    Lightbulb System Analaysis



    I'm a engineering student haveing few assignments to complet for System Analysis..
    I have to design a cool room that has a total heat load of 5.0KW and is to be used to hold product at 6 c in a 30 c design ambient.
    I have to " select the most suitable compressor set , remote air cooled condenser and forced or Induced deaft coolet to operate on R 22 at an evaporating temperature of 0 c and a condensing temperature of 40 c.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: System Analaysis

    And what was your question exactly?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: System Analaysis

    Quote Originally Posted by ivan25 View Post


    ....... I have to " select the most suitable .....

    Then firstly you need to chose the manufacturer you intend to use for your various pieces of kit and then get some engineering /performance data from them.
    Using their data you will be able to select your equipment and do a balance for optimum performance.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  4. #4
    ivan25's Avatar
    ivan25 Guest

    Exclamation Re: System Analaysis

    What i want here to know how to calculate the capacity of the evaporator, compressor and the condenser...
    I want to know the Td for calculating the evaporater...which is directly proportional to the capacity..
    at a 6 c room temperature whot would be the saturated suction temperature..

    Last edited by Peter_1; 02-08-2008 at 08:08 AM.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: System Analaysis

    product at 6 c - an evaporating temperature of 0 c = 6K temperature difference, so you have to find an evaporator with a 5 kW capacity at this temperature difference.

    You have almost answered all of your questions youself. You just needed to put the parameters in the right order...
    If all else fails, ask for help.


  6. #6
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: System Analaysis

    He is just trying to get someone else to do his assignment....not what the instructor had in mind, I'm sure.

    Ken

  7. #7
    ivan25's Avatar
    ivan25 Guest

    Re: System Analaysis

    nope it isnt true ...that i want help to do my assignment...
    i know it sound a bit silly,but the problem is there is limited information for me to calculate..
    i will give u a similar problem with the right information,
    a cool room at 3c & 85% Rh,on R404a , the required evaporator capacity is 10.5 kW. ok
    the solution..
    determine the necessary room Td to achive 85% Rh...
    from the graph i have i got a Td of 3.5 kTd..
    Calculate the required base capacity ie
    base capacity = evaporator capacity/ Td
    = 10500/3.5
    = 3000w @1kTd.
    Correction factor for the evaporator temperature
    ie the S.S.T - Td
    = 3 - 3.5
    = -0.5 k
    according to the table the capacity correction factor is 1.14

    therefore the required bas capacity is
    capacity correction factor * base capacity
    = 1.14 * 3000
    = 3420 w
    I can now select for the manufacturer which evaporator is the closest one for the capacity calculated


    in this problem i had Rh to find the Td...
    and the evaporator capacity...
    i know the solution is simple but i'm goin nuts... so i posted this question

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: System Analaysis

    You choose first your evaporator of 5 kW, 7 to 8 K DT (if no RH is demanded), then select a compressor which matches as close as possible 5 kW at te =0°C and tc=40°C, then add the power the compressors draws and add this to your capacity at the given conditions (+/-5 kW), let's say 6 .5 kW.
    Then search for a condenser which can extract 6.5 kW at a DT of 10 K in an ambient of 30°C.

    Use for all this correction factors for elevation (if any), other given capacities at other temperatures then you have here in you example (depends on the manufacturer), other liquid temperatures.. This is something you must find in your catalogues (spell checker says this is not a correct word. Is it?)

    Select your TEV at 5 kW with te=0°C and tc=40°C.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  4. Replies: 19
    Last Post: 15-04-2008, 07:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •