    How to decrease head pressure for an existing system?



    Assume constant ambient temp, constant evap load. What we can do to decrease heat pressure. (put larger condenser? Or smaller compressor?)



  2. #2
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: How to decrease head pressure for an existing system?

    In order of (my) preference:

    1. Correct maintenance of condensers like cleaning, checking for incondensables, rust, fin spacing, fouling, etc.
    2. Modify control philosophy if controls are the ones that are keeping head pressure up.
    3. Improve cooling media flow like checking for hot air recirculation or water flow.
    4. Check correct design at refrigerant exit so they are not being flooded.
    5. Modify condenser characteristics like changing fans in air cooled or sprays in water cooled.
    6. Look for other aids like water, for example read this: http://www.refrigeration-engineer.co...ad.php?t=13978
    7. Change condensers is obvious solution a little extreme.
    8. Changing compressor is even more extreme and I thing this should be done after a thorough system revision including demand estimation, energy use, etc.

  3. #3
    Join Date
    Mar 2007
    Location
    Iraq
    Posts
    57
    Rep Power
    18

    Re: How to decrease head pressure for an existing system?

    Hi
    Large condenser will decrease head pressure to a point limited by ambient temperature but would need another regulation in colder weather when we may forced to find away to rise head pressure to prevent a serious decline in system capacity.Changing the compressor leads to out_design system.

  4. #4
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: How to decrease head pressure for an existing system?

    Thank you both!

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: How to decrease head pressure for an existing system?

    Add a water heat reclaim
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: How to decrease head pressure for an existing system?

    Reduce subcooling

  7. #7
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: How to decrease head pressure for an existing system?

    I always forget to make a distinction between head pressure and condensing pressure.

    With this in mind you can reduce head pressure by decreasing any pressure drop from the compressor to the condenser without (necessarily) affecting condensing pressure.


  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: How to decrease head pressure for an existing system?

    Quote Originally Posted by NoNickName View Post
    Reduce subcooling
    This need some clarification A...o.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: How to decrease head pressure for an existing system?

    David,

    Check out the "Add-A-Cool" section at this web site.
    I've never applied to but it makes sense.

    http://www.boisdarccoils.com

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: How to decrease head pressure for an existing system?

    Quote Originally Posted by Peter_1 View Post
    This need some clarification A...o.
    Subcooling increases the heat rejection and normally it is obtained through a overcharging the condensing coil, so that at least one tube is filled with liquid.
    Reducing subcooling will clear the codnensing coil of the extra liquid (increasing the exchange surface) and decrease the compressor performance and the resulting heat rejection.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: How to decrease head pressure for an existing system?

    If the condenser has an in-build SC coil (last bends going upwards making a liquid seal like Guntner or Goedhart is doing it or even an additional SC coil mounted after the condenser, then no condensing surface was taken at all.

    You're right with a standard condenser with no receiver.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: How to decrease head pressure for an existing system?

    Fit a crankcase pressure regulating valve.

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: How to decrease head pressure for an existing system?

    Quote Originally Posted by Peter_1 View Post
    If the condenser has an in-build SC coil (last bends going upwards making a liquid seal like Guntner or Goedhart is doing it or even an additional SC coil mounted after the condenser, then no condensing surface was taken at all.

    You're right with a standard condenser with no receiver.
    Any tube filled with liquid is less surface for the condenser, whatever the geometry of the last bend, with or without receiver.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. simple suction/ head pressure
    By chill one in forum Fundamentals
    Replies: 1
    Last Post: 27-03-2008, 11:02 AM
  3. Low head pressure Versus Heat reclaim.
    By taz24 in forum Supermarket Refrigeration
    Replies: 17
    Last Post: 20-03-2008, 11:47 AM
  4. Replies: 10
    Last Post: 11-12-2007, 09:07 AM
  5. 404A head pressure to ambient rule of thumb
    By kengineering in forum Refrigerants
    Replies: 22
    Last Post: 08-05-2007, 10:40 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •