Thread: condensers
    Feb 2008
    505
    21
    condensers
    can anyone tel me how to calculate condenser size from evap duty
    Jun 2005
    California
    394
    Re: condensers
    Quote Originally Posted by martinw58 View Post
    Is this for air conditioning duty and is it air cooled or water cooled?
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    May 2008
    weston
    348
    Re: condensers
    You can't.
    Condenser heat rejected = evaporator heat absorbed + heat of compression
    Jun 2005
    California
    394
    Re: condensers
    If you know the evaporator temperature and you have the evaporator load then you need a mfg heat rejection factor for either an open compressor or a suction cooled compressor EX; evaporator load = 12,000 btu
    evaporator temperature = 20*F
    from mfg condensing table for suction cooled compressor the temperature heat correction factor = 1.33 for say 110 condensing temperature = ~ 4,000 btu for a total of 14,000 btu condenser.I would use 15,000 btu. If I wanted to know what HP fan motor to use I would devide 15,000 btu/1.08 x TD = CFM for air cooled condenser
  1. Replies: 9
    Last Post: 30-01-2009, 07:50 AM
  2. opinion on uneven parallel condensers
    By Dimitris in forum Technical Discussions
    Last Post: 28-05-2008, 04:23 PM
  3. Sourcing Condensers in USA
    By Vincent Yu in forum Fundamentals
    Last Post: 05-10-2005, 01:48 AM
  4. Question on condensers
    By EAMAN in forum Technical Discussions
    Last Post: 04-06-2002, 03:20 PM
  5. Blak Condensers
    By ben chaib in forum Domestic
    Last Post: 16-03-2002, 03:31 PM