    Question 30 gx screw chiller



    hi all

    we have 30 gx screw chillers.recetnly rewinded one compressor.again compressor damaged due to the reverse rotation.how do check the rotation befor starting the compressor?can anybody help



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: 30 gx screw chiller

    To connect the right way, mark the wires you disconnect, whoever replace the winding, must do it the way it was.

    They do check them before they return them to you, don't they?

  3. #3
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: 30 gx screw chiller

    The rewind company must tell you the direction of rotation that they have wound the stator for. You then need to contact Carrier technical to make sure of the correct rotation for this compressor. The next thing you need is to purchase a phase rotation meter and ensure that the starter wiring is correct all the way through before connecting to the motor. I assume that there are other compressors of the same model running at this site. You could certainly reference the rotation of these with your new phase rotation meter.

  4. #4
    Join Date
    Feb 2004
    Location
    USA
    Posts
    136
    Rep Power
    0

    Re: 30 gx screw chiller

    On the O6N compressors they temporaraly put a RRS switch on the discharge line in seiries with the HP switch for replacement comp start up.. If its running backwards, it will shut off before the screws crash into the walls.

    See page 56, item 19 about reverse rotation switch: http://www.docs.hvacpartners.com/idc...t/30g,h-8t.pdf

  5. #5
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Question Re: 30 gx screw chiller

    Quote Originally Posted by absrbrtek View Post
    On the O6N compressors they temporaraly put a RRS switch on the discharge line in seiries with the HP switch for replacement comp start up.. If its running backwards, it will shut off before the screws crash into the walls.

    See page 56, item 19 about reverse rotation switch: http://www.docs.hvacpartners.com/idc...t/30g,h-8t.pdf
    thanks to chemicool,ptsac,assrbrtek for replay.assrbrtek, i read the manual which you send.but i want to know more about RRS switch.when compressor working backwards,what is happening on discharge line.

  6. #6
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: 30 gx screw chiller

    06n compressor does not tolerate revers rotation.i think,if compressor starting reverse rotation compressor will be damaged within seconds.on this condition,how does work RRS switch?i want to know the character of RRS switch.

  7. #7
    Join Date
    Feb 2004
    Location
    USA
    Posts
    136
    Rep Power
    0

    Re: 30 gx screw chiller

    It is a low pressure switch, I do not know its settings. However, as there is no counterthust bearings, it will stop the compressor before the screws pull themselves into the wall. I just know that all new replacement screws require one to be installed temporarily in order to stop the screw from destroying the screw if its running backwards.
    Quote Originally Posted by moideen View Post
    06n compressor does not tolerate revers rotation.i think,if compressor starting reverse rotation compressor will be damaged within seconds.on this condition,how does work RRS switch?i want to know the character of RRS switch.

Similar Threads

  1. flooded evaporator in screw chiller
    By Lc_shi in forum Technical Discussions
    Replies: 25
    Last Post: 05-07-2010, 05:37 AM
  2. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 11:36 PM
  3. carrier screw chiller
    By moideen in forum Air Conditioning
    Replies: 4
    Last Post: 10-05-2008, 08:24 PM
  4. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  5. York Open Drive Screw Chiller
    By Cofreth in forum Air Conditioning
    Replies: 4
    Last Post: 24-10-2005, 02:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •