    Causes of LP Cut out
    Can anyone explain some reasons for my system tripping on LP. Its an industrial system in a food processing factory. Running with a Caryle compressor, 63amp. Also some typical reasons for high/low suction pressure and high/low discharge pressure.
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    May 2008
    weston
    348
    Re: Causes of LP Cut out
    It means your compressor is pumping more refrigerant than what's being injected into the evaporator.
    This may be caused normally by reaching temperature and has pump-down installed.
    This may be caused abnormally by:
    1. Expansion device not feeding enough refrigerant.
    2. Not enough thermal load in the evaporator.
    3. Not enough refrigerant in the system.
    4. High pressure drop in the suction line
    High discharge pressure is not the same as high condensing and would be mainly caused by high pressure drop between the condenser and the compressor.
    Depends on where you are measuring it could even be caused by having the discharge valve partially closed.
    Nov 2006
    veghel
    33
    5 frozen evaparator
    cheers
    3,856
    Lp switch out of adjustment or faulty.
    Blocked suction filters or strainers.
    Sep 2003
    ISRAEL
    72
    4,248
    LP will trip only if the pressure is below the set point + differential.
    The reasons can vary,
    At this point your skills as a fridgy are tested,
    Good luck.
    Oct 2003
    5,630
    34
    Good one Chemi
    GXMPLX's Avatar
    May 2008
    weston
    348
    Good luck.
    Not with the ones I work with! Correct setting would be just cut out. Cut in is Cut out - differential
    GXMPLX's Avatar
    May 2008
    weston
    348
    Good point! I have to remember this but havent't had a faulty one in some time!