    Outdoor coil icing up...



    Ok the customer has a ducted unit in the house and they complain of the outdoor unit icing up when they have the unit on heating and the temperature outside is below 5 degree celcius..........i have seen photos of the iced up coil and it seems it's only some sections of the coil icing up mainly the top half.

    I have checked charge and also relocted the thermistor to a better location due to it being placed very low on the coil and quite close to the compressor which may be affectng it's reading.........

    I couldn't get the unit to icing up at all when i was there but the ambient temp was 20 degree celcius, even tried blocking the coil but still no ice.

    I did witness the unit go into a defrost once while i had it running for 45min, when it goes into defrost i hear the Reversing valve go and the outdoor fans slow right down for 1 minute.

    Oh and it's doens't have its own defrost board.............the defrost is built in to the units outdoor pcb, i can't adjust any defrost setting as the unit doesn't allow it. The only thing i can change is the thermistor.

    Anyone got any suggestions??????



  2. #2
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: Outdoor coil icing up...

    quote "the outdoor fans slow right down for 1 minute." The outdoor fans should stop and stay
    off until if comes out of defrost.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Outdoor coil icing up...

    And the make and model of the unit is ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Outdoor coil icing up...

    Quote Originally Posted by Brian_UK View Post
    And the make and model of the unit is ?
    Important as always.

    Most heatpumps will build a white frost all over the outdoor coil before going in to defrost, as long as it isn't clear ice it is probably normal.

    The big question is: Does it deliver hot air inside?

    Make/model/pressures/temperatures please.

  5. #5
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,855
    Rep Power
    20

    Re: Outdoor coil icing up...

    OK, the icing up is normal, but the lack of defrosting is the problem.
    As above, what brand/model unit is it, what were the temps and pressures?
    I had to track down a problem pana, the issue went for over two winters with others looking at it (The issue was dropped after winter ended). No one could find the fault because of course no techs went there when it was cold between 9pm and 8am So it's a hard issue to solve without heaps of info.

  6. #6
    Join Date
    May 2008
    Location
    Australia
    Posts
    64
    Rep Power
    16

    Re: Outdoor coil icing up...

    The unit gets turned on heating 27degrees at 5:30am (outside air temp 4degree celcius) and by 7am it's iced up to the point where it will not blow warm air inside...............the unit is made in china and has a copeland scroll and is correctly charged with R407C using scales to charge.

    The defrost is built into the outdoor units pcb and i have already tried replacing and moving the condensor coil thermistor.

    I though only some units completly shut down the outdoor fan on defrost??? i have seen a few that actually slow right down during a defrost.

    Any ideas guys?

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36
    Quote Originally Posted by airflo View Post
    The unit gets turned on heating 27degrees at 5:30am (outside air temp 4degree celcius) and by 7am it's iced up to the point where it will not blow warm air inside...............the unit is made in china and has a copeland scroll and is correctly charged with R407C using scales to charge.

    The defrost is built into the outdoor units pcb and i have already tried replacing and moving the condensor coil thermistor.

    I though only some units completly shut down the outdoor fan on defrost??? i have seen a few that actually slow right down during a defrost.

    Any ideas guys?
    Do you have any other unit of that make/model in that area to compare functioning in same conditions. Could be small outdoor heat exchanger.

    What is humidity in that area at testing time?

    Also try to add more refrigerant (10% of total charge) to see if there is any difference in indoor unit discharge temperature.


    I did witness the unit go into a defrost once while i had it running for 45min, when it goes into defrost i hear the Reversing valve go and the outdoor fans slow right down for 1 minute.
    What was the outdoor ambient temperature when you witnessed this?

  8. #8
    Join Date
    May 2008
    Location
    Australia
    Posts
    64
    Rep Power
    16

    Re: Outdoor coil icing up...

    Quote Originally Posted by nike123 View Post
    Do you have any other unit of that make/model in that area to compare functioning in same conditions. Could be small outdoor heat exchanger.

    What is humidity in that area at testing time?

    Also try to add more refrigerant (10% of total charge) to see if there is any difference in indoor unit discharge temperature.


    What was the outdoor ambient temperature when you witnessed this?
    Unsure of the humidity........
    The outdoor temp was around 20dc when i witnessed what i thought was a defrost.
    I have had many of this particular unit icing up all over australia mainly in the colder areas.

  9. #9
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36
    Quote Originally Posted by airflo View Post
    Unsure of the humidity........
    The outdoor temp was around 20dc when i witnessed what i thought was a defrost.
    I have had many of this particular unit icing up all over australia mainly in the colder areas.

