    Fruit cold store design
    have some problem and need your help ... advice ... experience good or bad ...
    …. we have to design a new cold store for fruits. Half rooms with direct ammonia cooling and another half rooms with indirect water cooling. Our client likes to save some money requesting to install suction pressure regulating valve (to change room temperature) for two coolers in parallel connection (one cold room) …. liquid feeding line also will be common with hand regulating valve (for balancing) for each evaporator …. can we save some money to our client or only get a headache ….
    … for indirect water cooling system they also want to install one 3-way water regulating valve for two coolers (one cold room) in parallel connection
    …. the same question as above ...
    ...anyone had some similar situation ... what to do?
    Best regards, Josip
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Fruit cold store design
    Hey Josip
    I have built a big unit for fruit cold storage some years ago.
    Give me the storing temps required, humidity and fruit tonnage per room and I see how I can help.
    In short, it was a rack of compressors with flooded evaporators, HG defrost, compressors and condensers controlled by Danfoss AKC 25H and room temp, defrost controlled by individual controllers.
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    May 2008
    weston
    348
    Quote Originally Posted by Josip View Post
    ... can we save some money to our client or only get a headache ….
    Best regards, Josip
    Go for it!
    I thing that if you know what you are doing, and I'm sure you do, you cannot get headache's
    Having doubts is normal and will make you sit and think!
    Best formula for a sucessfull design!
    Aug 2005
    5,302
    Hi Josip.
    My recommendation is to use one set of valves for each evaporator (water or ammonia).
    At low thermal loads the respective valve capacity may not be able to control the flow properly.
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, US Iceman
    Hi Josip.
    Thanks, good advice ... we came to the same conclusion, but now we have a new moment...
    see this....
    http://www.refrigeration-engineer.co...ad.php?t=14979
    .... hope you'll contribute with some good suggestion
    Best regards, Josip