    PRV Calliberation problem



    We have YORK (model no.: YTJ3C3E25CNJ) Centrifugal chiller.
    Its vanes are NOT calliberating and its NOT running beyond 65%.
    We had changed vanes motor, ACC board but problem is same.
    please guide to overcome this problem.

    Thanks in advance.



  2. #2
    Nik BG's Avatar
    Nik BG Guest

    Re: PRV Calliberation problem

    Hi Bhasadu.
    I've been on J4 and J3, but honestly, i have never seen them on normal operation PRV opened more than 70%. Do you reach the set point? How are the pressures? See the liquid level. How much is HGBy-pass v/v opened.I ask because everything is complex and connected. Can you open it manualy 100%?By the way you can calibrate by means of the levers, and in fully closed position of PRV on the display you should see 5-6%. That's because vanes are never totaly closed, even in end position.

Similar Threads

  1. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  2. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  3. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM
  4. Oil carry over Problem in Refrigeration Unit
    By imranmd in forum Industrial
    Replies: 1
    Last Post: 27-08-2007, 03:09 PM
  5. Hot start problem on VRV REYQ14M7W1B
    By cool#9 in forum Air Conditioning
    Replies: 9
    Last Post: 20-04-2007, 08:09 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •