Results 1 to 15 of 15
  1. #1
    tinkerer's Avatar
    tinkerer Guest

    Change my heat pump to water source



    Hello, this is my first post. I'm no pro, just a guy that kept ACs going. What I would like to do is to cut into my outside condenser coil and run tubing into the house to a water source condenser and then back outside so I can have a geothermal setup. I'm retired on a fixed income and would need to make my own condenser from tubing inside tubing. Here in Nebraska the extremes are -25 to +105 f. I already have a well and also a small pond to dump to. The heat pump is a 3 ton unit. Is it worth it and feasible?



  2. #2
    Join Date
    Aug 2006
    Location
    China
    Age
    55
    Posts
    52
    Rep Power
    18

    Re: Change my heat pump to water source

    I am an geothermal heat pump unit disign engineer, to my experience ,it is feasible.

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Change my heat pump to water source

    Quote Originally Posted by tinkerer View Post
    Hello, this is my first post. I'm no pro, just a guy that kept ACs going. What I would like to do is to cut into my outside condenser coil and run tubing into the house to a water source condenser and then back outside so I can have a geothermal setup. I'm retired on a fixed income and would need to make my own condenser from tubing inside tubing. Here in Nebraska the extremes are -25 to +105 f. I already have a well and also a small pond to dump to. The heat pump is a 3 ton unit. Is it worth it and feasible?

    Yes you will be able to do it.
    Think about filtering this supply water.
    A pipe within a pipe would do the job you might need to experiment with the size to start with.
    I would fit service valves into the system to ease any future work that you may need to do.

    If you use 1/2 inch inside 7/8 or 5/8 inch what you need to do is thread the 1/2 inch inside the larger all the way and braze in the fittings for the water to one end only, while the pipes are still straight.
    Then coil from the fixed end one turn or full loop, then try to push the 1/2 inch back into the 5/8 from the free end and that will stop the 1/2 from being only on the inside of the internal 5/8 (pipes comercialy designed have spacers inside the seperate the two pipes to allow the water to circulate fully around the refrigerant pipe).

    Continue to coil the pipes as tight as need be (coil around somthing round and about a foot or 18inch diamiter. When you get to the end leave the water side free but conect the refrigerant to the system.

    Conect a hose pipe with tap water from your kitchen and just let the water flow to waste to start. Run the system and test that you have the right tempreture exchange if you have too much then you can cut the end of the water pipe by a foot or so.
    Keep testing till you get the correct settings and when you are happy remove it all and braze fit all the conections to finish it.

    Why do you need to bring it inside? Are you afraid the water may freeze in the winter?

    Any more questions feel free to ask.

    Cheers taz.

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Change my heat pump to water source

    Keep an eye on ebay, you can find some good deals on there for ready made rigs, a friend told me there is a 3 ton coaxial exchanger on there now, worth to see if it is still there!

  5. #5
    imad8's Avatar
    imad8 Guest

    Re: Change my heat pump to water source

    Quote Originally Posted by yangchenchen View Post
    I am an geothermal heat pump unit disign engineer, to my experience ,it is feasible.
    although it is not accurate to use the term ''geothermal'' for well- source heat pump,i think u can enhance the COP but u would not reduce the cost.

  6. #6
    Join Date
    Mar 2005
    Location
    wisconsin usa
    Age
    55
    Posts
    13
    Rep Power
    0

    Re: Change my heat pump to water source

    Rather than go through all of that and suffer in efficiency, why not go to packless.com and just buy a heat pump condenser coil?

  7. #7
    Join Date
    Jan 2008
    Location
    USA
    Posts
    16
    Rep Power
    0

    Re: Change my heat pump to water source

    how about the plate exchangers listed on ebay? claims are good to 400psi & usable on *****. i bought the smallest for use on an approx 3000btu water source heater ($55 total). project is listed elsewhere & is not completed yet.
    regards;
    eddc

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Change my heat pump to water source

    I would also go for PHE,

    here are some for great prices,

    http://shop.ebay.com/items/_W0QQ_fro...nger&_osacat=0

  9. #9
    Join Date
    Mar 2005
    Location
    wisconsin usa
    Age
    55
    Posts
    13
    Rep Power
    0

    Re: Change my heat pump to water source

    Although I agree that there is no better exchanger than a plate, I caution that in this situation it is very important to have proper controls to prevent freezup of the exchanger. A pressure switch and/or cold control are not enough for protection. I would use an adjustable low pressure control, a freezstat, and a water flow switch to protect the exchanger. I have seen many heat pump plates ruptured and if that happens, everything is junk. Compressor, reversing valve, line set, evap. coil, everything.

  10. #10
    Join Date
    Mar 2005
    Location
    wisconsin usa
    Age
    55
    Posts
    13
    Rep Power
    0

    Re: Change my heat pump to water source

    By the way, imad8, why is it not accurate to call an open loop heat pump a geothermal? I may be not understanding what you meant.

  11. #11
    JoB's Avatar
    JoB Guest

    Re: Change my heat pump to water source

    Tinkerer,

    I just stumbled on this forum and am wondering if you have gotten any answers that helped you convert your airsource heat pump to watersource. I am thinking of doing the same thing. I installed a new 3-1/2 ton airsource heatpump last summer when the old a/c wasn't doing the job anymore. I didn't thoroughly investigate or would have put in a watersource then. Now I don't want to take out a almost new hp that works very well down to 15F when it would most likely do all I need if it was working with 50F water.
    I also have a well and a place to dump the water.
    In MN it would have to give me all 42,000 btu's when it is gets below zero. I'm heating a 2800sqf log home.
    I have been thinking of cutting off the outside coil and replacing it with a heat exchanger made with copper refrigerant tubing inside a larger PEX water tube of the correct length would be easy to make and should work with sufficient well water flow. It should also be easy to clean the iron fouling with chemical (iron out) occasionally. I would eliminate the outside coil entirely and move everything inside the basement if it works. I don't know what the length should be, but seeing pictures of manufactured units the don't look to be very long. A homemade exchanger would not be as space efficient using regular copper tubing instead of the spiral type but I think a 25' coil would be very inexpensive to make.

  12. #12
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Change my heat pump to water source

    It looks like tinkerer hasnt been around since August 16th 2008 I guess he doenst care

  13. #13
    JoB's Avatar
    JoB Guest

    Re: Change my heat pump to water source

    nh3wizard,

    Have you been to Joel's Pizza Palace in Valrico? I heard they have the best food in town.

  14. #14
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Change my heat pump to water source

    Quote Originally Posted by JoB View Post
    nh3wizard,

    Have you been to Joel's Pizza Palace in Valrico? I heard they have the best food in town.
    Never heard of them, but know you have my curiosity up and I will have to check them out.

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Change my heat pump to water source

    Comercial Hxs are riffled inside the refrigerant side.

Similar Threads

  1. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  2. Evaporator Design-Air Source Heat Pump for water heating
    By anup in forum Technical Discussions
    Replies: 7
    Last Post: 20-03-2006, 02:26 PM
  3. water source heat pump
    By Lc_shi in forum New Technologies
    Replies: 12
    Last Post: 29-03-2005, 09:09 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. Mcquay water source heat pump
    By bernie in forum Air Conditioning
    Replies: 2
    Last Post: 10-02-2003, 01:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •