Page 1 of 2 12 LastLast
Results 1 to 50 of 52
    London
    57
    82
    Angry Fujitsu Aoy30 Lnawl
    Folks i installed a brand new fujitsu cassette type and all ran well for a few weeks and suddenly the customer complained ,that a loud noise from the outdoor unit.When there to do a bit of troubleshooting and found Active Filter Module gone.What is the possible cause for that.I need some input as i am affraid to fit the new one and the same thing to happen to the new one as well.
    If power surge then some fuses will blow but in this case i found all fuses O'K.System error code 0:01 E
    Dec 2006
    Mansfield
    57
    231
    Re: Fujitsu Aoy30 Lnawl
    Check your outdoor fan motors, I've had the same fault myself.
    PP
    London
    57
    82
    Quote Originally Posted by p_p View Post
    PP
    Yeah i definitely will check the fan motor,thank you for the advise.As a matter of fact tomorrow morning i am supposed to change it.I got a manual from Fujitsu technical guys and will check resistance on windings of the fan motoer as well.
    Dec 2006
    Mansfield
    57
    231
    Hi Subcontractor
    Did you read my thread AOY45LATN. Posted friday updated today.
    Find it and read all posts sounds like you have the same fault.
    Fault code that doesn't relate to a fault. ( Worst Kind ) even Fujitsu had no idea.
    Good Look
    PP
    Dec 2006
    Mansfield
    57
    231
    The unit i worked on diagnosed by led so i wired a remote to it to try and get a numerical fault code and got the same code as you.Take the blades of the motors and make sure they spin freely, check resistance, insulation etc
    Let me know how you get on if you pm me I'll send you my no.
    PP
    Dec 2006
    Mansfield
    57
    231
    I received your pm but can't reply as you have chosen not to receive pm's
    I have the no for fujitsu's top split guy if you need it, but can't post on here, you will have to pm me your email.
    PP
    London
    57
    82
    PP
    I checked so many times ,yes it is ticked i allow others to pm me but why this is happening don't have a clue.
    Dec 2006
    Mansfield
    57
    231
    Contact WEBRAM He will be able to sort it.
    PP
    Oct 2001
    Nottingham UK
    5,668
    Guys
    If you click on the username and view the Public Profile, there is a link to send a message, (top left, just under the Avatar).
    Either a Visitor message or a Private Message.
    Dec 2006
    Mansfield
    57
    231
    How did you get on mate!
    PP
    London
    57
    82
    Angry Re: Fujitsu Aoy30 Lnawl
    I fitted the p.c.b. and the system ran for 10 min cooling good and suddenly the circuit breaker went off.Same error 0:01 E and i lost the second p.c.b. as well.We all learn ,you know, simply this is the last Fujitsu that i buy . I'd better cut from my f***ing profit and fit a top make so make more and more happy cutomers (recommendations)and i have to go back dismantle the outdoor unit and fit a new one.It s in a tight place ....jeez give me power to the brain cells. Now the customer don't wanna talk to me as he thinks that i sold a ****ty equipment. ******* unit i checked the fan motor 540 k oms ,450 koms,540,540 and between the red one and violet one 0 . If the system runs for a while and do not show error codes and it simply happens after time i presume it is something to do with the insulation.I checked the compressor with insulation tester It is O'K.
    no not happy ,bad day ....
    Dec 2006
    Mansfield
    57
    231
    Did you want the no for Fujitsus main man ?
    Have you tested the inverter, metered the interconnecting atc, what pulsed voltage on no 3 due you have.
    Shame your'e not a bit more local i would happily come and give you a hand.
    keep us posted
    Last edited by frank; 24-07-2008 at 08:54 PM. Reason: contact details forwarded by PM
    Jul 2007
    Australia
    1,845
    You can't test the motors by ohms, they are dc fans and run like an inverter compressor. It's all diode testing you need to do.
    I've dropped out of the fuji game, so I have limited info and rusty memory. But any good tech that works for Fuji can help you out. Get the number from P_P, or maybe some fuji experts on the forum can help you if they read this.
    As I said before, here the installers don't deal with warranty, the manufacturers do, so theres a lot of information they've got in troubleshooting for the companies they subcontract.
    Unfortunately I don't have anything on inverter cassettes, but I'm sure any current fuji techs do.
    London
    57
    82
    Paul in this case the readings will be only going in one direction like every normal diod.As i measure the oms in both directions why the fan is still running after fitting a new active power module.(ran for ten min and gone again with error E :01)
    I think this is something to do with overheating of the fins which are supposed to cool the lil bast**d.
    Jul 2007
    Australia
    1,845
    I've measured indoor fan motors with decent ohm ratings before, and still they blow the PCB or fuse, and that's conventional AC fan motors. To get ohm ratings that don't seem shorted means nothing.
    But your problem of running for 10min is new to me, so I don't confess of being an expert in the matter.
    All I remember in testing fuji fan motors is testing the red and black wires in a diode test mode, should be open circuit one way and about 0.8-1 volts the other. And testng the white and black wires, should be 0.8.v one way and 1.6v the other. If any shorts, ie 0 to under 0.8 V shows up, you need a new fan motor.
    I'm sure theres a fuji tech is living in your neck of the woods, get in touch with them lke P_P suggested, fuji don't make that bad of a product, they are huge sellers down here, similar to mitsubishi, and they have the tech knowledge and experience to back it up, they've been in the game longer than most companies.
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by SUBCONTRACTOR View Post
    It is obvious that you managed to cure consequence and not the cause of problem here. I don't see reason why are you blaming manufacturer for that!
    Error 0:01 mean: Indoor unit doesn't accept the signal from
    outdoor unit.
    Of course that indoor is not accepting signal, when fuse and/or outdoor PCB is blown!
    Checking what part of outdoor PCB has malfunctioned gives you the clue about what part is faulty (compressor, fan, solenoid or, maybe it is power source problem). By the description, my best bet is on compressor.
    May 2008
    170
    Ive just had a similar problem, system worked for 2 months, then.....
    Outdoor board blew. It was the microchip which is on the underside of the board, it also blew the 25A fuse on the outdoor unit.
    Checked compessor-all okay.
    Replaced outdoor and indoor board and still get error 0.01.
    We are going to change all the boards, again
    If you ask me, I think Fujitsu are complete bottom end quality and always have been.
    Been working with these for about 12 years for a company and the faults with PCB's and compressors never seem to end.
    Jul 2007
    Australia
    1,845
    So the IPM blew.
    Did you megger the compressor?
    The IPM normally only goes when the compressor is shorted, and you NEED to megger test it.
    Also could have a fault with the AFM.
    Swapping boards and finding it still doesn't work, doesn't mean you get another board and try again.
    Something is wrong with the system and you need to diagnose it. Sounds like the outdoor is not powering up and I'm going to guess it's the AFM, could be something else though.
    I don't think I ever have got a faulty replacement PCB from fujitsu, if I did, maybe 1 out of 400. Some other brands...
    But I know where you're coming from regarding inverter reliability.
  19. #19
    London
    57
    82
    Quite a few answers,thank you guys this is very helpful as this is my weak point the electronics.An update :Today we replaced an active power module and condenser fan motor.We vacced the system and put a 500 g just to have some gas in it 'cause i was not sure about the performance.We powered up the system(the voltage was measures before of course 229 V) and the circuit breaker goes "bang".That is it when the system was running for 10 min then bloody we had some fault codes ...now it just go straight bang.
    We detached the interconnecting cable the cond. fan motor and the compressor cables and we powered up the outdoor unit.The circuit breaker switched off again.
    Do you thing that if the pcb diod bridge is faulty it will be able to trip fuses.??
  20. #20
    Split Croatia
    57
    6,151
    36
    Try with disconnected IPM board (orange W28 and brown W29 wire)!
    If holds, you have damaged IPM board! If not, you have power supply PCB damaged.
    That doesn't necessary mean that something else is not faulty (compressor), that's only consequences of other faulty part/s.
  21. #21
    Jul 2007
    Australia
    1,845
    You have a serious short there. Fujis normally don't trip the breaker unless the compresor is bad.
    The way they normally work is : control system shorted = they won't even power up, they detect the short and cut the power to the outdoor unit, giving you a comms 01 error. AFM, IPM, Diode bridge etc will do this, you wont get a c/b trip, for most of the control side faults, just a comms error because the unit hasn't powered up because it detected the short and shut the system down.
    If the motors are shorted, it may power up, then draw high current through the faulty motor and trip a breaker.
    Always a first for everything though.
    But start with a megger test the compressor, diode test the fan motor, diode test of the IPM.
  22. #22
    London
    57
    82
    When the unit was on the floor i measured the compressor with a MEGGER it was very good.
  23. #23
    London
    57
    82
    Since all those problems with the condensing unit, i forgot to tell you we don't have a single fuse on a p.c.b. blown.Even the last time when the interconnecting cable,fan motor and compressor were disconnected it trip the 240 V circuit breaker without blowing any fuse on the p.c.b.
  24. #24
    Split Croatia
    57
    6,151
    36
    What is that circuit breaker size and curve?
    On board fuse is 25A B curve. If your instalation circuit breaker is, say 20A B curve, it is normal for him to act first.
  25. #25
    Dec 2006
    London & Surrounding Counties
    122
    Thumbs up Re: Fujitsu Aoy30 Lnawl
    Nike123's on the right path in my view!
    I always fit curve C spec MCB's on Inverter installs because of nuisance Inverter noise related tripping issues. I haven't read through the entire posts on this thread so apologies if this has been suggested, and please don't think I'm teaching you to suck eggs here but.....
    1) What size supply cable are you using?
    2) Any rotary isolators in the circuit? If so bypass them and put them in a suitably sized connecting block for the purpose of testing. Somethings down to earth so start eliminating such like.
    3) How many amps does the CCU pull?
    4)Are you sure your not exceeding the load the electrical instalation is designed to. Theres still fault current being detected by the protective device if you've disconnected compressor etc and it's still tripping!
    5) Failing all that. Change the breaker......I had faulty breakers do just this when there on the way out especially after the amount of tripping this protective device has under gone lately it would be wise.
    Essentially, go back to basics. You've changed most of the components in the outdoor unit, it just doesn't add up mate it's an earth fault..............definately no trapped wires in the CCU casing anywhere-I've fallen foul of this too??
    Best of luck.
    J.
  26. #26
    Nov 2006
    Cheshire, UK
    56
    360
    Inverter units should not require a Type C breaker by default.
    You cannot just dump a 'Type C' MCB in for a 'Type B' without checking the Zs complies at the 'Point of Utilisation'!
    He who dies with the most Toys, WINS!
  27. #27
    London
    57
    82
    sparky supplied and fitted twin and earth 4 mm grey fat type electrical cable to a rotary switch by the machine and the circuit breaker is not 25 as it should be but 32 amps C type.I know that B type is better for inverter systes.
    A fujitsu representative will turn up on site soon ,i will keep you updated.
  28. #28
    Dec 2006
    122
    Wink Re: Fujitsu Aoy30 Lnawl
    Quote Originally Posted by sinewave View Post
    Who's suggesting he does? I stated that in my installations I design the supply around a type C MCB. I haven't told him to replace his with one. I'm raising the point because regardless of whether he's got a type B, C or whatever, he's essentially an earth fault or a defective MCB from what I can gather.
    J.
  29. #29
    Dec 2006
    122
    What was the outcome on this in the end then??
  30. #30
    foundahobby's Avatar
    foundahobby Guest
    Anyone suggest running a 100amp delicated line to the outdoor unit and see what blow's up?
    Now, just trace the smoke to the faulty part.
  31. #31
    London
    57
    82
    Quote Originally Posted by foundahobby View Post
    Main p.c.b. on the condensing unit trips the fuse.Ordered a new one and waiting patiently to fit it.Let's see what happens.I will keep you updated
  32. #32
    christian's Avatar
    christian Guest
    Hello subcontractor,
    Just some quick advise.
    Make certain that the pcb is securely fastened down with its original fixings so that there is good contact between the pcb and heatsink fins.
    Otherwise it will blow the board in seconds!
    I apologise if sounds like i'm teaching you how to suck eggs.
    Good luck!
  33. #33
    christian's Avatar
    christian Guest
    Also to make sure there is no manufacturers wrapping attached when finally installing.
    There is sometimes small pieces of foam protecting electrical circuits that need removing prior to installing.
  34. #34
    Jan 2004
    Queenstown, New Zealand
    48
    In original post you saiud that 'that a loud noise from the outdoor unit'
    What kind of noise? may be root of problem?
    It is pratice here to replace ALL the boards in an outdoor unit if one fails especially inverter boards.
  35. #35
    London
    57
    82
    Quote Originally Posted by sighman View Post
    Not me,the customer heard loud "bang" and actually the active power module gone.Of course other p.c.b. gone as well changed them one by one and finally it stopped blowing fuses....sad because it took all the p.c.b. and two months scratching heads.
    The real cause guys was the heat sink overheating and killed inverter p.c.b.
    The ambient around the outdoor unit is quite high and at peak moments it goes very ,very high.
  36. #36
    May 2008
    101
    Vaillant would have sorted this themselves, without you ever having to have to go back to site!
  37. #37
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by Prince Vaillant View Post
    Are you saying that Vaillant would fix it self without human intervention? Are they installed some nanobots in the unit?
  38. #38
    May 2008
    101
    lol no mate, the warranty covers mechanical breakdown. If a part is faulty on the system they will send their own engineers to sort it. So the customer has a "Vaillant" engineer turn up to fix it. While you get on with your next job!
  39. #39
    Oct 2001
    Nottingham UK
    5,668
    Quote Originally Posted by Prince Valliant View Post
    This sounds expensive for Valliant as a Company.
    How do you control the installation to ensure that a proper job has been done?
    With some of the Numpties I've seen installing, breakdowns are only a few months away
    Who picks up the tab?
    Do you monitor warranty callouts to find a pattern with certain companies?
  40. #40
    Mar 2006
    Lancashire
    1,859
    28
    Haha no reply, he musn't have thought about that
    Marc
  41. #41
    Mar 2007
    Warwickshire UK
    723
    21
    Valliant installers are mainly domestic plumbing & central heating 'engineers'
    They are trained by Valliant to install split systems but would not have any idea how to trouble shoot or solve technical problems with the equipment.
    So to support the product Vailliant have to carry out warrantee repairs.
    As we suspect the equipment is from the China Haier factories the Vailliant UK service department will be busy if & when they start selling any significant number of split systems.
  42. #42
    Dec 2006
    Mansfield
    57
    231
    Hi All
    Just to say we have installed quite alot of vaillant kit for ourselves and direct to vaillant, we offer it as a budget alternative to mitsi and I have to be honest we have had only 1 system with an intermittent fault.
    Jason allen, vaillants tech guy came out, a new outdoor was fitted the next day, problem over.
    Thats pretty good service to me.
    PP
  43. #43
    May 2008
    170
    Well, what a nightmare you had. I've had some head scratching with pcb's of late. Is it a good idea then to replace all pcb's in an outdoor unit if only one has failed. I don't think the customer is going to be very happy about this.
  44. #44
    Oct 2001
    Nottingham UK
    5,668
    Now that sounds like taking a hammer to crack a nut.
    Why replace the outdoor unit to solve a problem? Aren't Vaillant able to fault find properly?
    Seems an awfully expensive way to run a business.
  45. #45
    Dec 2006
    Mansfield
    57
    231
    I'll speak to jason and ask him to reply to your last post ken.
    PP
  46. #46
    Jan 2007
    They probably replaced the outdoor unit as they had no spares in the UK. They would have to take a whole unit from stock to obtain a PCB then it cannot be resold as they probably do not have the facility to rebuild and restock. Not a good way to run a business!
  47. #47
    Dec 2006
    Mansfield
    57
    231
    Maybe you and frank should run vaillant, I bet they don,t realise what they are missing.
    For people who have nothing to do with vaillant you seem to know an awfull lot ( or not ) remember little or no knowledge can be dangerous.
    Have a nice day, I,m sure Jason will be here soon!
  48. #48
    Jul 2007
    Australia
    1,845
    It's the same way it's handled here, manufacturer's tech or contracted service agents handle warranty.
    That includes fujitsu, panasonic, LG, mitsubishi, samsung etc.
    All but daikin basically and the new/cheap/small brands that don;t have service agents, they just deal with the people that sell or installed them.
    If the install is bad, warranty is not given and the customer is billed for any repairs.
    Most manufacturers use service agents, so the agent is the one screwed over if no one pays, that's how the manufacturers stay profitable because they don't eat all the loss. ie don't pay the service contractor for the initial diagnosis when installer fault is found. It's up to the agent to bill the customer, and up to the customer to seek compensation from the installer/retailer.
    As far as swapping whole units, that's mainly done by non service agents, ie installers who want to be paid for the install they just did.
    Complete whole units as spares are very rare here fr the mainstream brands, they mainly are imported JIT straight to resellers, so the manufacturers have no units to spare, just parts and good service agents diagnosing things properly. Installers have better access to replace whole unit's and often they do just to get their money from the customer, then they try their luck getting the unit cost reimbursed from the manufacturer.
    It is a bad system IMHO, it encourages the shoddy, backyard, dissapear never to be seen again installers that don't have to worry about doing the job properly, don't have to know how to repair anything, or even how a/cs work. They take their money and run.
    If the unit breaks down, the customer has to contact the manufacturer or service agent, who may not honour warranty if the install is bad.
    All except Daikin of course, who only sell through there own service agents so they have a reputation for reliability, because only people knowing what they are doing and know that if they stuff it up, they have to fix it themselves during the warranty period anyway.
    Do the other brands lose money? Probably, for one, their units are sold at electrical retailers offen discounted. Secondly, any sparky or plumber can become an installer here, and often does a crap job installing them. Thirdly, the customers get annoyed at long wait times for repairs to be done, or for being billed by the repairer if the install is bad. So brand image suffers.
    Last, the manufacturer has to pay salaries for their own engineers, and for service agent techs to run around and diagnose all the bad installs.
    It's the manufacturers fault though, allowing anybody to buy and install their product.
    They could build up a network of specialist sellers and preferred installers, run their own courses for those people etc.
  49. #49
    Jun 2008
    Nottingham
    Hi All,
    I have read all comments made about Vaillant.
    Firstly many thanks to P-P. For trying our units and the previous messages.
    I have been in the industry for 22 years starting in the refrigeration game then on to Air Conditioning firstly on install then on service so I believe I do know a thing or 2 about fault finding.
    The decision to change the outdoor unit was purely a commercial decision.
    The PCB had an fault which only showed up now and then this caused the compressor to over heat.
    Changing the PCB only was not an option as I did not know if the compressor had been damaged.
    The cost of an outdoor unit compared to a compressor and PCB is much cheaper.
    So a hammer to crack a nut is far from the truth.
    The end result was a happy customer and a happy installer, what more can anyone ask.
    We do have spares in the uk, in Derbyshire.
    Please try the Vaillant equipment before judging it.
    Thanks for reading.
    Jason
  50. #50
    Jul 2007
    Australia
    1,845
    Argh! You valiant people are mulitplying!
    Got nothing to say about valiant because they aren't sold here. So I'm not knocking the brand or your explanation.
    I agree with what you say, if you can replace a unit easily because you have stock, it's always cheaper than trying to stuff around and swap bits.
    Think about it, paying a service tech to reclaim, weld and recharge at current western world rates with the techs own prices for welding, refrigerant, labour rates etc is always going to cost a manufacturer more than fitting a premade cheap assembled unit from china. That's not a direct attack at the brand either, because mainy of the mainstream japanese brands are made in china or other southern asian countries now too.
    I wish the mainstream brands I serviced had spare units for me. It's a lot easier to change a unit than change a compressor, inverter PCB and reversing valve and possibly adding a drier.
    In fact, I've heard of customers, installers and techs falling in love with brands that will just change over a unit, so I don't know why there was criticism in that regard here.
    I've worked on mainstream brands that can't get units as mentioned before, or even some times can't get spare parts.
    But I've also come acros brands that aren't in the "big 6" that you can't get any help with, as there's boat loads of no name asian stuff dumped in the au market.
  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Last Post: 26-08-2009, 05:06 PM
  2. Fujitsu or not?
    By LRAC in forum Air Conditioning
    Last Post: 29-08-2007, 09:45 AM
  3. desperately seeking fujitsu
    By rbartlett in forum Air Conditioning
    Last Post: 04-08-2007, 09:06 PM
  4. Fujitsu Cassette not running
    By Climateman in forum Air Conditioning
    Last Post: 22-06-2007, 10:39 PM
  5. R22 Fujitsu FCUs on new Inverter Multi-Condenser?
    By Makeit go Right in forum Air Conditioning
    Last Post: 09-01-2007, 11:22 PM
