    pressure difference in TXV system



    Hi there,

    For a TXV system, what is the pressure difference between condenser and evaporator during cycle off? Thanks.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: pressure difference in TXV system

    How long is a piece of string?

    It would depend on the refrigerant, the respective standing temperatures of the condenser and evaporator, the temperature range of the tev/txv, if the valve has a bleed port, pumpdown/solenoid etc.

    Are you thinking about a specific system or just wondering?

    Jon

  3. #3
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: pressure difference in TXV system

    Jon,
    I am wondering, for a cap system, they will equal to each other. For a txv system, will they? We assume it is a R134a system. No bleed port. Cond is about 100F, evap is about 10F.
    Thanks.

    David

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: pressure difference in TXV system

    If you know the temperatures then you have your answer already.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: pressure difference in TXV system

    Quote Originally Posted by Brian_UK View Post
    If you know the temperatures then you have your answer already.
    My fault. Temperature is refer to cycle on. I don't know the temp of cycle off.

  6. #6
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: pressure difference in TXV system

    Depends on system design.

    If you don't use pump down or a special kind of expansion valve the difference is CERO ZIP NADA NIE.

    If you use pumpdown it'll vary slowly and be saturation pressure at condenser temperature minus the cut out pressure for the compressor. If the pressure moves above low pressure cut in the compressor will start and leave it at cut out.

    If you have a special type of valve, depends on what else is closing the system.

  7. #7
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: pressure difference in TXV system

    Quote Originally Posted by GXMPLX View Post
    Depends on system design.

    If you don't use pump down or a special kind of expansion valve the difference is CERO ZIP NADA NIE.
    After I google, I know CERO ZIP NADA NIE means zero. Thank you.

    David

  8. #8
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: pressure difference in TXV system

    Quote Originally Posted by david2008 View Post
    After I google, I know CERO ZIP NADA NIE means zero. Thank you.

    David

    What? You mean you don't whatch Stallone movies?

  9. #9
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: pressure difference in TXV system

    Last edited by david2008; 16-07-2008 at 12:11 PM.

  10. #10
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16
    I’m not too fond of politics! May get you in trouble.

  11. #11
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: pressure difference in TXV system

    Quote Originally Posted by GXMPLX View Post
    I’m not too fond of politics! May get you in trouble.
    me too. . .
    Last edited by david2008; 16-07-2008 at 12:12 PM.

  12. #12
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: pressure difference in TXV system

    Quote Originally Posted by david2008 View Post
    me too. . .
    I can't believe it! Tried to post the answer here yet got the internal error again.

    Well to sumarize the example you gave in other post lacks fundamental data like the system volume yo need it to estimate the refrigerant charge.

    The only new thing is that to estimate the amount of liquid refrigerant in the receiver at maximum load you'll get a minimum height in the receiver and can calculate the height by equating potential energy of the fluid=maximum kinetic energy of the fluid at the vena contracta.

    Use half the area of the outlet pipe of the receiver as the size of the vena contracta and apply bernoulli to calculate the height needed in the receiver.

    With this height and refrigerant densities at the conditions you mentioned you can estimate the mass of refrigerant in the receiver.

    Collect manufacturer data for condenser and evaporator. If you don't have estimate 70/30 percent of volume for vapor/liquid in the condenser and 30/70 percent of vapor/liquid in the evaporator. With this and densities at the corresponing temperatures give you the mass of refrigerant.

    Add the volume of the liquid line times the density

    And you have an estimation.

    You read in other threads you have to check by measuring superheat at minumum load and this is about it!

  13. #13
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: pressure difference in TXV system

    This got through! I must have a non printable character somewhere in my original answer!

  14. #14
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: pressure difference in TXV system

    Quote Originally Posted by GXMPLX View Post
    I can't believe it! Tried to post the answer here yet got the internal error again.

    Well to sumarize the example you gave in other post lacks fundamental data like the system volume yo need it to estimate the refrigerant charge.

    The only new thing is that to estimate the amount of liquid refrigerant in the receiver at maximum load you'll get a minimum height in the receiver and can calculate the height by equating potential energy of the fluid=maximum kinetic energy of the fluid at the vena contracta.

    Use half the area of the outlet pipe of the receiver as the size of the vena contracta and apply bernoulli to calculate the height needed in the receiver.

    With this height and refrigerant densities at the conditions you mentioned you can estimate the mass of refrigerant in the receiver.

    Collect manufacturer data for condenser and evaporator. If you don't have estimate 70/30 percent of volume for vapor/liquid in the condenser and 30/70 percent of vapor/liquid in the evaporator. With this and densities at the corresponing temperatures give you the mass of refrigerant.

    Add the volume of the liquid line times the density

    And you have an estimation.

    You read in other threads you have to check by measuring superheat at minumum load and this is about it!
    Thanks. I will have a try using the method above.

Similar Threads

  1. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  2. Need Help On experimental System
    By manuelcm in forum Fundamentals
    Replies: 16
    Last Post: 17-12-2006, 05:47 AM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. R507 in an R134a compressor: system design
    By DaBit in forum Technical Speculations
    Replies: 17
    Last Post: 01-05-2003, 09:25 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •