    Help me 4 selection of DWM compressor with R22



    Is there somebody help me ?
    I want to make a freezer with -40 C ,
    single stage , R22 refregerant , single phase power,
    about 0.8 cubic meter volume 80W 100H 100L Cm, capacity about 150 KG of stuff,
    speed of cooling rate is 4 hours +40 to -40, ambient temp. is +40 C, isolation is 7.5 Cm rock wool.



  2. #2
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Help me 4 selection of DWM compressor with R22

    at -40sst and 45sct you are asking a lot out of an R22 single stage machine, you would be better off with 2 stage or a different refrigerant.

    you can download copeland select from here: http://www.ecopeland.com/download.cfm?what=download


    you say load is 150kg of "stuff", what sort of "stuff"?
    ...and she said "give it to me you big fridgie"

  3. #3
    ayat's Avatar
    ayat Guest

    Re: Help me 4 selection of DWM compressor with R22

    Thank you for your advice, and about stuff I think we can simulate it by 150 Kg of iron.

Similar Threads

  1. Capillary Tube Selection
    By lana in forum Commercial
    Replies: 17
    Last Post: 12-03-2009, 05:57 PM
  2. Selection of capillary tubes
    By patrickj in forum Commercial
    Replies: 11
    Last Post: 19-06-2008, 02:45 PM
  3. condensing unit selection?
    By ibraheem in forum Technical Speculations
    Replies: 0
    Last Post: 28-05-2008, 06:06 PM
  4. Replies: 3
    Last Post: 19-02-2007, 04:22 PM
  5. selection of centrifugal fan
    By watana in forum Air Conditioning
    Replies: 0
    Last Post: 14-09-2003, 04:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •