    3 Phase compressor



    hello everybody,

    i have a IMI marstaire unit,a CUE 100 condenser. The unit keeps tripping its contactor overload.

    I've taken its readings and on the three phases its pulling,

    red= 6.1
    yellow= 6.0
    blue= 5.2

    The overload is set to 10amps.

    I noticed on the compressor start up the amps go up to 14.9amps for a milli second, is this normal for a three phase compressor to go that high on start up??



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 3 Phase compressor

    The deferences between the 3 phases are too big, thats the compressor way of saying good bye.

    But, a 10 amp OL should not trip. I would change it first and follow its behaviour.

    Starting currant of this compressor [3 HP?] is about 70 amps but your amp meter doesn't have the "peak" function.

    And of course, let us know your progress.

  3. #3
    yoda22's Avatar
    yoda22 Guest

    Re: 3 Phase compressor

    Thanks Chemi-Cool. I've already ordered another overload,fitting it on Monday, see how it goes.

  4. #4
    Join Date
    Feb 2006
    Location
    England
    Posts
    64
    Rep Power
    19

    Re: 3 Phase compressor

    Quote Originally Posted by yoda22 View Post
    Thanks Chemi-Cool. I've already ordered another overload,fitting it on Monday, see how it goes.
    Hi, I would recommend you also change the contactor, as one of the legs may have a bad connection !

  5. #5
    Join Date
    Jul 2008
    Location
    australia
    Posts
    8
    Rep Power
    0

    Re: 3 Phase compressor

    g,day all.
    i assume you are taking the current draw of the compressor only. check the insulation resistance of the compressor ,and look for hot joints ( high resistance joints ) on the 3 supply (line and load)and contactor. then test the contactor and o/load.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Thumbs up Re: 3 Phase compressor

    Quote Originally Posted by yoda22 View Post
    hello everybody,

    i have a IMI marstaire unit,a CUE 100 condenser. The unit keeps tripping its contactor overload.

    I've taken its readings and on the three phases its pulling,

    red= 6.1
    yellow= 6.0
    blue= 5.2

    The overload is set to 10amps.

    I noticed on the compressor start up the amps go up to 14.9amps for a milli second, is this normal for a three phase compressor to go that high on start up??
    Yoda.
    All the Guys before have given good advise.
    I will add that according to the Marstair Site the current drawn for a MCU 100 (Can't find CUE 100) is
    Start Current LRA 51A.
    Nominal Current FLA 7.2A

    So in answer to part of your question 14.9A Would not seem excessive.
    That's assumeing the data I am using is relevant to your model?
    Having said that you would expect a surge on initial start-up.
    good luck Steve.

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 3 Phase compressor

    It would be worth checking the voltages on the phases as well and swaping the wires around to see if the low current follows the swaped wires or stays on the blue phase.

    contactor in-swap to-contactor out
    red -swap to-yellow
    yellow -swap to-blue
    blue -swap to-red

    In effect you have just rotated the phases so the compressor should still run the same way.

    Jon

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Testing Inverters
    By fridge doctor in forum Air Conditioning
    Replies: 38
    Last Post: 15-06-2011, 06:52 AM
  3. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  4. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  5. Three Phase Compressor
    By joeslad in forum Trouble Shooting
    Replies: 1
    Last Post: 12-10-2005, 11:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •