    Question dakin e3 code



    Hi to you all ,Dose any one have a list of errer codes for a dakin conducted unit?Its on r22 but i dont have the model number unless i go to see it.



  2. #2
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    515
    Rep Power
    18

    Re: dakin e3 code

    AO Indoor Error of external protection device
    A1 Indoor PCB defect
    A3 Indoor Malfunction of drain Level control system
    A5 Indoor Freeze-up prevention
    A6 Indoor Fan motor lock, Overload
    A7 Indoor Malfunction of swing motor flap
    A9 Indoor Malfunction of EEV
    AF Indoor Drain level above limit (clogging)
    AJ Indoor Malfunction of capacity set device
    C3 Indoor Malfunction of drain thermistor
    C4 Indoor Malfunction of liquid pipe thermistor
    C5 Indoor Malfunction of gas pipe thermistor
    C7 Indoor Lower louvre limit switch/motor
    C9 Indoor Malfunction of air thermistor
    CC Indoor Malfunction of moisture sensor
    CA Indoor Malfunction of discharge air thermistor
    CJ Indoor Malfunction of remote control thermistor
    CE Indoor Malfunction of radiant heat sensor
    E0 Outdoor Activation of outdoor safety device
    E1 Outdoor PCB defect
    E3 Outdoor Activation of high pressure switch
    E4 Outdoor Activation of low pressure switch
    E5 Outdoor Activation of compressor over heat protection
    E5 Outdoor Compressor motor lock
    E6 Outdoor Compressor start up error
    E6 Outdoor Standard compressor lock/overcurrent
    E7 Outdoor Fan motor lock, Overload
    E8 Outdoor Inverter input overcurrent
    E9 Outdoor Malfunction of EEV
    EA Outdoor Four way valve defective.
    F3 Outdoor Abnormal discharge pipe temperature
    F6 Outdoor Refrigerant overcharged
    FC Outdoor Low pressure drop.
    H3 Outdoor High pressure switch defect
    H4 Outdoor Low pressure switch defect
    H6 Outdoor Compressor motor position detection sensor error
    H7 Outdoor Fan motor position detection sensor error
    H8 Outdoor Current transformer error
    H9 Outdoor Malfunction of air thermistor
    J1 Outdoor Malfunction of pressure sensor
    J2 Outdoor Current sensor malfunction
    J3 Outdoor Malfunction of discharge pipe thermistor
    J4 Outdoor Low pressure saturation thermistor
    J5 Outdoor Malfunction of suction pipe thermistor
    J6 Outdoor Malfunction of heat exchanger thermistor
    J7 Outdoor Malfunction of heat exchanger liquid thermistor
    J8 Outdoor Malfunction of liquid pipe thermistor
    J9 Outdoor Malfunction of gas pipe thermistor
    JA Outdoor Malfunction of discharge pipe pressure sensor
    JC Outdoor Malfunction of suction pipe pressure sensor
    JH Outdoor Malfunction of oil temperature sensor
    L0 Outdoor Malfunction of inverter
    L3 Outdoor Electronic component box overheat
    L4 Outdoor Inverter cooling defect
    L5 Outdoor Comp motor ground fault, Short circuit
    L6 Outdoor Compressor motor grounding/short circuit
    L7 Outdoor Total input overcurrent
    L8 Outdoor Comp overload, Motor disconnected
    L9 Outdoor Compressor lock
    LA Outdoor Power unit malfunction
    LC Outdoor Transmission between inverter & outdoor
    P1 Outdoor Inverter over ripple
    P3 Outdoor Thermistor abnormality
    P4 Outdoor Power unit humidity sensor malfunction
    PJ Outdoor Failure of capacity set resistor
    U0 System Shortage of refrigerant or EEV failure
    U1 System Negative phase, Open phase
    U2 System Power supply insufficient
    U3 System Wiring check operation not executed
    U3 System Mismatch of indoor and outdoor units (Split only)
    U4 System Transmission between indoor units
    U5 System Transmission to remote controller
    U6 System Malfunction transmission outdoor to BP unit
    U7 System Transmission between outdoor units
    U7 Outdoor Malfunction between outdoor boards(RMX/RX RK)
    U8 System Transmission between master & slave R/C
    U9 System Transmission error between indoor to outdoor
    UA System Excessive number of fancoils
    UC System Address duplication of central controllers
    UE System Transmission error between indoor & central
    UF System Refrigeration system not set/wiring - piping
    UF System Terminals 1 and 3 crossed (Split/Skyair)
    If it ain't broke, it doesn't have enough features yet.


    Damo

  3. #3
    Join Date
    Sep 2005
    Location
    spain
    Age
    53
    Posts
    54
    Rep Power
    0

    Re: dakin e3 code

    wow thanks alot. you have been a grate help.thanks

Similar Threads

  1. lennox fault code
    By richelli in forum Trouble Shooting
    Replies: 0
    Last Post: 01-02-2008, 10:13 PM
  2. A6 Fault Code Problem
    By markcubed in forum Air Conditioning
    Replies: 3
    Last Post: 29-12-2007, 12:29 PM
  3. Daikin secret's code, is it true? How?
    By cool#9 in forum Air Conditioning
    Replies: 24
    Last Post: 20-12-2007, 02:11 PM
  4. Intermitent Daikin Fault Code?
    By sinewave in forum Air Conditioning
    Replies: 10
    Last Post: 24-11-2007, 01:40 AM
  5. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •