  1. #1
    Sumoguy's Avatar
    Sumoguy Guest

    Cool Need advice for proper ventalation and cooling for busy Irish Pub(400 people)



    Pub has rooftop H.V.A.C. system that handles load during normal operating hours. On nights with max. occupancy (400 people) Pub becomes like a sweat box. Pub is on bottom floor of 3 storey office building. Fresh air ventalation, exhaust and cooling could possibly be done with through the wall units and ductless mini-splits. What`s the best cost effective and long term solution for the Pub....Cheers from Canada...



  2. #2
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    pub space was probably originally set aside as office space.

    Where are you in Canada, different answer for Vancouver as opposed to winterpeg
    Take the V out of HVAC and you are left with a HAC job

  3. #3
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Water cooled condenser?

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    If you use the outside air for cooling at night you kill two birds with one stone, reduce the temp and change the air, you will need many air changes per hour.

  5. #5
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Quote Originally Posted by chemi-cool View Post
    If you use the outside air for cooling at night you kill two birds with one stone, reduce the temp and change the air, you will need many air changes per hour.
    All in all I would agree but-

    That will naturally work during the cooler nights, in peak summer trying to cool a building with 20+ C air is likely to fail
    (depending upon location)

    Then there is noise breakout which fans (esp in night clubs) always suffer from

    Multisync
    London

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    I wonder how many nights per year, you will get over 20°C anywhere in Canada.

    Fans do not have to be noisy, there are quite fans, I will get you a link later.

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Hey

    Hold on there a minute, irish pubs=lots of drink, hence lots of sweat and lots more drink, cool the place effectively and watch the profits plummet

    al

  8. #8
    Sumoguy's Avatar
    Sumoguy Guest

    Talking Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Thx for reply guys....Pub is located near Toronto, and if water cooled unit was installed would have to be on a closed loop system that might become too costly for Pub? The additional cooling would be required for 6-8 hours a night on Thurs, Fridays and Saturdays. Does 200 Ft cubed/sec (6m cubed/sec) of fresh air ventilation and approximately 18-20 tons (72KW) of cooling sound reasonable...or is it too much?

  9. #9
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    I tend to agree with Al as a lot of my Customers with nightclubs only want partial cooling for this very reason.Make the kids sweat and keep the profits up.

  10. #10
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    would a Lossnay system be any good (LGH series) free cooling

    http://www.mitsubishi-aircon.co.uk/d....asp?id=120065


    https://www.mrslim.com/Products/Cate...tCategoryID=23

    other manufactures are available
    Paul


    "KEEP IT COOL"

  11. #11
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Sounds about spot on Sumoguy but let your client think about the other point.

  12. #12
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    400 people = 4000 litres per second minimum.
    Have a look at these.
    This is the type of thing you need.
    If cash is a bit tight, you might look at using some long cased axial fans, with a few silencers.

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Take a look at the Fedders Addison web site, Addison was making superb 100% fresh air packages,

  14. #14
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Quote Originally Posted by Sumoguy View Post
    Thx for reply guys....Pub is located near Toronto, and if water cooled unit was installed would have to be on a closed loop system that might become too costly for Pub? The additional cooling would be required for 6-8 hours a night on Thurs, Fridays and Saturdays. Does 200 Ft cubed/sec (6m cubed/sec) of fresh air ventilation and approximately 18-20 tons (72KW) of cooling sound reasonable...or is it too much?
    Well they are already open so it does not sound like there is going to be a building permit involved, but you should still give them some air, at least 10 CFM per person, good thing they banned smoking in Ontario.

    So in the heat of the summer, you can get a worse place dewpoint of about 71 in the TO area.

    To do this job right you will need reheat, probably 35 to 40 tons of cooling, then reheating.

    I would look size the system to handle the load of the people only plus the ventialtion. Any heat from from lights bar equipment will be your friend as you will need the reheat in there.

    I would have a system that could take about 4000 CFM of outside air and perhaps 1000 CFM of return air. You need a fair bit of exhaust as well.

    This sounds like it will blow your budget to do it right, but I have some Engineered Air equipment that could handle this doing a night club in the Caribbean.

    When it is not a heat wave out, something with a lot of outside air will cool it fine, they will need cooling in the winter as well.

    Otherwise, slap in some exahust and as many mini-splits as they can afford.

    No matter what you do it is going to be hot and sweaty this time of year. But when they are hot, they drink more.
    Take the V out of HVAC and you are left with a HAC job

  15. #15
    Sumoguy's Avatar
    Sumoguy Guest

    Smile Re: Thanks ALL

    Thanks guys..first time I ever posted on forum...its pretty cool site...look like there going for the ductless with fresh air and exhaust...told them to think of putting proper proper air exchanger if they plan on staying in that location for a long time.

  16. #16
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    I have attached a picture of Jet air diffusers, these will throw air over 20 M.

    They come in diameters from 6" to 16"
    Attached Images Attached Images

  17. #17
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    Quote Originally Posted by chemi-cool View Post
    I have attached a picture of Jet air diffusers, these will throw air over 20 M.

    They come in diameters from 6" to 16"
    Hello Chemi

    I used the exact same jet difusers to cool a large high ceiling bakery, 19m throw, work very well.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  18. #18
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Need advice for proper ventalation and cooling for busy Irish Pub(400 people)

    punkah louvers
    Take the V out of HVAC and you are left with a HAC job