I'm a engineering student haveing few assignments to complet for System Analysis..
I have to design a cool room that has a total heat load of 5.0KW and is to be used to hold product at 6 c in a 30 c design ambient.
I have to " select the most suitable compressor set , remote air cooled condenser and forced or Induced deaft coolet to operate on R 22 at an evaporating temperature of 0 c and a condensing temperature of 40 c.
-
01-08-2008, 06:47 PM #2
Re: System Analaysis
And what was your question exactly?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
01-08-2008, 10:59 PM #3
Re: System Analaysis
Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
02-08-2008, 01:08 AM #4
Re: System Analaysis
What i want here to know how to calculate the capacity of the evaporator, compressor and the condenser...
I want to know the Td for calculating the evaporater...which is directly proportional to the capacity..
at a 6 c room temperature whot would be the saturated suction temperature..
Last edited by Peter_1; 02-08-2008 at 08:08 AM.
-
02-08-2008, 01:55 AM #5
Re: System Analaysis
product at 6 c - an evaporating temperature of 0 c = 6K temperature difference, so you have to find an evaporator with a 5 kW capacity at this temperature difference.
You have almost answered all of your questions youself. You just needed to put the parameters in the right order...If all else fails, ask for help.
-
02-08-2008, 03:23 AM #6
Re: System Analaysis
He is just trying to get someone else to do his assignment....not what the instructor had in mind, I'm sure.
Ken
-
02-08-2008, 03:54 AM #7
Re: System Analaysis
nope it isnt true ...that i want help to do my assignment...
i know it sound a bit silly,but the problem is there is limited information for me to calculate..
i will give u a similar problem with the right information,
a cool room at 3c & 85% Rh,on R404a , the required evaporator capacity is 10.5 kW. ok
the solution..
determine the necessary room Td to achive 85% Rh...
from the graph i have i got a Td of 3.5 kTd..
Calculate the required base capacity ie
base capacity = evaporator capacity/ Td
= 10500/3.5
= 3000w @1kTd.
Correction factor for the evaporator temperature
ie the S.S.T - Td
= 3 - 3.5
= -0.5 k
according to the table the capacity correction factor is 1.14
therefore the required bas capacity is
capacity correction factor * base capacity
= 1.14 * 3000
= 3420 w
I can now select for the manufacturer which evaporator is the closest one for the capacity calculated
in this problem i had Rh to find the Td...
and the evaporator capacity...
i know the solution is simple but i'm goin nuts... so i posted this question
-
02-08-2008, 08:17 AM #8
Re: System Analaysis
You choose first your evaporator of 5 kW, 7 to 8 K DT (if no RH is demanded), then select a compressor which matches as close as possible 5 kW at te =0°C and tc=40°C, then add the power the compressors draws and add this to your capacity at the given conditions (+/-5 kW), let's say 6 .5 kW.
Then search for a condenser which can extract 6.5 kW at a DT of 10 K in an ambient of 30°C.
Use for all this correction factors for elevation (if any), other given capacities at other temperatures then you have here in you example (depends on the manufacturer), other liquid temperatures.. This is something you must find in your catalogues (spell checker says this is not a correct word. Is it?)
Select your TEV at 5 kW with te=0°C and tc=40°C.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM