    Enviormental Chamber Question



    I have to rebuild an environmental chamber, and that environmental chamber need to be holding constant temperature(within 3 degree C) in a range of 20 to 25 and 30 to 35.

    So I have an idea of routing a air compressor, condenser, evaporator, and a valve which could alternate the flow of refrigerant. so when I need the enviormental chamber hotter the valve can make this "air conditioning system" hotter, and colder the other way.

    My question is:
    Is this going to work like this, if not, any suggestion will be appreciate.

    What kind of refrigerant should I use?

    Also, is there anything that I need to be aware of.

    I am totally new to refrigerant system



  2. #2
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Enviormental Chamber Question

    Don't understat what you want to do with an air compressor!

    Take hot and cold air from the refrigeration system?

    Where will you get thermal load for the system from?

    In a normal syste any attempt to controll such a short differential will cause cycling problems unless you use an air handler with two coils.

    One coil for refrigeration as usual, another for heating.

    The design/controll of this system is not easy and beyond what I can do for you in these posts.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Enviormental Chamber Question

    Are you a magician??

  4. #4
    MaxPoon's Avatar
    MaxPoon Guest

    Re: Enviormental Chamber Question

    So is there anyway to make this to work, that's the job that my boss give me, and I have no clue about refrigeration.

  5. #5
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Enviormental Chamber Question

    Quote Originally Posted by MaxPoon View Post
    So is there anyway to make this to work, that's the job that my boss give me, and I have no clue about refrigeration.

    You could:
    1. Use a refrigeration system the usual way with a refrigeration compressor and the evaporator in the room.
    2. Use the air compressor to draw in hot air from the condenser air discharge when you need to heat the room but the only way to distribute the air correctly is discharging the air evenly into the air suction of the evaporator. This would make your refrigeration system work like a wild horse!

    Any attempt to use the air compressor for refrigeration will fail.

    Don't tell anybody here I suggested this!

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Enviormental Chamber Question

    Quote Originally Posted by MaxPoon
    So is there anyway to make this to work?
    Call someone who has worked on applications where environmental chambers are used!

    These are very precisely controlled and tend to be complex systems due to the close tolerances required for temperature.

    If you have no refrigeration experience, you should be willing to call and pay someone for the expertise.

    These chambers are NOT just a walk-in cooler....
    If all else fails, ask for help.


  7. #7
    Join Date
    Mar 2008
    Location
    Belgium
    Age
    40
    Posts
    32
    Rep Power
    0

    Re: Enviormental Chamber Question

    just call the guys from thermotron USA

  8. #8
    Join Date
    Jan 2010
    Location
    Southern California
    Posts
    19
    Rep Power
    0

    Re: Enviormental Chamber Question

    Piece of cake.

    Install an insulated hot gas line running from the discharge of the compressor to the point between the TXV and the distributor on the evaporator coil.

    Install a hot gas solenoid valve near the compressor.

    Use a digital temperature controller, set the Diff. to
    1 deg c

    When cooling cut-out is reached, instead of shutting off the compressor, energize the hot gas solenoid.
    When cooling cut in is reached, de-energize the hot gas sol'n.

    This means that your compressor will always be running. This method will actually extend the life of the compressor due to minimal starts/stops.

    This also provides the heating mode you need to reach your higher temperature setpoints.

    Just make sure you install a suction accumulator, and size your lines properly paying attention to proper oil return.

    You don't need any extra or special evap. coils, size them like a normal system.

    Make sure to insulate your hot gas line from compressor to evap.

    You can get accurate control with this configuration, as close as plus or minus 0.5 deg F

    You don't need a shut off sol'n on the liquid line for temp. control, only for pump down cycle when shutting down system.

    I hope this helps, if you have questions ,...feel free.

    Jeff P.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Enviormental Chamber Question

    Quote Originally Posted by MaxPoon View Post
    I have to rebuild an environmental chamber, and that environmental chamber need to be holding constant temperature(within 3 degree C) in a range of 20 to 25 and 30 to 35.

    So I have an idea of routing a air compressor, condenser, evaporator, and a valve which could alternate the flow of refrigerant. so when I need the enviormental chamber hotter the valve can make this "air conditioning system" hotter, and colder the other way.

    My question is:
    Is this going to work like this, if not, any suggestion will be appreciate.

    What kind of refrigerant should I use?

    Also, is there anything that I need to be aware of.

    I am totally new to refrigerant system
    As I understand it, you are not building the system, you are rebuilding the system.

    How is it currently being done?

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Enviormental Chamber Question

    I wouldn't worry Gary, the OP was two years ago and the thread is only revived by Zpoint as he has an interest in these things.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Enviormental Chamber Question

    Somehow, I always miss the OP date... gets me every time... lol

  12. #12
    Join Date
    Jan 2010
    Location
    Southern California
    Posts
    19
    Rep Power
    0

    Re: Enviormental Chamber Question

    So sorry,

    I will check op date from now on.

    Just trying to help.

Similar Threads

  1. Refriferation cycle question
    By ozmecheng in forum Fundamentals
    Replies: 32
    Last Post: 26-03-2008, 10:38 PM
  2. Hitachi RAC25NH5 question
    By Yonas in forum Heat Pumps
    Replies: 11
    Last Post: 30-01-2008, 10:53 AM
  3. Humidity Chamber - Please Help
    By Deejay in forum Technical Discussions
    Replies: 4
    Last Post: 29-09-2007, 03:17 AM
  4. quizy type question thingy
    By rbartlett in forum Chit Chat & Service Stories
    Replies: 25
    Last Post: 06-02-2006, 09:22 PM
  5. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •