24-07-2008, 01:08 AM #1
Foster 1/3 Lack of airflow problem
Evening/Morning all,
Just thought i would share this one with you, may help out a less expreienced engineer who hasnt come across it before. I was asked by another angineer to go and have a look at a Foster 1/3 case where the opposite end to the evap, the cabinet temp was 6/7 degrees c higher than the return air at the coil.
Turned out the centre set of drawers had the incorrect size drawer in it so was blocking the air off and short cycling inside the unit. Hopefully you can see from the picture the drawer size difference. Not one i would expect to see often, obviously someones changed the drawers at some point and only put a low sided drawer on the top on of the first set.
Hope this makes sense.
Regards
Fatboy