    Mass Flow Rate with Big Condenser



    What will be the effect of Bigger Condenser in the system as compare to sub cooling and mass flow rate?



  2. #2
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: Mass Flow Rate with Big Condenser

    same charge?

  3. #3
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Mass flow rate has to do with compressor and expansion device.

    There are two opposing effects:
    1. Lower condensing improves compressor flow (less reexpansion).
    2. lower pressure differential at expansion device -> less refrigerant fed->lower suction pressure->higher specific volume at compressor suction.

    What wins depends on compressort type, model, refrigerant, expansion device...

    Subcooling should improve

    david2008 has a point depending on how big the condenser is. Just imagine that inner volume is so much bigger that flow turns from turbulent to transitional or laminar, it would condense much worse!

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Mass Flow Rate with Big Condenser

    The effect of lowering condensing pressure is much bigger than the lowering of the evaporating pressure.
    We have some packs running in winter with less than 4 bar (58 PSI) DP over the Danfoss TEV's. We achieve COP's over 7 under these conditions!

    Will subcool not be more dependent on the condenser coil construction? Real controlled subcooling in a condenser can only be done if the second-last bends in the coil are going upwards so that you make a small liquid collector.
    Of course, the sooner the liquid is condensed - in a bigger condenser, the gases are already condensed somewhere in the middle of the coil - the more it will then subcool.

    If we need a real subcooler, we install a supplementary coil after the liquid receiver or order a condenser with an integrated subcooler.
    This is a good example of a real subcooler.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Thumbs up Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Peter_1
    We have some packs running in winter with less than 4 bar (58 PSI) DP over the Danfoss TEV's.
    This is exactly what you want to have happen as often as you can (and as long as you can)!

    From a simple viewpoint, you want to keep the discharge pressure as low as you possibly can. This helps to lower the kW power input (the demand power) and the kWh.

    If you need a larger condenser, then use one that offers a cost-effective solution to lowering the discharge pressure.

    The mass flow will only change incrementally by using a larger condenser. The mass flow is determined by the operating conditions the compressor works in.
    If all else fails, ask for help.


  6. #6
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Thanks a lot to ALL!!

  7. #7
    Join Date
    Mar 2008
    Location
    Belgium
    Age
    40
    Posts
    32
    Rep Power
    0

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Peter_1 View Post
    The effect of lowering condensing pressure is much bigger than the lowering of the evaporating pressure.
    We have some packs running in winter with less than 4 bar (58 PSI) DP over the Danfoss TEV's. We achieve COP's over 7 under these conditions!
    Isn't it also that you need a minimum DP over a TEV and isn't 4bar a little low?
    Also if you have very low discharge in winter, than liquid will also be subcooled very much... and it is possible that you don't have liquid-gas after expansion, but 100% liquid... no?

    Also couldn't you have the problem of very low suction pressures in winter with a very low discharge? You need to keep a certain min, no??

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by majo
    Isn't it also that you need a minimum DP over a TEV and isn't 4bar a little low?

    [...]

    Also couldn't you have the problem of very low suction pressures in winter with a very low discharge? You need to keep a certain min, no??
    All of this depends on the TEV's ability to react to the lower DP, while controlling the evaporator superheat. Balanced port TEV's do this quite well.

    Obviously, if the valve cannot operate at the low DP then the suction pressure would decrease. This is all based on the design of the system and the components used to achieve this lower operating conditions.

    Quote Originally Posted by majo
    Also if you have very low discharge in winter, than liquid will also be subcooled very much... and it is possible that you don't have liquid-gas after expansion, but 100% liquid... no?
    It is conceivable the liquid would have a lot of subcooling. This would simply increase the Net Refrigerating Effect of the liquid and reduce the run-time required of the compressor. While the amount of flash gas would be considerably reduced, the TEV should still be controlling the evaporator superheat.
    If all else fails, ask for help.


  9. #9
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by US Iceman View Post
    All of this depends on the TEV's ability to react to the lower DP, while controlling the evaporator superheat. Balanced port TEV's do this quite well.
    Generally speaking, what is the number for low DP? 100psi? For low DP system, is the solution to use a Balanced port TEV?

  10. #10
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Peter_1 View Post
    Real controlled subcooling in a condenser can only be done if the second-last bends in the coil are going upwards so that you make a small liquid collector.
    What is the difference between upwards and downwards? They have the same pressure, so the same function for TXV?

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by David2008
    Generally speaking, what is the number for low DP? 100psi? For low DP system, is the solution to use a Balanced port TEV?


    A reasonable lower limit for DP is what Peter said. I have had some systems operating at less. And yes, I would use balanced port TEV's on ANY direct expansion system.
    If all else fails, ask for help.


  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by David2008
    What is the difference between upwards and downwards?


    You must be kidding? Up means up and down means down. (sorry, couldn't resist)

    The difference is what you call a liquid seal. If you drain downwards the liquid may not stay in the condenser to achieve any subcooling.

    If you provide a liquid seal, the liquid has a place to collect so that it can subcool.

    Condenser manufacturers handle this differently in their designs.
    If all else fails, ask for help.


  13. #13
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by US Iceman View Post
    [/size][/font]

    You must be kidding? Up means up and down means down. (sorry, couldn't resist)

    The difference is what you call a liquid seal. If you drain downwards the liquid may not stay in the condenser to achieve any subcooling.

    If you provide a liquid seal, the liquid has a place to collect so that it can subcool.

    Condenser manufacturers handle this differently in their designs.
    Thank you.

  14. #14
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: Mass Flow Rate with Big Condenser

    A bigger condenser could have all of the following positive effects on a refrigeration system because it would have a lower condensing temperature.
    1. A better refrigeration effect
    2. A lower mass flow rate
    3. A lower volume flow rate
    4. A higher COP
    5. A lower condenser heat of rejection
    6. A lower condenser temp difference
    7. A lower condenser split
    8. A lower KW/ton
    9. higher efficiency and a happy compressor and it's components

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Quote Originally Posted by majo View Post
    Isn't it also that you need a minimum DP over a TEV and isn't 4bar a little low?
    Also if you have very low discharge in winter, than liquid will also be subcooled very much... and it is possible that you don't have liquid-gas after expansion, but 100% liquid... no?

    Also couldn't you have the problem of very low suction pressures in winter with a very low discharge? You need to keep a certain min, no??
    You need indeed a certain minimum Dp over the TEV but 4 bar is also given by Danfoss themselves.
    And we have the proof it works (even 3.5 bar)
    Look ones in the Danfoss tables and you will see that the capacity doesn't decrease that much with decreasing pressures.
    You say that SC increases during winter which is true but this increases also the capacity of the TEV and compensates a little for the lower DP.
    In theory, you can only have full liquid after the valve if you SC liquid to evaporating temperature.
    But I think this won't give any problem.
    Last edited by Peter_1; 21-07-2008 at 08:02 AM.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Quote Originally Posted by US Iceman View Post
    [The difference is what you call a liquid seal. If you drain downwards the liquid may not stay in the condenser to achieve any subcooling.
    Indeed, that's the correct expression, liquid seal

    We had - perhaps 20 years ago - some condensing units running (Copeland with hermetic piston DCRQ's running), evaporating at 5°C.
    The compressor could handle this perfectly but the condensers were ways too small. So we installed in line a second condenser and this decreased HP almost nothing. Only if we placed one in parallel, then it resulted in a serious HP decrease.
    In line, what we made was a huge subcooler which didn't increase the condenser area, so HP remained almost unchanged.
    Last edited by Peter_1; 21-07-2008 at 02:04 PM.

  17. #17
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Peter_1 View Post
    The effect of lowering condensing pressure is much bigger than the lowering of the evaporating pressure.
    You are absolutely right if the oversize is small, but here I get equipment designed for 60Hz working in 50Hz and if ambient temperature lowers or have two compressors with one off they inmediatelly start hunting.

    So what will happen really depends on how the other system components are sized.

    Even the type of expansion valve affects, (type of charge and balanced or not port).

  18. #18
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by wambat View Post
    A bigger condenser could have all of the following positive effects on a refrigeration system because it would have a lower condensing temperature.
    1. A better refrigeration effect
    2. A lower mass flow rate
    3. A lower volume flow rate
    4. A higher COP
    5. A lower condenser heat of rejection
    6. A lower condenser temp difference
    7. A lower condenser split
    8. A lower KW/ton
    9. higher efficiency and a happy compressor and it's components
    If Bigger Cond is a WIN-Win situation, then why we dont design all the systems with BIGGER cond.

    The initial cost will be high but system efficieny, COP, etc will increase drastically.

    There must be some disadvantages......

  19. #19
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by GXMPLX
    ...off they immediately start hunting.
    Hhhmmm, usually hunting only occurs when the components are not balanced or going through some severe/strange transients.

    If the equipment is balanced at 60Hz, the same should be expected at 50Hz with the only exception being the rated duty should be compensated for to achieve the desired results while operating at 50 Hz.
    Last edited by US Iceman; 21-07-2008 at 03:39 PM. Reason: fixed quote
    If all else fails, ask for help.


  20. #20
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Peter_1
    You need indeed a certain minimum Dp over the TEV but 4 bar is also given by Danfoss themselves.
    And we have the proof it works (even 3.5 bar)
    Look ones in the Danfoss tables and you will see that the capacity doesn't decrease that much with decreasing pressures.
    You say that SC increases during winter which is true but this increases also the capacity of the TEV and compensates a little for the lower DP.
    In theory, you can only have full liquid after the valve if you SC liquid to evaporating temperature.
    But I think this won't give any problem.
    These comments offer so much information that you do not typically learn in school. It would be well worth the time of other members to try to understand what Peter is describing and how it applies to refrigeration systems.

    Refrigeration systems do NOT have to have high discharge pressures to work.

    The only time you should see higher discharge pressures on air-cooled condensers (or evaporative condensers) is in the summer time (or during the hottest temperatures of you location).
    If all else fails, ask for help.


  21. #21
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by jwasir
    There must be some disadvantages......
    Well, there could be if the system is not designed to work under the lower discharge pressures. The refrigerant charge may increase a little, but the biggest problem is the additional cost of the condenser heat rejection capacity.

    From my experience... the smallest condensers are used so that the installing contractor can have the lowest price.
    If all else fails, ask for help.


  22. #22
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Usually, big condenser will improve system efficiency. Usually but not always. Greatly oversized condenser will use a lot of energy(fans, pumps). Sometimes, total energy use of the system with big condenser can be higher than for the system with smaller condenser.
    For proper evaporator operation demand(refrigeration load) and supply(liquid supply) should be balanced. At lower head pressure supply can be reduced. However, demand can be reduced as well. If this happen simultaneously, system will be balanced.

  23. #23
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    Condenser size is has a lot to do with maximum ambient temp.

    For example, I use very big condensers on milk tanks where the maximum ambient is 50°C, this is the only way I get condensate refrigerant in the receiver.
    Head pressure is very high anyway at these conditions.

  24. #24
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by jwasir View Post
    If Bigger Cond is a WIN-Win situation, then why we dont design all the systems with BIGGER cond.

    The initial cost will be high but system efficieny, COP, etc will increase drastically.

    There must be some disadvantages......
    They do make bigger condensers that is why the SEeR is going up every year, 15 years ago the seer was about 8 now it's 18 /19

  25. #25
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by US Iceman View Post
    Well, there could be if the system is not designed to work under the lower discharge pressures. The refrigerant charge may increase a little, but the biggest problem is the additional cost of the condenser heat rejection capacity.

    From my experience... the smallest condensers are used so that the installing contractor can have the lowest price.
    Whether the mfg likes it or not they will be mandated to increase to bigger condensers and the customer will have to pay. The return on investment will be lower KW use and maybe lower operating costs

  26. #26
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by US Iceman View Post
    Hhhmmm, usually hunting only occurs when the components are not balanced or going through some severe/strange transients.
    Not necessarily. You get TEV instability if the valve tries to operate below a curve called MSS (Minimum Stable Superheat) that graphs capacity versus valve superheat. By increasing subcooling you are moving this curve to higher superheat and will produce instability more often with TEVs that have fast acting charges.

    TEV stability problems are the ones I find less understood in these posts, not an easy subject that needs some drawings and I'll post something on this when I'm ready.

    Quote Originally Posted by US Iceman View Post
    If the equipment is balanced at 60Hz, the same should be expected at 50Hz with the only exception being the rated duty should be compensated for to achieve the desired results while operating at 50 Hz.
    Though the equipment remains in balance due to the fact that TEV works fine at 20% off nominal capacity, the compressor capacity is 20%less.

    The evaporator and condenser are different because it depends if the manufacturer changed blade´s attack angle to compensate for lower RPMs or not.

    The problem arises when you have low thermal loads the system becomes completely unstable and out of balance. The TEV is oversized and perform VERY poorly if thermal load drops 20% to 30% below the 50Hz value! Except for balanced port valves or absorber charges, that can control well as low as 20% off their rated capacity.

    This is worse in some equipment that already had the TEV oversized for the 60Hz capacity (It was correctly chosen but a little oversized).

  27. #27
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Sergei View Post
    Usually, big condenser will improve system efficiency. Usually but not always. Greatly oversized condenser will use a lot of energy(fans, pumps). Sometimes, total energy use of the system with big condenser can be higher than for the system with smaller condenser.
    For proper evaporator operation demand(refrigeration load) and supply(liquid supply) should be balanced. At lower head pressure supply can be reduced. However, demand can be reduced as well. If this happen simultaneously, system will be balanced.
    Air conditioning equipment condensers are already oversized. Water cooled do this because of the fouling factor, air cooled condensers have a fouling factor too on the ouside (bugs, dirt, corrosion).

  28. #28
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by jwasir View Post
    If Bigger Cond is a WIN-Win situation, then why we dont design all the systems with BIGGER cond.
    Cost is a BIG disadvantage.

    Quote Originally Posted by jwasir View Post
    The initial cost will be high but system efficieny, COP, etc will increase drastically.

    There must be some disadvantages......
    No! Some compressor are optimized for high condensing other for low condensing, if you use the wrong compressor with a large condenser you will get less COP.

    Consider that with this line of thought all condensers should be water cooled! Go ask Chemi_cool if this is possible!

    Every application has some optimizing to be done. Little larger condensers ok, too large will cause problems and probably lower system COP.

  29. #29
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by GXMPLX View Post
    Air conditioning equipment condensers are already oversized. Water cooled do this because of the fouling factor, air cooled condensers have a fouling factor too on the ouside (bugs, dirt, corrosion).
    Why do you think they are oversized? What is the right size?

  30. #30
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    This is worse in some equipment that already had the TEV oversized for the 60Hz capacity (It was correctly chosen but a little oversized).
    No argument on that point at all.

    I always prefer to have the valve slightly undersized and recommend the balanced port valves because I have had such good luck with them.
    If all else fails, ask for help.


  31. #31
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16
    Quote Originally Posted by Sergei View Post
    Why do you think they are oversized? What is the right size?


    Don´t make me dig on semantics here if you need X, anything bigger is oversized.

    Oversize is just another way of saying "safety factor".

    Your design objectives give you the right safety factor.

    Usually economical decisions let you choose the "right" condenser (No, US_Iceman please don't comment this on me! You simply have to fit in!)

  32. #32
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by US Iceman View Post
    No argument on that point at all.

    I always prefer to have the valve slightly undersized and recommend the balanced port valves because I have had such good luck with them.
    It´s not luck they are well designed, good valves!

  33. #33
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by GXMPLX View Post

    Don´t make me dig on semantics here if you need X, anything bigger is oversized.

    Oversize is just another way of saying "safety factor".

    Your design objectives give you the right safety factor.

    Usually economical decisions let you choose the "right" condenser (No, US_Iceman please don't comment this on me! You simply have to fit in!)
    This is my question. How big is the X? Why is it so big? Certainly, anything bigger than X is oversized.
    Wambat mentioned that bigger condensers will improve efficiency of the plant. Who is right?

  34. #34
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Mass Flow Rate with Big Condenser

    X = 10 deg TD.


    Hows that for starters.

  35. #35
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Billy Ray View Post
    X = 10 deg TD.


    Hows that for starters.
    Deg. C or deg. F. Why is it 10, not 8 or 15? This is question for professionals.

  36. #36
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Sergei View Post
    This is my question. How big is the X? Why is it so big? Certainly, anything bigger than X is oversized.
    Wambat mentioned that bigger condensers will improve efficiency of the plant. Who is right?

    Many times I have read absolute remarks in these posts, the problem is that most of them are right under certain conditions and maybe that's what makes people disagree.

    I agree that oversized condensers improve COP if they are little oversized in my case with 60Hz 50Hz problems see them 40% oversized and up.
    X in condensers stand for heat of compression+absorbed heat in the evap at the maximum operating suction pressure.

    This means that if you operate a system below its operating suction pressure the condenser is oversized and you won't see me pulling my hair (sorry scarce hair) having an oversized condenser.

    Low suction pressures usually (remark usually) means that the compressor COP goes down and it is the most important device of the system so the system should lower its COP

  37. #37
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by GXMPLX
    It´s not luck they are well designed, good valves!
    I did not mean I got lucky and they worked. I meant I had good results with the valve I carefully selected.
    If all else fails, ask for help.


  38. #38
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by GXMPLX View Post
    Many times I have read absolute remarks in these posts, the problem is that most of them are right under certain conditions and maybe that's what makes people disagree.

