17-07-2008, 10:30 PM #1
retro fitting 22 syt for ***** change 134a
just wondering whats involved in or can it be done any thing from 15 ton to 80 ton syst
-
18-07-2008, 02:28 PM #2
Re: retro fitting 22 syt for ***** change 134a
It cant be done.
-
18-07-2008, 04:50 PM #3
Re: retro fitting 22 syt for ***** change 134a
I dont understand the part about 15 to 80 ton system please clarify.
The short answer is it can be done,but with 407c but should only be done by a professional,134a is not generably suitable for airconditioning and used in cars for saftey reasons due to the extream temperature.
-
18-07-2008, 05:26 PM #4
Re: retro fitting 22 syt for ***** change 134a
I'll follow up chemi-cool and castrigg statements. R-22 is a high pressure gas and R134a is a low pressure gas.
Some compressors will pump both but the capacity and operating range changes. It depends on the compressors design criteria.
-
11-01-2009, 08:58 AM #5
Re: retro fitting 22 syt for ***** change 134a
Yar. One word - Displacement.