    If you have icing and need for defrosting at outdoor temperature of 20°C, and if we presume that charge is right, than you have problem with insufficient air flow or restriction in some point of liquid line-strainer-expansion-device.
    Last edited by nike123; 06-08-2008 at 12:48 PM.

  10. #10
    Join Date
    May 2008
    Location
    Australia
    Posts
    64
    Rep Power
    16

    Re: Outdoor coil icing up...

    the unit didn't ice up when i was there but when i blocked off the coil for 15min or so i caused the unit to go into defrost, there was no frost on the coil though.

    The outdoor fan is working fine......... all pipes from the distributor are at equal temps....

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Outdoor coil icing up...

    Quote Originally Posted by airflo View Post
    the unit didn't ice up when i was there but when i blocked off the coil for 15min or so i caused the unit to go into defrost, there was no frost on the coil though.

    The outdoor fan is working fine......... all pipes from the distributor are at equal temps....

    Then you have bad design problem! Small outdoor heat exchanger. Compare that heat exchanger and outdoor air flow with other manufacturers models of same capacity which are working properly.

  12. #12
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    218
    Rep Power
    17

    Re: Outdoor coil icing up...

    We can assume the suction pressure has been running lower than what we are used to?

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Outdoor coil icing up...

    Quote Originally Posted by Drew View Post
    We can assume the suction pressure has been running lower than what we are used to?

    It is higher Td, because of smaller heat exchanger/air flow, and therefore, lower evaporation temperature/suction pressure. That conditions accelerate ice formation when outdoor temperature is low and humidity high.

  14. #14
    Join Date
    May 2008
    Location
    Australia
    Posts
    64
    Rep Power
    16

    Re: Outdoor coil icing up...

    The coil is actually quite large and the fans are also pretty powerfull.

    I did notice that the coil seems to be doubled up and that the fins are extremely close together it's pretty much impossible to see through the coil due to it being doubled up.........and thats a brand new unit with no dirt on it yet.

    Could i possibly improve the airflow over the coil by using a fincomb to widen the fins ????

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Outdoor coil icing up...

    Quote Originally Posted by airflo View Post
    The coil is actually quite large and the fans are also pretty powerfull.

    Could i possibly improve the airflow over the coil by using a fincomb to widen the fins ????

    I think that is now time to stop guessing and to start measuring. Take full set of measurements to see what is really happening.

  16. #16
    Join Date
    May 2008
    Location
    Australia
    Posts
    64
    Rep Power
    16

    Re: Outdoor coil icing up...

    well i won't be going back out to the job untill i hear from the manufacturer..........but i checked all the neccassary measurements.............when i was there.

    Gas is all good..........

  17. #17
    Join Date
    Aug 2006
    Location
    China
    Age
    54
    Posts
    52
    Rep Power
    18

    Re: Outdoor coil icing up...

    It is normal the outside coil iced up. So, many customer are beginning to select GSHP to replace air source HP.

  18. #18
    Join Date
    Oct 2008
    Location
    USA
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: Outdoor coil icing up...

    Does the outdoor unit sit under the drip line of the roof. Could be moisture dripping from the roof causing top half of the unit to freeze. You will need a gutter to deflect the moisture from drpping on top of the system.

  19. #19
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Outdoor coil icing up...

    Quote Originally Posted by airflo View Post
    The unit gets turned on heating 27degrees at 5:30am (outside air temp 4degree celcius) and by 7am it's iced up to the point where it will not blow warm air inside...
    At that point, it should be going into defrost... which narrows it down to the coil sensor, sensor placement or board.

Similar Threads

  1. Compressor suction icing up on cold room set up
    By Leviathan in forum Trouble Shooting
    Replies: 9
    Last Post: 02-06-2007, 05:08 AM
  2. Krack Evaporator Icing
    By Rob@goldcoast in forum Technical Discussions
    Replies: 11
    Last Post: 15-08-2006, 02:53 AM
  3. What causes the icing of the evaporator
    By donrtc in forum Technical Discussions
    Replies: 12
    Last Post: 19-08-2005, 12:35 PM
  4. why icing on the suction valve
    By ong in forum Fundamentals
    Replies: 14
    Last Post: 12-06-2005, 10:03 PM
  5. Evaporator Icing Up
    By Abe in forum Commercial
    Replies: 6
    Last Post: 25-01-2003, 03:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •