53 PM #3
TDSH233S, short rotor, -5F saturated propane suction, 110 F condensing (202 Psig), economized at 3550 RPM with auxiliary glycol cooled oil system.
Last edited by chillin out; 04-08-2009 at 07:30 PM.
-
04-08-2008, 07:11 PM #4
Re: TDSH 233 Capacity
Evaporator load: 219 TR
Compressor power: 438 HP
Mass Flow suction lbs/min:308.8
Mass Flow discharge lbs/min: 423.3
VFR (cfm) suction 959.2
VFR (cfm) discharge 231.4
I hope this helps. If you need more info please let me know.
-