    I agree that oversized condensers improve COP if they are little oversized in my case with 60Hz 50Hz problems see them 40% oversized and up.
    X in condensers stand for heat of compression+absorbed heat in the evap at the maximum operating suction pressure.

    This means that if you operate a system below its operating suction pressure the condenser is oversized and you won't see me pulling my hair (sorry scarce hair) having an oversized condenser.

    Low suction pressures usually (remark usually) means that the compressor COP goes down and it is the most important device of the system so the system should lower its COP
    Why do not control suction pressure? Bigger condenser will lead to lower condensing pressure and better compressor COP. What about system COP? This is the different question. To run bigger condenser we have to use more energy(fans, pumps). Sometimes additional condenser energy is greater than compressor energy savings from lower condensing pressure. Another issue, every refrigeration plant has minimum allowable condensing pressure. What is this pressure? Certainly, it is better if we can reduce this minimum. How can we do that? Sorry, but have many questions.

  39. #39
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Sergei
    Who is right?
    I think we are all dancing around the right answer.

    Larger condensers improve the COP of the refrigeration cycle.

    If the fan or pump power is higher than the compressor energy saved, you lose.

    The condenser is the correct size, if the heat rejection capacity is equal to that of the compressor(s).

    The correct condenser selection is one that balances all of the above in a cost-effective manner.

    We could continue to say absolute statements or settle into semantics. I'm quilty of this too. Therefore, if we look at the underlying logic of our statements I think we can all agree.

    These are not directed at anyone specifically, just in general...

    Can we shake hands on that?
    Last edited by US Iceman; 22-07-2008 at 02:04 AM. Reason: edit
    If all else fails, ask for help.


  40. #40
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: Mass Flow Rate with Big Condenser

    Sergei, What GLMPLX is saying is absolutely correct If the condenser is too big then you can have some of the problems suggested by US Icaman and GLMPLX. That's what makes this forom so valuable is the comments and discussions about problem solving. I.m sorry if I was incomplete with my statement.
    The thing you need to know and understand with refrigeration is that all the components will do a good job (within certain perameters) you can't have too much and you can't have too little that's why we have to understand the complete refrigeration cycle and what all the effects that will happen when we make any changes
    Last edited by wambat; 22-07-2008 at 01:47 AM.

  41. #41
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by wambat
    ...that's why we have to understand the complete refrigeration cycle and what all the effects that will happen when we make any changes.
    I think Sergei already knows based on some our past discussions. I also think what seems like divergent views are a lot closer than we might want to admit also.
    If all else fails, ask for help.


  42. #42
    Join Date
    Jan 2007
    Location
    Canada
    Age
    65
    Posts
    158
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    I think that X is optimum size of condenser. What is the optimum? The optimum is the size of condenser when total(compressors, condensers, evaporators) power use per unit of refrigeration is minimum. If condenser is oversized we should reduce capacity(and energy use) of this condenser. So capacities of compressors and condensers should balanced to keep total power use at minimum level. This balancing should be done at different ambient conditions and different refrigeration loads. Sometimes optimum condensing pressure is low and we have a barriers to keep it low. However, every barrier has a solution. The longer we run plant at optimum condensing pressure, the better efficiency of this plant.

  43. #43
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Didn't know "X" would make such a fuzz!

    Optimums are hard to get at, when we are more like searching for feasible solutions! ... like not having our fuses blown!

  44. #44
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    I certinaly don't think anyone is getting their fuses (or fuzzes) blown.

    What we see with this discussion is the many different ways people look at topics and how they attack them to develop solutions.

    It is also important to recognize that any topic will have differing viewpoints because the posters all have different skill sets and experience levels.

    So...a simple question on over-sizing condensers went from theoretical to optimization to practical in the span of only several posts. How cool is that?!
    If all else fails, ask for help.


  45. #45
    Join Date
    Mar 2008
    Location
    Belgium
    Age
    40
    Posts
    32
    Rep Power
    0

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by Peter_1 View Post
    Look ones in the Danfoss tables and you will see that the capacity doesn't decrease that much with decreasing pressures.

    In theory, you can only have full liquid after the valve if you SC liquid to evaporating temperature.
    But I think this won't give any problem.
    Ok, didn't think it was able to work at these low pressures, I'll take a look.

    But If you have such a huge condensor with pressures as low as these. When working in a chamber at e.g. 10°C, with outside temps of -10° for example, you could have major problems with head pressure and need to keep your pressures up, no?

