Results 1 to 16 of 16
    Mar 2008
    US
    74
    Is it better to use cap tube for small capacity?
    Because for TEV system, there will be pressure difference between two side. Small compressor will not start. Correct?
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    May 2008
    weston
    348
    Re: Is it better to use cap tube for small capacity?
    No, you can always unload and start a compressor.
    If the thermal load is too small maybe yes but cap tubes are best used for constant thermal load and/or limited refrigerant charge.
    Not for nothing some places are not using cap tubes anymore TEV are more efficient.
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    May 2006
    Yorkshire
    72
    417
    Even so, It's always best to have a time delay relay to creat a rest period after the compressor has stopped and before it starts up, to allow the system pressures to equalise. If you try to start the compressor too soon after it has stopped then there will be a pressure difference between the high and low sides, this will probably cause the compressor to stall, and possibly take out a line breaker.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
    Mar 2008
    US
    74
    Thanks for reply. Will the pressure difference disappear if waiting more time? How to unload a compressor?
    Aug 2005
    5,302
    To my knowledge, small compressors, using cap tubes for expansion devices, do not have capacity control for unloading. If the compressor is off for a sufficient period of time to allow the high and low side pressures to equalize, it is essentially starting at no load (briefly).
    If you try to start it before the pressures ahve equalized it is trying to start against a load (the pressure differential that exists at that specific time).
    GXMPLX's Avatar
    May 2008
    weston
    348
    You guys need to let your imagination fly once in a while!
    1. Wait with a timer, more usual in Europe than here but possible.
    2. You can use TEV with bleed (a bypass orifice) to equalize quickly
    3. Use a small capillary in parallel with the TEV
    4. Bypass with a solenoid valve that opens just before energizing the compressor (not usual)
    5. Or not equalize and use a start capacitor to improve compressor torque
    6. Set the control to start with a high enough suction pressure for the compressor not to have problems.
    7. Use controls with mechanical delays
    Aug 2005
    5,302
    Quote Originally Posted by GXMPLX
    ...TEV are more efficient.
    Why, and based on what?
    GXMPLX's Avatar
    May 2008
    weston
    348
    Vox populi vox dei!
    Aug 2005
    5,302
    Nec audiendi qui solent dicere, Vox populi, vox Dei, quum tumultuositas vulgi semper insaniae proxima sit
    Et tu, Brute?
    GXMPLX's Avatar
    May 2008
    weston
    348
    If thermal load goes higher (condensing constant) a capillary tube reduces flow because it has less pressure differential.
    TEV do the opposite, if thermal load goes up it senses more superheat and injects more refrigerant suction pressure goes up, thus adapting better to thermal load and therefore are more efficient.
    The good thing of capillaries is that they protect the compressor better from overloading than TXV.
    For this you should know that your motherland passed a bill requiring TXV to be used in all US manufactured air conditioners, because TXVs are more energy efficient, causing a word shortage of TXVs!
    This is a test right?
    Save yourself 25 bucks and read:
    http://ecaaser3.ecaa.ntu.edu.tw/weif...conditions.pdf
    GXMPLX's Avatar
    May 2008
    weston
    348
    Quoque fili?
    Mar 2008
    US
    74
    Quote Originally Posted by GXMPLX View Post
    Good article!
    Mar 2008
    US
    74
    If the compressor is RSIR, not capacitor start, can we add a separate capacitor?
    GXMPLX's Avatar
    May 2008
    weston
    348
    Quote Originally Posted by david2008 View Post
    Yes generally you can, but this is a question the compressor manufacturer or it's rep has to answer.
    GXMPLX's Avatar
    May 2008
    weston
    348
    Et tu, Brute?
    I can't answer, rule 6!
    nevgee's Avatar
    May 2006
    Yorkshire
    72
    417
    U might get away with a hard start capacitor like the SUPCO SSP version, they're supposed to help "kick" the motor up.
    We have used sol valves to relieve pressures on small units with good effect. But usually a delay timer which then limits the compressor to minimum starts / hour is an added safe guard.
  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Last Post: 16-11-2010, 11:44 PM
  2. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Last Post: 15-11-2007, 06:03 AM
  3. Coils - Inline vs Staggered tube
    By nh3simman in forum Fundamentals
    Last Post: 03-04-2007, 08:25 PM
  4. metric capillary tube
    By tralex in forum Fundamentals
    Last Post: 21-02-2006, 06:57 AM
  5. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Last Post: 06-12-2002, 05:11 PM