    Question McQuay PSF Flooded screw reset problem



    Hi..any McQuay experts out there...am currently involved with a large site that amongst other chillers has several McQuay PSF twin parallel compressor flooded screws.
    The PCO controller presents a"Reset evaporater pump hours" for number two compressor...this presents as an alarm for the number two circuit and holds off the compressor....it is possible to reset the hours in the maintenance menu for compressor number ONE but there dosnt appear to be this facility in the maintenance menu for circuit TWO (press info button to change between circuit/compressor menus)...have been playing with the controllers for hours...any of you brains out there come across this or have a ready solution...I would be very grateful.best regards...Superheatman


    Not getting wiser at the same rate as I am getting older??

  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: McQuay PSF Flooded screw reset problem

    Quote Originally Posted by Superheatman View Post
    Hi..any McQuay experts out there...am currently involved with a large site that amongst other chillers has several McQuay PSF twin parallel compressor flooded screws.
    The PCO controller presents a"Reset evaporater pump hours" for number two compressor...this presents as an alarm for the number two circuit and holds off the compressor....it is possible to reset the hours in the maintenance menu for compressor number ONE but there dosnt appear to be this facility in the maintenance menu for circuit TWO (press info button to change between circuit/compressor menus)...have been playing with the controllers for hours...any of you brains out there come across this or have a ready solution...I would be very grateful.best regards...Superheatman
    Superheatman.
    Hi I will forward a manual to you via email.
    AS previously mentioned I can't post anymore.
    Take a look at page 29 and on.
    Explaining how to enable / test individual circuits ECT.
    Cheers Steve.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: McQuay PSF Flooded screw reset problem

    Superheatman.
    For some reason I have had the email I tried to send returned.
    "As unable to send."
    If you PM me with your email address I will try again!!!!
    Steve.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: McQuay PSF Flooded screw reset problem

    That's a known bug of the Carel software of that application. There's no easy workaround. The bug consists of an hour counter enabled for a underlying non-existing hardware. For this reason, the hour counter mask, which is correctly disabled for pump n.2, is not visible and therefore the hour counter can't be reset.
    The only workaround is to swap the pco address card between master and slave, mimicking n.1 as n.2 and vice versa. Quickly access maintenance menu, reset hour counter, switch off everything and swap back the address boards.
    Last edited by NoNickName; 24-07-2008 at 10:25 PM.

  5. #5
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Re: McQuay PSF Flooded screw reset problem

    Thanks very much to Grizzly and NoNickName for their replies...I will action as recommended....cheers again....John
    Not getting wiser at the same rate as I am getting older??

  6. #6
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    16

    Re: McQuay PSF Flooded screw reset problem

    Is this imformation still availible, I could do with it myself.

  7. #7
    Join Date
    Sep 2010
    Location
    Hungary
    Age
    40
    Posts
    10
    Rep Power
    0

    Re: McQuay PSF Flooded screw reset problem

    Hi,
    I'd like to ask manufacture codes for McQuay screw chiller, if you don't mind (for Control Panel Microtech II
    c plus)
    Best regards

Similar Threads

  1. flooded evaporator in screw chiller
    By Lc_shi in forum Technical Discussions
    Replies: 25
    Last Post: 05-07-2010, 05:37 AM
  2. SCREW Compressor Problem
    By lana in forum Trouble Shooting
    Replies: 17
    Last Post: 24-01-2010, 05:31 AM
  3. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 03:48 PM
  4. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 11:36 PM
  5. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •