Is it better to use cap tube for small capacity?
Because for TEV system, there will be pressure difference between two side. Small compressor will not start. Correct?
-
26-07-2008, 12:45 AM #2
Re: Is it better to use cap tube for small capacity?
Hi,
No, you can always unload and start a compressor.
If the thermal load is too small maybe yes but cap tubes are best used for constant thermal load and/or limited refrigerant charge.
Not for nothing some places are not using cap tubes anymore TEV are more efficient.
-
26-07-2008, 12:48 AM #3
Re: Is it better to use cap tube for small capacity?
Even so, It's always best to have a time delay relay to creat a rest period after the compressor has stopped and before it starts up, to allow the system pressures to equalise. If you try to start the compressor too soon after it has stopped then there will be a pressure difference between the high and low sides, this will probably cause the compressor to stall, and possibly take out a line breaker.
Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
26-07-2008, 01:29 AM #4
Re: Is it better to use cap tube for small capacity?
Thanks for reply. Will the pressure difference disappear if waiting more time? How to unload a compressor?
-
26-07-2008, 01:42 AM #5
Re: Is it better to use cap tube for small capacity?
To my knowledge, small compressors, using cap tubes for expansion devices, do not have capacity control for unloading. If the compressor is off for a sufficient period of time to allow the high and low side pressures to equalize, it is essentially starting at no load (briefly).
If you try to start it before the pressures ahve equalized it is trying to start against a load (the pressure differential that exists at that specific time).If all else fails, ask for help.
-
26-07-2008, 03:55 AM #6
Re: Is it better to use cap tube for small capacity?
You guys need to let your imagination fly once in a while!
- Wait with a timer, more usual in Europe than here but possible.
- You can use TEV with bleed (a bypass orifice) to equalize quickly
- Use a small capillary in parallel with the TEV
- Bypass with a solenoid valve that opens just before energizing the compressor (not usual)
- Or not equalize and use a start capacitor to improve compressor torque
- Set the control to start with a high enough suction pressure for the compressor not to have problems.
- Use controls with mechanical delays
-
26-07-2008, 04:11 AM #7
Re: Is it better to use cap tube for small capacity?
Originally Posted by GXMPLXIf all else fails, ask for help.
-
26-07-2008, 04:27 AM #8
-
26-07-2008, 04:44 AM #9
Re: Is it better to use cap tube for small capacity?
Nec audiendi qui solent dicere, Vox populi, vox Dei, quum tumultuositas vulgi semper insaniae proxima sit
Et tu, Brute?If all else fails, ask for help.
-
26-07-2008, 04:46 AM #10
Re: Is it better to use cap tube for small capacity?
If thermal load goes higher (condensing constant) a capillary tube reduces flow because it has less pressure differential.
TEV do the opposite, if thermal load goes up it senses more superheat and injects more refrigerant suction pressure goes up, thus adapting better to thermal load and therefore are more efficient.
The good thing of capillaries is that they protect the compressor better from overloading than TXV.
For this you should know that your motherland passed a bill requiring TXV to be used in all US manufactured air conditioners, because TXVs are more energy efficient, causing a word shortage of TXVs!
This is a test right?
Save yourself 25 bucks and read:
http://ecaaser3.ecaa.ntu.edu.tw/weif...conditions.pdf
-
26-07-2008, 04:47 AM #11
Re: Is it better to use cap tube for small capacity?
Quoque fili?
-
26-07-2008, 02:52 PM #12
-
26-07-2008, 03:05 PM #13
-
26-07-2008, 04:36 PM #14
-
26-07-2008, 04:39 PM #15
-
26-07-2008, 08:07 PM #16
Re: Is it better to use cap tube for small capacity?
U might get away with a hard start capacitor like the SUPCO SSP version, they're supposed to help "kick" the motor up.
We have used sol valves to relieve pressures on small units with good effect. But usually a delay timer which then limits the compressor to minimum starts / hour is an added safe guard.Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
Similar Threads
-
Capillary tube sizing
By Sledge in forum RefrigerantsReplies: 7Last Post: 16-11-2010, 11:44 PM -
excess tube length on condenser tube plate
By onquin in forum FundamentalsReplies: 4Last Post: 15-11-2007, 06:03 AM -
Coils - Inline vs Staggered tube
By nh3simman in forum FundamentalsReplies: 15Last Post: 03-04-2007, 08:25 PM -
metric capillary tube
By tralex in forum FundamentalsReplies: 5Last Post: 21-02-2006, 06:57 AM -
TEV capacity related to pressure drop
By DaBit in forum CPU OverclockersReplies: 8Last Post: 06-12-2002, 05:11 PM