Thread: oil pressure and diff trip
25-07-2008, 08:02 PM #1
Hey can anyone please expain what role oil plays in a system. I work with industrial systems in a food processing factory. Most compressors are carlye reciprocating type. How do i measure oil pressure and add more if required?
25-07-2008, 08:22 PM #2
Re: oil pressure and diff trip
If the compressor has got the oil pump, the pump pressure can be measured on the flare joint on top of the oil pump (usually). More often you may be interested in diff. pressure, so you have to subtract suction pression from oil pressure and make sure it is greater than specified by carlyle.
Oil is not added based on pressure or diff. pressure, but on quantity. For that, look at the sight glass, either in the compressor or oil separator, if any at all, and add until spec., usually half way of the sight glass.
25-07-2008, 08:39 PM #3
It seems you have a lot of LP/Oil related problems... or homework?
Haven't done a homework in few days so ...
Functions of oil hmmm...that's an easy one!
- Oil LUBRICATES!
- Transfers heat from where it is produced to where it doesn't hurt...except...
- May be used to move some parts hydraulically
- Cleans off metal particles produced by NATURAL use wear.
Not familiarized with Carlyle but you generally measure oil pressure with calibrated gages connected at the compressor crankcase and pump outlet.
If you are asking these questions PLEASE DO NOT ADD OIL INTO THE SYSTEM.
If the system has pressure it is done usually with a hand pump into the crankcase but several other places may be as good and several other methods may be as good.
25-07-2008, 09:35 PM #4
oil pressure in Carlyle's is low compare to other makes, therefore a lot of oil pressure problems.
On the other hand, the oil filter is internal and unreachable, [state of the art ]
Oil pressure controls should be set to a minimum.
25-07-2008, 10:14 PM #5
Welcome Mish.
LOG ONTO THE SITE LINK ATTACHED AND LOTS OF OIL RELATED QUESTIONS ARE ANSWERED.
ALSO SEARCH THE SITE AS THERE IS A VERY COOD COMPRESSOR BOOKLET
ON ONE OF THE PAGES.
STEVE.
SORRY HAD CAPS LOCK ON AND COULD NOT BE BOTHERED TO RETYPE ONCE I HAD REALISED.
NO OFFENCE MEAN'T.
http://www.carlylecompressor.com/cor...0.html#129081b
pressure switches
By wilks in forum Trouble ShootingReplies: 9Last Post: 02-05-2010, 07:22 AM -
Oil pressure problem of aerzen VMY 346 HR
By CrimsonK in forum Trouble ShootingReplies: 7Last Post: 09-03-2008, 07:08 PM -
minimum pressure diff. on TXV
By hiitsme in forum Trouble ShootingReplies: 10Last Post: 14-01-2008, 04:19 PM -
High Deferential Oil Pressure Alarm
By NNNNNN in forum Trouble ShootingReplies: 27Last Post: 24-12-2007, 01:06 PM -
TEV range & minimum pressure diff issue
By Lc_shi in forum FundamentalsReplies: 2Last Post: 24-04-2006, 04:32 PM