Thread: 30 gx screw chiller
-
27-07-2008, 05:40 PM #1
30 gx screw chiller
hi all
we have 30 gx screw chillers.recetnly rewinded one compressor.again compressor damaged due to the reverse rotation.how do check the rotation befor starting the compressor?can anybody help
-
27-07-2008, 06:09 PM #2
Re: 30 gx screw chiller
To connect the right way, mark the wires you disconnect, whoever replace the winding, must do it the way it was.
They do check them before they return them to you, don't they?
-
27-07-2008, 07:38 PM #3
Re: 30 gx screw chiller
The rewind company must tell you the direction of rotation that they have wound the stator for. You then need to contact Carrier technical to make sure of the correct rotation for this compressor. The next thing you need is to purchase a phase rotation meter and ensure that the starter wiring is correct all the way through before connecting to the motor. I assume that there are other compressors of the same model running at this site. You could certainly reference the rotation of these with your new phase rotation meter.
-
28-07-2008, 06:35 AM #4
Re: 30 gx screw chiller
On the O6N compressors they temporaraly put a RRS switch on the discharge line in seiries with the HP switch for replacement comp start up.. If its running backwards, it will shut off before the screws crash into the walls.
See page 56, item 19 about reverse rotation switch: http://www.docs.hvacpartners.com/idc...t/30g,h-8t.pdf
-
28-07-2008, 07:44 AM #5
-
28-07-2008, 08:50 PM #6
Re: 30 gx screw chiller
06n compressor does not tolerate revers rotation.i think,if compressor starting reverse rotation compressor will be damaged within seconds.on this condition,how does work RRS switch?i want to know the character of RRS switch.
-
29-07-2008, 12:41 AM #7
Re: 30 gx screw chiller
It is a low pressure switch, I do not know its settings. However, as there is no counterthust bearings, it will stop the compressor before the screws pull themselves into the wall. I just know that all new replacement screws require one to be installed temporarily in order to stop the screw from destroying the screw if its running backwards.
Similar Threads
-
flooded evaporator in screw chiller
By Lc_shi in forum Technical DiscussionsReplies: 25Last Post: 05-07-2010, 05:37 AM -
Compressors - screw or reciprocating?
By Josip in forum Industrial CompressorsReplies: 18Last Post: 27-01-2009, 10:36 PM -
carrier screw chiller
By moideen in forum Air ConditioningReplies: 4Last Post: 10-05-2008, 08:24 PM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM -
York Open Drive Screw Chiller
By Cofreth in forum Air ConditioningReplies: 4Last Post: 24-10-2005, 02:17 PM