Results 1 to 13 of 13
27-07-2008, 06:33 PM #1
How to decrease head pressure for an existing system?
Assume constant ambient temp, constant evap load. What we can do to decrease heat pressure. (put larger condenser? Or smaller compressor?)
27-07-2008, 07:11 PM #2
Re: How to decrease head pressure for an existing system?
In order of (my) preference:
- Correct maintenance of condensers like cleaning, checking for incondensables, rust, fin spacing, fouling, etc.
- Modify control philosophy if controls are the ones that are keeping head pressure up.
- Improve cooling media flow like checking for hot air recirculation or water flow.
- Check correct design at refrigerant exit so they are not being flooded.
- Modify condenser characteristics like changing fans in air cooled or sprays in water cooled.
- Look for other aids like water, for example read this: http://www.refrigeration-engineer.co...ad.php?t=13978
- Change condensers is obvious solution a little extreme.
- Changing compressor is even more extreme and I thing this should be done after a thorough system revision including demand estimation, energy use, etc.
27-07-2008, 07:27 PM #3
Large condenser will decrease head pressure to a point limited by ambient temperature but would need another regulation in colder weather when we may forced to find away to rise head pressure to prevent a serious decline in system capacity.Changing the compressor leads to out_design system.
27-07-2008, 11:13 PM #4
Thank you both!
28-07-2008, 11:15 AM #5
Add a water heat reclaim
28-07-2008, 03:42 PM #6
Reduce subcooling
28-07-2008, 05:53 PM #7
I always forget to make a distinction between head pressure and condensing pressure.
With this in mind you can reduce head pressure by decreasing any pressure drop from the compressor to the condenser without (necessarily) affecting condensing pressure.
28-07-2008, 10:01 PM #8
28-07-2008, 10:52 PM #9
David,
Check out the "Add-A-Cool" section at this web site.
I've never applied to but it makes sense.
http://www.boisdarccoils.com
29-07-2008, 07:02 AM #10
Subcooling increases the heat rejection and normally it is obtained through a overcharging the condensing coil, so that at least one tube is filled with liquid.
Reducing subcooling will clear the codnensing coil of the extra liquid (increasing the exchange surface) and decrease the compressor performance and the resulting heat rejection.
29-07-2008, 09:44 PM #11
If the condenser has an in-build SC coil (last bends going upwards making a liquid seal like Guntner or Goedhart is doing it or even an additional SC coil mounted after the condenser, then no condensing surface was taken at all.
You're right with a standard condenser with no receiver.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
30-07-2008, 09:23 PM #12
Fit a crankcase pressure regulating valve.
30-07-2008, 09:46 PM #13
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
simple suction/ head pressure
By chill one in forum FundamentalsReplies: 1Last Post: 27-03-2008, 11:02 AM -
Low head pressure Versus Heat reclaim.
By taz24 in forum Supermarket RefrigerationReplies: 17Last Post: 20-03-2008, 11:47 AM -
Refrigerated display cabinet, low head pressure
By expat in forum CommercialReplies: 10Last Post: 11-12-2007, 09:07 AM -
404A head pressure to ambient rule of thumb
By kengineering in forum RefrigerantsReplies: 22Last Post: 08-05-2007, 10:40 PM