  46. #46
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    18

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by majo View Post
    Ok, didn't think it was able to work at these low pressures, I'll take a look.

    But If you have such a huge condensor with pressures as low as these. When working in a chamber at e.g. 10°C, with outside temps of -10° for example, you could have major problems with head pressure and need to keep your pressures up, no?
    Ofcourse, thats why we use low ambient package to maintain the min.design pressure differential across the TXV.

  47. #47
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Sorry I didn't have enough time to answer these, my way.

    Quote Originally Posted by wambat View Post
    ...
    The thing you need to know and understand with refrigeration is that all the components will do a good job (within certain perameters) you can't have too much and you can't have too little that's why we have to understand the complete refrigeration cycle and what all the effects that will happen when we make any changes
    Thanks wambat I think this is a wise post! And it was in response to Sergei's below.

    The only problem with it is that it implies that an optimum is somewhere in the middle and if I interpret Sergei right it's what he's after.

    Quote Originally Posted by Sergei View Post
    I .... What is the optimum? The optimum is the size of condenser when total(compressors, condensers, evaporators) power use per unit of refrigeration is minimum. If condenser is oversized we should reduce capacity(and energy use) of this condense .
    Unfortunately I've never seen a system designed so that it minimizes power per unit refrigeration.
    The big problem is this is impossible to do in the field you can calculate it and we better do, but it is done after the system is built not before.

    This is exactly what people in NASA should do with good computer models and crystal clear objectives and lots of computing resources, and maybe then build the system.

    YOU ARE ABSOLUTLY RIGHT WANTING THIS OBJECTIVE but I'm afraid we are far from it!

    Quote Originally Posted by Sergei View Post
    So capacities of compressors and condensers should balanced to keep total power use at minimum level. This balancing should be done at different ambient conditions and different refrigeration loads. Sometimes optimum condensing pressure is low and we have a barriers to keep it low. However, every barrier has a solution. The longer we run plant at optimum condensing pressure, the better efficiency of this plant.
    Yes, the balancing is done depending on ambient and cold room conditions but with a different objective an that is comply with demand.

    The primary objective of the system is to do the cooling what it is supposed to. All optimizations that I know are done are on component basis, not on system basis because it is impossible to stretch the condenser 5 inches to reach a better working condition.

    What you do is once you have the system (or at least selected componets) you do all optimization possible like adding capacity control maybe add a VFD but your system may be far from working at any optimum.

    A big one and very cost effective is heat recovery, that's why it has become a must with all big brands!

    Some system designers have programs to work in this direction but their own components cannot be assembled in such a way that you can make enough combinations to get even close to an energy use optimum like you want, THAT I KNOW OF!

  48. #48
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by US Iceman View Post
    I did not mean I got lucky and they worked. I meant I had good results with the valve I carefully selected.
    I hope jwasir forgives me for messing with his post in so many different directions like I know you would whack me for!

    This reminded me of something ... but I´ll better post it in the new balanced port TEV post.

  49. #49
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by majo View Post
    Ok, didn't think it was able to work at these low pressures, I'll take a look.

    But If you have such a huge condensor with pressures as low as these. When working in a chamber at e.g. 10°C, with outside temps of -10° for example, you could have major problems with head pressure and need to keep your pressures up, no?
    Well, we then use a VFD or switch-off the fans.
    But of course, you must take in account that the savings with running fans consuming power no longer match the savings they make.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  50. #50
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Mass Flow Rate with Big Condenser

    Quote Originally Posted by GXMPLX
    Unfortunately I've never seen a system designed so that it minimizes power per unit refrigeration.
    The big problem is this is impossible to do in the field you can calculate it and we better do, but it is done after the system is built not before.
    This is what I do for a living. If you are lucky to do this before the system is built it is so much easier. If you have to do it after installation it is a lot of work.

    There is an optimum for each operating condition. The real trick is to find these operating points and match the system response to these with the most cost effective method of operation.
    If all else fails, ask for help.


Page 1 of 2 12 LastLast

Similar Threads

  1. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  2. high volume flow rate
    By cakabo28 in forum Technical Discussions
    Replies: 5
    Last Post: 04-10-2007, 03:41 AM
  3. Shell/Tube flow rate?
    By reggie in forum Fundamentals
    Replies: 4
    Last Post: 17-11-2002, 06:41 PM
  4. Replies: 15
    Last Post: 24-10-2002, 06:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •