    Converting Care back to HCFC's



    Hi Guys,

    I have come accross a few under counter cabinets that were originally Care according to the label but have had compressors changed and are now on R134/R404

    Is this common place within the industry, does anyone out there do it, if so what else if anything has to be done apart from changing pot & drier

    I think the units are either fosters ot williams (Cant remember)

    regards

    fatboy



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Converting Care back to HCFC's

    Hi Raymond

    Don't forget that you should be trained on HC's to do this conversion. How many on the forum are trained ? I for one am not and anytime I come across R600 I simply walk away. Any thoughts anyone ?

  3. #3
    rbartlett's Avatar
    rbartlett Guest

    Re: Converting Care back to HCFC's

    i have been trained back in '99 and as i don't work on domestics it has been a complete waste of someone elses money!!

    cheers

    richard

  4. #4
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Converting Care back to HCFC's

    Hi Frank,
    While i appreciate what you say about being trained on CARE from what i hear for EVERY engineer that has done the course is that it is a waste of time. Nothing practical is done, just sitting about telling people the obvious. Dont use a flame on a system with gas in, Dont vent near something that can set light.

    I assume most pots have been changed after a gas leak & it's seized in which cases i would remove unit to outside, purge with OFN Before even thinking of starting to sweat it.

    I was just wondering if this was common place to convert these units back.
    By the way, if you take H & S seriously by the book, what the hell are they doing putting CARE fridges in kitchens right next to naked flames

    Regards

    Fatboy

  5. #5
    Join Date
    Jul 2004
    Location
    England
    Posts
    5
    Rep Power
    0

    Re: Converting Care back to HCFC's

    I,ve changed many a comp on care 30 usually fitted on elstar and staycold bottle coolers some under counter fridges and some gram units not seen a williams or fosters using care yet,if the comps dead we fit a new comp on R134a if its still ok then new filter and charge R409a being carfull not to overcharge as this is very easy to do,I have found many capillary,s blocked in care 30 units and sometimes just scrap the unit,gram use spark free condenser fan motors on theres but there crap so we end up fitting multifits anyway,they only use a small amount of gas and are not that scary but I think the problems out way the green benefits.

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. anyone in the uk care qualified xs forums member needs help
    By pocketbikeuk in forum Refrigerants
    Replies: 9
    Last Post: 24-04-2006, 10:44 AM
  3. Compressor back pressure rating
    By Cary in forum Fundamentals
    Replies: 9
    Last Post: 05-12-2004, 08:42 AM
  4. Care
    By Reeferjon in forum Refrigerants
    Replies: 6
    Last Post: 14-12-2001, 05:32 PM
  5. Low back pressure compressor application
    By Abe in forum Technical Discussions
    Replies: 5
    Last Post: 31-07-2001, 11:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •