    x terminal paragon clock



    If a defrost termination / fan delay switch is stuck and continuously feeds a neutral to the x terminal on a paragon clock will the system still attempt to defrost or will this stuck neutral over ride the defrost?



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: x terminal paragon clock

    Quote Originally Posted by Drew View Post
    If a defrost termination / fan delay switch is stuck and continuously feeds a neutral to the x terminal on a paragon clock will the system still attempt to defrost or will this stuck neutral over ride the defrost?
    Drew
    Could you let me know what model you are refering to.
    Once Identified I may be able to help?
    Steve

  3. #3
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: x terminal paragon clock

    Hello Drew. On the Paragon clocks I used to use, the x terminal was fed with a live, either switched through a stat or pressure switch. Is Paragon the P990 or was that the venner ECL? I don't know, It's been over ten years since.

  4. #4
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: x terminal paragon clock

    Quote Originally Posted by Drew View Post
    If a defrost termination / fan delay switch is stuck and continuously feeds a neutral to the x terminal on a paragon clock will the system still attempt to defrost or will this stuck neutral over ride the defrost?
    Drew,

    If you're referring to the typical 8145 series Paragon timer, when the defrost/fan switch sticks with power going to the X terminal the system will not go into defrost and the fans will not come on.
    Last edited by powell; 23-07-2008 at 11:07 PM.

  5. #5
    Join Date
    Jan 2009
    Location
    jax, fl,
    Posts
    23
    Rep Power
    0

    Re: x terminal paragon clock

    Is the delay bad? or are you trying to determine why your defrost is terminating. The termination solenoid on the back of the 8145-20 could be swelled up (burnt) and that will terminate the defrost every time, power or no power to it. If the delay is good the warm evaporator will cause termination. Inspect the back of the timer. Unhook x and see if it will go into defrost and stay. These are the only things that will cause a termination problem

Similar Threads

  1. paragon defrost timer 8145-20
    By kengineering in forum Commercial
    Replies: 4
    Last Post: 20-10-2009, 02:55 AM
  2. Hermetic compressor terminal blown off
    By racknovice in forum Supermarket Refrigeration
    Replies: 4
    Last Post: 17-09-2009, 07:54 PM
  3. AMF/Venner Clock
    By Brian Vx in forum Trouble Shooting
    Replies: 4
    Last Post: 04-03-2008, 12:23 AM
  4. Venner time clock
    By LRAC in forum Commercial
    Replies: 2
    Last Post: 08-10-2007, 08:42 PM
  5. Daikin Schedule Time Clock
    By breckle in forum Air Conditioning
    Replies: 1
    Last Post: 12-06-2007, 11:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •